JA
John Ackermann N8UR
Sun, May 26, 2024 2:39 PM
I need to replace the batteries in my 28 VDC power distribution system
in the clock room. It's currently two series 12V AGM batteries with an
IOTA Engineering float charger.
This system has two purposes: (a) primary power for some OCXOs and other
gear; and (b) failover power for some AC/DC gear like HP standards.
Under normal conditions, power draw is 2 or 3 amps. During mains
outage, it could reach 10 amps. Now that I have a house generator, long
run-time isn't a big issue so 25 Ah or so of capacity is plenty.
I haven't explored LiFePo4 batteries until now, and I'm having trouble
finding a charger that can provide significant continuous load current
while maintaining a battery floated across the line. Does anyone have
recommendations for something like this?
Thanks,
John
I need to replace the batteries in my 28 VDC power distribution system
in the clock room. It's currently two series 12V AGM batteries with an
IOTA Engineering float charger.
This system has two purposes: (a) primary power for some OCXOs and other
gear; and (b) failover power for some AC/DC gear like HP standards.
Under normal conditions, power draw is 2 or 3 amps. During mains
outage, it could reach 10 amps. Now that I have a house generator, long
run-time isn't a big issue so 25 Ah or so of capacity is plenty.
I haven't explored LiFePo4 batteries until now, and I'm having trouble
finding a charger that can provide significant continuous load current
while maintaining a battery floated across the line. Does anyone have
recommendations for something like this?
Thanks,
John
PS
paul swed
Sun, May 26, 2024 7:43 PM
John there seem to be various LI technology in Ham Radio for remote ops.
But they seem expensive from what I have looked at. Then a bit more of a
challenge stacking batteries for 24 V.
Possiblity, just get two AGM batteries in the 25A class and use what you
have.
Understanding the last comment is totally boring.
Regards
Paul
WB8TSL
On Sun, May 26, 2024 at 3:35 PM John Ackermann N8UR via time-nuts <
time-nuts@lists.febo.com> wrote:
I need to replace the batteries in my 28 VDC power distribution system
in the clock room. It's currently two series 12V AGM batteries with an
IOTA Engineering float charger.
This system has two purposes: (a) primary power for some OCXOs and other
gear; and (b) failover power for some AC/DC gear like HP standards.
Under normal conditions, power draw is 2 or 3 amps. During mains
outage, it could reach 10 amps. Now that I have a house generator, long
run-time isn't a big issue so 25 Ah or so of capacity is plenty.
I haven't explored LiFePo4 batteries until now, and I'm having trouble
finding a charger that can provide significant continuous load current
while maintaining a battery floated across the line. Does anyone have
recommendations for something like this?
Thanks,
John
time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe send an email to time-nuts-leave@lists.febo.com
John there seem to be various LI technology in Ham Radio for remote ops.
But they seem expensive from what I have looked at. Then a bit more of a
challenge stacking batteries for 24 V.
Possiblity, just get two AGM batteries in the 25A class and use what you
have.
Understanding the last comment is totally boring.
Regards
Paul
WB8TSL
On Sun, May 26, 2024 at 3:35 PM John Ackermann N8UR via time-nuts <
time-nuts@lists.febo.com> wrote:
> I need to replace the batteries in my 28 VDC power distribution system
> in the clock room. It's currently two series 12V AGM batteries with an
> IOTA Engineering float charger.
>
> This system has two purposes: (a) primary power for some OCXOs and other
> gear; and (b) failover power for some AC/DC gear like HP standards.
> Under normal conditions, power draw is 2 or 3 amps. During mains
> outage, it could reach 10 amps. Now that I have a house generator, long
> run-time isn't a big issue so 25 Ah or so of capacity is plenty.
>
> I haven't explored LiFePo4 batteries until now, and I'm having trouble
> finding a charger that can provide significant continuous load current
> while maintaining a battery floated across the line. Does anyone have
> recommendations for something like this?
>
> Thanks,
> John
> _______________________________________________
> time-nuts mailing list -- time-nuts@lists.febo.com
> To unsubscribe send an email to time-nuts-leave@lists.febo.com
>
RK
Richard Karst
Sun, May 26, 2024 7:47 PM
The LiFePo4 batteries are amazing things but for backup purposes there is a catch. They often have a build in BMS (Battery Management System) and under certain conditions such as for example a small overvoltage the MosFET in the BMS can switch of the power to you equipment without prior notice.
