GPS Antenna Grounding/Lightning protection.

DK
Dan Kemppainen
Mon, Jun 18, 2018 6:29 PM

Hi,

I have (or had, I guess) a GPS antenna on a tower that took a lightning
hit yesterday.

You can tell it's going to be a bad day when you walk into your shop,
and smell burnt electronics. Still have to troubleshoot exactly what got
hit, but the GPSDO was flashing no GPS signal, the 5V supply for the
antenna to the GPS splitter was dead, the data logging computer had
rebooted and the data logging computer monitor was dead. Other network
hardware was dead also.

This is a bit surprising since the tower itself is grounded with 4
ground rods and bonded to a 150 foot deep well casing near by. The
antenna is on the end of 250 ft run of RG6. The GPS antenna cable shield
has a grounding block bonded to two ground rods driven down below the
basement foundation where it enters the house. I'm guessing the surge
ran the coax into the splitter, then through everything connected to it,
despite the grounding block.

So, I'm wondering if there are better surge protectors for lightning
protection? Maybe something that actually protect the center conductor
also? Hopefully something that will pass GPS signal reasonably and let
DC power through. If so, can you recommend some starting points? Other
suggestions also welcome.

Also, If you are considering upgrading your own lightning protection,
hopefully this will be some inspiration to get started. As I said
earlier, it's a bad day when you smell burnt electronics in the shop.

Thanks,
Dan

Hi, I have (or had, I guess) a GPS antenna on a tower that took a lightning hit yesterday. You can tell it's going to be a bad day when you walk into your shop, and smell burnt electronics. Still have to troubleshoot exactly what got hit, but the GPSDO was flashing no GPS signal, the 5V supply for the antenna to the GPS splitter was dead, the data logging computer had rebooted and the data logging computer monitor was dead. Other network hardware was dead also. This is a bit surprising since the tower itself is grounded with 4 ground rods and bonded to a 150 foot deep well casing near by. The antenna is on the end of 250 ft run of RG6. The GPS antenna cable shield has a grounding block bonded to two ground rods driven down below the basement foundation where it enters the house. I'm guessing the surge ran the coax into the splitter, then through everything connected to it, despite the grounding block. So, I'm wondering if there are better surge protectors for lightning protection? Maybe something that actually protect the center conductor also? Hopefully something that will pass GPS signal reasonably and let DC power through. If so, can you recommend some starting points? Other suggestions also welcome. Also, If you are considering upgrading your own lightning protection, hopefully this will be some inspiration to get started. As I said earlier, it's a bad day when you smell burnt electronics in the shop. Thanks, Dan
CS
Chris Smith
Mon, Jun 18, 2018 6:38 PM

I have purchased and deployed Huber+Suhner lightning protectors
https://www.hubersuhner.com/en/products/radio-frequency/lightning-emp-protectors/gas-discharge-tube-gdt-protectors
in the past but have thankfully never suffered an actual strike, so I can't
say how well they work under duress.

I've heard it said that basically nothing can protect you from a direct
hit, but again, I haven't had the opportunity to test that theory that you
so recently suffered.

On Mon, Jun 18, 2018 at 2:29 PM, Dan Kemppainen dan@irtelemetrics.com
wrote:

Hi,

I have (or had, I guess) a GPS antenna on a tower that took a lightning
hit yesterday.

You can tell it's going to be a bad day when you walk into your shop, and
smell burnt electronics. Still have to troubleshoot exactly what got hit,
but the GPSDO was flashing no GPS signal, the 5V supply for the antenna to
the GPS splitter was dead, the data logging computer had rebooted and the
data logging computer monitor was dead. Other network hardware was dead
also.

This is a bit surprising since the tower itself is grounded with 4 ground
rods and bonded to a 150 foot deep well casing near by. The antenna is on
the end of 250 ft run of RG6. The GPS antenna cable shield has a grounding
block bonded to two ground rods driven down below the basement foundation
where it enters the house. I'm guessing the surge ran the coax into the
splitter, then through everything connected to it, despite the grounding
block.