Richard
Op 26 mei 2024, om 16:39 heeft John Ackermann N8UR via time-nuts time-nuts@lists.febo.com het volgende geschreven:
I need to replace the batteries in my 28 VDC power distribution system in the clock room. It's currently two series 12V AGM batteries with an IOTA Engineering float charger.
This system has two purposes: (a) primary power for some OCXOs and other gear; and (b) failover power for some AC/DC gear like HP standards. Under normal conditions, power draw is 2 or 3 amps. During mains outage, it could reach 10 amps. Now that I have a house generator, long run-time isn't a big issue so 25 Ah or so of capacity is plenty.
I haven't explored LiFePo4 batteries until now, and I'm having trouble finding a charger that can provide significant continuous load current while maintaining a battery floated across the line. Does anyone have recommendations for something like this?
Thanks,
John
time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe send an email to time-nuts-leave@lists.febo.com
Met vriendelijke groet | With kindest regards | Cordialement | Med vennlig hilsen | Mit freundlichen Grüßen,
Richard Karst
PA1fYB
Dit bericht is slechts bestemd voor de geadresseerde en kan informatie bevatten die persoonlijk en/of vertrouwelijk is en die niet openbaar mag worden gemaakt. Indien u niet zelf de geadresseerde bent, wordt u erop gewezen dat verdere verspreiding, openbaarmaking of vermenigvuldiging van dit bericht verboden is. Indien u dit bericht per vergissing hebt ontvangen, verzoek ik u mij zo snel mogelijk op de hoogte te stellen en het originele bericht en eventuele kopieen ervan, te verwijderen. Dank voor uw medewerking.
This e-mail and any attachment is for authorised use by the intended recipient(s) only. It may contain proprietary material, confidential information and/or be subject to legal privilege. It should not be copied, disclosed to, retained or used by, any other party. If you are not an intended recipient then please promptly delete this e-mail and any attachment and all copies and inform the sender. Thank you.
The LiFePo4 batteries are amazing things but for backup purposes there is a catch. They often have a build in BMS (Battery Management System) and under certain conditions such as for example a small overvoltage the MosFET in the BMS can switch of the power to you equipment without prior notice.
Richard
Op 26 mei 2024, om 16:39 heeft John Ackermann N8UR via time-nuts <time-nuts@lists.febo.com> het volgende geschreven:
I need to replace the batteries in my 28 VDC power distribution system in the clock room. It's currently two series 12V AGM batteries with an IOTA Engineering float charger.
This system has two purposes: (a) primary power for some OCXOs and other gear; and (b) failover power for some AC/DC gear like HP standards. Under normal conditions, power draw is 2 or 3 amps. During mains outage, it could reach 10 amps. Now that I have a house generator, long run-time isn't a big issue so 25 Ah or so of capacity is plenty.
I haven't explored LiFePo4 batteries until now, and I'm having trouble finding a charger that can provide significant continuous load current while maintaining a battery floated across the line. Does anyone have recommendations for something like this?
Thanks,
John
_______________________________________________
time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe send an email to time-nuts-leave@lists.febo.com
Met vriendelijke groet | With kindest regards | Cordialement | Med vennlig hilsen | Mit freundlichen Grüßen,
Richard Karst
PA1fYB
Dit bericht is slechts bestemd voor de geadresseerde en kan informatie bevatten die persoonlijk en/of vertrouwelijk is en die niet openbaar mag worden gemaakt. Indien u niet zelf de geadresseerde bent, wordt u erop gewezen dat verdere verspreiding, openbaarmaking of vermenigvuldiging van dit bericht verboden is. Indien u dit bericht per vergissing hebt ontvangen, verzoek ik u mij zo snel mogelijk op de hoogte te stellen en het originele bericht en eventuele kopieen ervan, te verwijderen. Dank voor uw medewerking.
This e-mail and any attachment is for authorised use by the intended recipient(s) only. It may contain proprietary material, confidential information and/or be subject to legal privilege. It should not be copied, disclosed to, retained or used by, any other party. If you are not an intended recipient then please promptly delete this e-mail and any attachment and all copies and inform the sender. Thank you.
MD
Magnus Danielson
Sun, May 26, 2024 7:55 PM
Hi John,
So, I have used three pairs of 12V batteries that have been charged
similarly. That has worked out very well. I was now given another 10
batteries that I've similarly charged up individually and will wire up
so that they can form another 5 pairs.
Now, I know people that use LiFePo4. They have a few key learnings for
their use:
-
Use only appropriate chargers. They are more tricky on that.
-
Be carefull to cut off so they do not discharge too much (also valid
for lead batteries)
-
Yes, the initial cost is higher, but treat them right and they
survive better than lead, so total economy can be better.
Since I have been given lead batteries, I've stayed with that and use
it. If I had to invest from scratch, LiFePo4 looks interesting.
Cheers,
Magnus
On 2024-05-26 16:39, John Ackermann N8UR via time-nuts wrote:
I need to replace the batteries in my 28 VDC power distribution system
in the clock room. It's currently two series 12V AGM batteries with
an IOTA Engineering float charger.
This system has two purposes: (a) primary power for some OCXOs and
other gear; and (b) failover power for some AC/DC gear like HP
standards. Under normal conditions, power draw is 2 or 3 amps. During
mains outage, it could reach 10 amps. Now that I have a house
generator, long run-time isn't a big issue so 25 Ah or so of capacity
is plenty.
I haven't explored LiFePo4 batteries until now, and I'm having trouble
finding a charger that can provide significant continuous load current
while maintaining a battery floated across the line. Does anyone have
recommendations for something like this?
Thanks,
John
time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe send an email to time-nuts-leave@lists.febo.com
Hi John,
So, I have used three pairs of 12V batteries that have been charged
similarly. That has worked out very well. I was now given another 10
batteries that I've similarly charged up individually and will wire up
so that they can form another 5 pairs.
Now, I know people that use LiFePo4. They have a few key learnings for
their use:
1) Use only appropriate chargers. They are more tricky on that.
2) Be carefull to cut off so they do not discharge too much (also valid
for lead batteries)
3) Yes, the initial cost is higher, but treat them right and they
survive better than lead, so total economy can be better.
Since I have been given lead batteries, I've stayed with that and use
it. If I had to invest from scratch, LiFePo4 looks interesting.
Cheers,
Magnus
On 2024-05-26 16:39, John Ackermann N8UR via time-nuts wrote:
> I need to replace the batteries in my 28 VDC power distribution system
> in the clock room. It's currently two series 12V AGM batteries with
> an IOTA Engineering float charger.
>
> This system has two purposes: (a) primary power for some OCXOs and
> other gear; and (b) failover power for some AC/DC gear like HP
> standards. Under normal conditions, power draw is 2 or 3 amps. During
> mains outage, it could reach 10 amps. Now that I have a house
> generator, long run-time isn't a big issue so 25 Ah or so of capacity
> is plenty.
>
> I haven't explored LiFePo4 batteries until now, and I'm having trouble
> finding a charger that can provide significant continuous load current
> while maintaining a battery floated across the line. Does anyone have
> recommendations for something like this?
>
> Thanks,
> John
> _______________________________________________
> time-nuts mailing list -- time-nuts@lists.febo.com
> To unsubscribe send an email to time-nuts-leave@lists.febo.com
G
glenlist
Sun, May 26, 2024 8:43 PM
For charging LiFePO4 batteries, these are reasonably compatible with
lead acid chargers with the following caveats
-
Lifepo4 have approx zero temperature coefficient, so any temperature
compensation on the lead acid charger, if present needs to be disabled.
(if is a good lead acid charger, it will have compensation and a
temperature probe)
-
Equalise mode on the lead acid charger , if present must be disabled.
Equalise mode is designed to deliberately overcharge the battery to
being all cells to max. This will dramically overcharge the LIFEPO4
cells. no good.
-
Low battery cutoff, like on a lead acid, is essential. Set for 2.7V
per cell. LIFEPO4 cells if discharged below 2.7V per cell say all the
way to 2.5, must have initial charge rate of less than C/50 ideally
until they reach 2.7/cell.
LIFEPO4 batteries, due to their all-off -capacity performance, will
provide approximately 2x the effective useable capacity of a lead acid
cell, especially at something like 0.333C discharge (3 hours). Most lead
acid batteries are specified for 10 or 20 hour discharge rates .
overall you are a factor of 4 ahead of weight !.
Now- time has marched on, and many modern chargers either have
microprocessor contrained LIFEPO4 profiles or chips that know what they
are doing, so finding a suitable charger is fairly straightforward. A
pro lead acid charger will be fine most likely, also- because on a pro
charger you would have control over options like temp comp and equalise
mode.
feel free to contact me direct
glen
On 27/05/2024 12:39 am, John Ackermann N8UR via time-nuts wrote:
I need to replace the batteries in my 28 VDC power distribution system
in the clock room. It's currently two series 12V AGM batteries with
an IOTA Engineering float charger.
This system has two purposes: (a) primary power for some OCXOs and
other gear; and (b) failover power for some AC/DC gear like HP
standards. Under normal conditions, power draw is 2 or 3 amps. During
mains outage, it could reach 10 amps. Now that I have a house
generator, long run-time isn't a big issue so 25 Ah or so of capacity
is plenty.
I haven't explored LiFePo4 batteries until now, and I'm having trouble
finding a charger that can provide significant continuous load current
while maintaining a battery floated across the line. Does anyone have
recommendations for something like this?
Thanks,
John
time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe send an email to time-nuts-leave@lists.febo.com
For charging LiFePO4 batteries, these are reasonably compatible with
lead acid chargers with the following caveats
1) Lifepo4 have approx zero temperature coefficient, so any temperature
compensation on the lead acid charger, if present needs to be disabled.
(if is a good lead acid charger, it will have compensation and a
temperature probe)
2) Equalise mode on the lead acid charger , if present must be disabled.
Equalise mode is designed to deliberately overcharge the battery to
being all cells to max. This will dramically overcharge the LIFEPO4
cells. no good.
3) Low battery cutoff, like on a lead acid, is essential. Set for 2.7V
per cell. LIFEPO4 cells if discharged below 2.7V per cell say all the
way to 2.5, must have initial charge rate of less than C/50 ideally
until they reach 2.7/cell.
LIFEPO4 batteries, due to their all-off -capacity performance, will
provide approximately 2x the effective useable capacity of a lead acid
cell, especially at something like 0.333C discharge (3 hours). Most lead
acid batteries are specified for 10 or 20 hour discharge rates .
overall you are a factor of 4 ahead of weight !.
Now- time has marched on, and many modern chargers either have
microprocessor contrained LIFEPO4 profiles or chips that know what they
are doing, so finding a suitable charger is fairly straightforward. A
pro lead acid charger will be fine most likely, also- because on a pro
charger you would have control over options like temp comp and equalise
mode.
feel free to contact me direct
glen
On 27/05/2024 12:39 am, John Ackermann N8UR via time-nuts wrote:
> I need to replace the batteries in my 28 VDC power distribution system
> in the clock room. It's currently two series 12V AGM batteries with
> an IOTA Engineering float charger.
>
> This system has two purposes: (a) primary power for some OCXOs and
> other gear; and (b) failover power for some AC/DC gear like HP
> standards. Under normal conditions, power draw is 2 or 3 amps. During
> mains outage, it could reach 10 amps. Now that I have a house
> generator, long run-time isn't a big issue so 25 Ah or so of capacity
> is plenty.
>
> I haven't explored LiFePo4 batteries until now, and I'm having trouble
> finding a charger that can provide significant continuous load current
> while maintaining a battery floated across the line. Does anyone have
> recommendations for something like this?
>
> Thanks,
> John
> _______________________________________________
> time-nuts mailing list -- time-nuts@lists.febo.com
> To unsubscribe send an email to time-nuts-leave@lists.febo.com
PK
Poul-Henning Kamp
Sun, May 26, 2024 9:40 PM
John Ackermann N8UR via time-nuts writes:
I haven't explored LiFePo4 batteries until now, and I'm having trouble
finding a charger that can provide significant continuous load current
while maintaining a battery floated across the line.
LiOn is a weird battery chemistry: Strictly speaking it is only a
~3.7V cell, but for strange reasons you can overcharge them to ~4.1V,
and get another 20% capacity, which is how nameplate capacity is
specified.
In theory you can float LiOn in the range 2.7V to 3.7V, but you
cannot trust the cells to balance themselves, you have to regulate
the voltage over each individual cell, and that complicates things.
But if you already have all the infrastructure and dont need a particular
long runtime: Buy two new AGM batteries and spend your time and money
on something else.
--
Poul-Henning Kamp | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG | TCP/IP since RFC 956
FreeBSD committer | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.
--------
John Ackermann N8UR via time-nuts writes:
> I haven't explored LiFePo4 batteries until now, and I'm having trouble
> finding a charger that can provide significant continuous load current
> while maintaining a battery floated across the line.
LiOn is a weird battery chemistry: Strictly speaking it is only a
~3.7V cell, but for strange reasons you can overcharge them to ~4.1V,
and get another 20% capacity, which is how nameplate capacity is
specified.
In theory you can float LiOn in the range 2.7V to 3.7V, but you
cannot trust the cells to balance themselves, you have to regulate
the voltage over each individual cell, and that complicates things.
But if you already have all the infrastructure and dont need a particular
long runtime: Buy two new AGM batteries and spend your time and money
on something else.
--
Poul-Henning Kamp | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG | TCP/IP since RFC 956
FreeBSD committer | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.
MF
Michael Fahmie
Sun, May 26, 2024 9:46 PM
John,
I have found that the HLG series of Meanwell power supplies work quite well
in that service. The HLG-600H-30A is rated at 20 amps and is adjustable for
constant current/voltage. My 12v home system uses a HLG-600H-15A to
charge/maintain a 600 AH LiFePO4 bank, and I have used their lower powered
HLG supplies in several other LiFePO4 applications.
-Mike-
WA6ZTY
On Sun, May 26, 2024 at 12:35 PM John Ackermann N8UR via time-nuts <
time-nuts@lists.febo.com> wrote:
I need to replace the batteries in my 28 VDC power distribution system
in the clock room. It's currently two series 12V AGM batteries with an
IOTA Engineering float charger.
This system has two purposes: (a) primary power for some OCXOs and other
gear; and (b) failover power for some AC/DC gear like HP standards.
Under normal conditions, power draw is 2 or 3 amps. During mains
outage, it could reach 10 amps. Now that I have a house generator, long
run-time isn't a big issue so 25 Ah or so of capacity is plenty.
I haven't explored LiFePo4 batteries until now, and I'm having trouble
finding a charger that can provide significant continuous load current
while maintaining a battery floated across the line. Does anyone have
recommendations for something like this?
Thanks,
John
time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe send an email to time-nuts-leave@lists.febo.com
John,
I have found that the HLG series of Meanwell power supplies work quite well
in that service. The HLG-600H-30A is rated at 20 amps and is adjustable for
constant current/voltage. My 12v home system uses a HLG-600H-15A to
charge/maintain a 600 AH LiFePO4 bank, and I have used their lower powered
HLG supplies in several other LiFePO4 applications.
-Mike-
WA6ZTY
On Sun, May 26, 2024 at 12:35 PM John Ackermann N8UR via time-nuts <
time-nuts@lists.febo.com> wrote:
> I need to replace the batteries in my 28 VDC power distribution system
> in the clock room. It's currently two series 12V AGM batteries with an
> IOTA Engineering float charger.
>
> This system has two purposes: (a) primary power for some OCXOs and other
> gear; and (b) failover power for some AC/DC gear like HP standards.
> Under normal conditions, power draw is 2 or 3 amps. During mains
> outage, it could reach 10 amps. Now that I have a house generator, long
> run-time isn't a big issue so 25 Ah or so of capacity is plenty.
>
> I haven't explored LiFePo4 batteries until now, and I'm having trouble
> finding a charger that can provide significant continuous load current
> while maintaining a battery floated across the line. Does anyone have
> recommendations for something like this?
>
> Thanks,
> John
> _______________________________________________
> time-nuts mailing list -- time-nuts@lists.febo.com
> To unsubscribe send an email to time-nuts-leave@lists.febo.com
>
BC
Bob Camp
Sun, May 26, 2024 10:30 PM
Hi
There are several outfits that do very good LiFePO4 chargers. One is Victron. Often the answer is a hybrid inverter/ charger. They aren’t cheap…..
Bob
Sent from my iPhone
On May 26, 2024, at 4:35 PM, John Ackermann N8UR via time-nuts time-nuts@lists.febo.com wrote:
I need to replace the batteries in my 28 VDC power distribution system in the clock room. It's currently two series 12V AGM batteries with an IOTA Engineering float charger.
This system has two purposes: (a) primary power for some OCXOs and other gear; and (b) failover power for some AC/DC gear like HP standards. Under normal conditions, power draw is 2 or 3 amps. During mains outage, it could reach 10 amps. Now that I have a house generator, long run-time isn't a big issue so 25 Ah or so of capacity is plenty.
I haven't explored LiFePo4 batteries until now, and I'm having trouble finding a charger that can provide significant continuous load current while maintaining a battery floated across the line. Does anyone have recommendations for something like this?
Thanks,
John
time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe send an email to time-nuts-leave@lists.febo.com
Hi
There are several outfits that do very good LiFePO4 chargers. One is Victron. Often the answer is a hybrid inverter/ charger. They aren’t cheap…..
Bob
Sent from my iPhone
> On May 26, 2024, at 4:35 PM, John Ackermann N8UR via time-nuts <time-nuts@lists.febo.com> wrote:
>
> I need to replace the batteries in my 28 VDC power distribution system in the clock room. It's currently two series 12V AGM batteries with an IOTA Engineering float charger.
>
> This system has two purposes: (a) primary power for some OCXOs and other gear; and (b) failover power for some AC/DC gear like HP standards. Under normal conditions, power draw is 2 or 3 amps. During mains outage, it could reach 10 amps. Now that I have a house generator, long run-time isn't a big issue so 25 Ah or so of capacity is plenty.
>
> I haven't explored LiFePo4 batteries until now, and I'm having trouble finding a charger that can provide significant continuous load current while maintaining a battery floated across the line. Does anyone have recommendations for something like this?
>
> Thanks,
> John
> _______________________________________________
> time-nuts mailing list -- time-nuts@lists.febo.com
> To unsubscribe send an email to time-nuts-leave@lists.febo.com
GH
Germán Herrera
Mon, May 27, 2024 12:21 PM
Hi John
Probably a little overkill, but I have good experience with the Mini-Box
OpenUPS boards (the original, one not the OpenUPS2). It can be setup
with multiple cell chemistries, does balancing, has wide input/output
voltage, 6A (10A peak) output current, etc.. Only issue (beside cost) is
that it's switching, so maybe the added noise makes this a no-go.
BR, German
On 2024-05-26 11:39, John Ackermann N8UR via time-nuts wrote:
I need to replace the batteries in my 28 VDC power distribution system
in the clock room. It's currently two series 12V AGM batteries with an
IOTA Engineering float charger.
This system has two purposes: (a) primary power for some OCXOs and
other gear; and (b) failover power for some AC/DC gear like HP
standards. Under normal conditions, power draw is 2 or 3 amps. During
mains outage, it could reach 10 amps. Now that I have a house
generator, long run-time isn't a big issue so 25 Ah or so of capacity
is plenty.
I haven't explored LiFePo4 batteries until now, and I'm having trouble
finding a charger that can provide significant continuous load current
while maintaining a battery floated across the line. Does anyone have
recommendations for something like this?
Thanks,
John
time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe send an email to time-nuts-leave@lists.febo.com
Hi John
Probably a little overkill, but I have good experience with the Mini-Box
OpenUPS boards (the original, one not the OpenUPS2). It can be setup
with multiple cell chemistries, does balancing, has wide input/output
voltage, 6A (10A peak) output current, etc.. Only issue (beside cost) is
that it's switching, so maybe the added noise makes this a no-go.
BR, German
On 2024-05-26 11:39, John Ackermann N8UR via time-nuts wrote:
> I need to replace the batteries in my 28 VDC power distribution system
> in the clock room. It's currently two series 12V AGM batteries with an
> IOTA Engineering float charger.
>
> This system has two purposes: (a) primary power for some OCXOs and
> other gear; and (b) failover power for some AC/DC gear like HP
> standards. Under normal conditions, power draw is 2 or 3 amps. During
> mains outage, it could reach 10 amps. Now that I have a house
> generator, long run-time isn't a big issue so 25 Ah or so of capacity
> is plenty.
>
> I haven't explored LiFePo4 batteries until now, and I'm having trouble
> finding a charger that can provide significant continuous load current
> while maintaining a battery floated across the line. Does anyone have
> recommendations for something like this?
>
> Thanks,
> John
> _______________________________________________
> time-nuts mailing list -- time-nuts@lists.febo.com
> To unsubscribe send an email to time-nuts-leave@lists.febo.com
PS
paul swed
Mon, May 27, 2024 3:38 PM
Good morning to the group. Since this thread started I have been reading
about the LiFePo4 batteries.
They really can be treated much more like a traditional 12V battery in some
respects. It seems they come with a battery management
system internally. Price is easily 3-4X typical batteries. Though honestly
PB batteries are all over the place in cost.
Very hard to compare.
There are youtube videos of LiFePo4 tear downs and those are really
interesting in the wide range of mechanical construction.
By looking at the specs you have no idea what you are buying. Well the same
goes for PB batteries....
John thanks for getting the mind working and relooking at the battery
technology.
Paul
WB8TSL
On Mon, May 27, 2024 at 11:07 AM Germán Herrera via time-nuts <
time-nuts@lists.febo.com> wrote:
Hi John
Probably a little overkill, but I have good experience with the Mini-Box
OpenUPS boards (the original, one not the OpenUPS2). It can be setup
with multiple cell chemistries, does balancing, has wide input/output
voltage, 6A (10A peak) output current, etc.. Only issue (beside cost) is
that it's switching, so maybe the added noise makes this a no-go.
BR, German
On 2024-05-26 11:39, John Ackermann N8UR via time-nuts wrote:
I need to replace the batteries in my 28 VDC power distribution system
in the clock room. It's currently two series 12V AGM batteries with an
IOTA Engineering float charger.
This system has two purposes: (a) primary power for some OCXOs and
other gear; and (b) failover power for some AC/DC gear like HP
standards. Under normal conditions, power draw is 2 or 3 amps. During
mains outage, it could reach 10 amps. Now that I have a house
generator, long run-time isn't a big issue so 25 Ah or so of capacity
is plenty.
I haven't explored LiFePo4 batteries until now, and I'm having trouble
finding a charger that can provide significant continuous load current
while maintaining a battery floated across the line. Does anyone have
recommendations for something like this?
Thanks,
John
time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe send an email to time-nuts-leave@lists.febo.com
Good morning to the group. Since this thread started I have been reading
about the LiFePo4 batteries.
They really can be treated much more like a traditional 12V battery in some
respects. It seems they come with a battery management
system internally. Price is easily 3-4X typical batteries. Though honestly
PB batteries are all over the place in cost.
Very hard to compare.
There are youtube videos of LiFePo4 tear downs and those are really
interesting in the wide range of mechanical construction.
By looking at the specs you have no idea what you are buying. Well the same
goes for PB batteries....
John thanks for getting the mind working and relooking at the battery
technology.
Paul
WB8TSL
On Mon, May 27, 2024 at 11:07 AM Germán Herrera via time-nuts <
time-nuts@lists.febo.com> wrote:
> Hi John
>
> Probably a little overkill, but I have good experience with the Mini-Box
> OpenUPS boards (the original, one not the OpenUPS2). It can be setup
> with multiple cell chemistries, does balancing, has wide input/output
> voltage, 6A (10A peak) output current, etc.. Only issue (beside cost) is
> that it's switching, so maybe the added noise makes this a no-go.
>
> BR, German
>
> On 2024-05-26 11:39, John Ackermann N8UR via time-nuts wrote:
> > I need to replace the batteries in my 28 VDC power distribution system
> > in the clock room. It's currently two series 12V AGM batteries with an
> > IOTA Engineering float charger.
> >
> > This system has two purposes: (a) primary power for some OCXOs and
> > other gear; and (b) failover power for some AC/DC gear like HP
> > standards. Under normal conditions, power draw is 2 or 3 amps. During
> > mains outage, it could reach 10 amps. Now that I have a house
> > generator, long run-time isn't a big issue so 25 Ah or so of capacity
> > is plenty.
> >
> > I haven't explored LiFePo4 batteries until now, and I'm having trouble
> > finding a charger that can provide significant continuous load current
> > while maintaining a battery floated across the line. Does anyone have
> > recommendations for something like this?
> >
> > Thanks,
> > John
> > _______________________________________________
> > time-nuts mailing list -- time-nuts@lists.febo.com
> > To unsubscribe send an email to time-nuts-leave@lists.febo.com
> _______________________________________________
> time-nuts mailing list -- time-nuts@lists.febo.com
> To unsubscribe send an email to time-nuts-leave@lists.febo.com
>