So, I'm wondering if there are better surge protectors for lightning
protection? Maybe something that actually protect the center conductor
also? Hopefully something that will pass GPS signal reasonably and let DC
power through. If so, can you recommend some starting points? Other
suggestions also welcome.

Also, If you are considering upgrading your own lightning protection,
hopefully this will be some inspiration to get started. As I said earlier,
it's a bad day when you smell burnt electronics in the shop.

Thanks,
Dan


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to https://lists.febo.com/cgi-bin
/mailman/listinfo/time-nuts
and follow the instructions there.

I have purchased and deployed Huber+Suhner lightning protectors <https://www.hubersuhner.com/en/products/radio-frequency/lightning-emp-protectors/gas-discharge-tube-gdt-protectors> in the past but have thankfully never suffered an actual strike, so I can't say how well they work under duress. I've heard it said that basically nothing can protect you from a direct hit, but again, I haven't had the opportunity to test that theory that you so recently suffered. On Mon, Jun 18, 2018 at 2:29 PM, Dan Kemppainen <dan@irtelemetrics.com> wrote: > Hi, > > I have (or had, I guess) a GPS antenna on a tower that took a lightning > hit yesterday. > > You can tell it's going to be a bad day when you walk into your shop, and > smell burnt electronics. Still have to troubleshoot exactly what got hit, > but the GPSDO was flashing no GPS signal, the 5V supply for the antenna to > the GPS splitter was dead, the data logging computer had rebooted and the > data logging computer monitor was dead. Other network hardware was dead > also. > > This is a bit surprising since the tower itself is grounded with 4 ground > rods and bonded to a 150 foot deep well casing near by. The antenna is on > the end of 250 ft run of RG6. The GPS antenna cable shield has a grounding > block bonded to two ground rods driven down below the basement foundation > where it enters the house. I'm guessing the surge ran the coax into the > splitter, then through everything connected to it, despite the grounding > block. > > So, I'm wondering if there are better surge protectors for lightning > protection? Maybe something that actually protect the center conductor > also? Hopefully something that will pass GPS signal reasonably and let DC > power through. If so, can you recommend some starting points? Other > suggestions also welcome. > > > Also, If you are considering upgrading your own lightning protection, > hopefully this will be some inspiration to get started. As I said earlier, > it's a bad day when you smell burnt electronics in the shop. > > Thanks, > Dan > > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com > To unsubscribe, go to https://lists.febo.com/cgi-bin > /mailman/listinfo/time-nuts > and follow the instructions there. >
G/
Graham / KE9H
Mon, Jun 18, 2018 7:05 PM

If you want to protect your installation from lightening, then there is a
body of information that has been developed within the cellular industry
that allows a properly installed cellular base site to take a direct hit
and continue operating.

An example of what they do is documented in "Motorola R56 2005 manual.pdf"

Google that term to download the document.

It is likely more than most individuals are willing to take on, but you can
see the approach.

In addition to good grounding and common Voltage points, it also involves
making sure that there is not a Voltage differential across the equipment
that you want to protect, during the event.

There is an old folk saying that "Lightning never strikes twice."
Why?
Because it doesn't have to.

--- Graham

==

On Mon, Jun 18, 2018 at 1:39 PM Chris Smith chris.smith@alum.mit.edu
wrote:

in the past but have thankfully never suffered an actual strike, so I can't
say how well they work under duress.

I've heard it said that basically nothing can protect you from a direct
hit, but again, I haven't had the opportunity to test that theory that you
so recently suffered.

On Mon, Jun 18, 2018 at 2:29 PM, Dan Kemppainen dan@irtelemetrics.com
wrote:

Hi,

I have (or had, I guess) a GPS antenna on a tower that took a lightning
hit yesterday.

You can tell it's going to be a bad day when you walk into your shop, and
smell burnt electronics. Still have to troubleshoot exactly what got hit,
but the GPSDO was flashing no GPS signal, the 5V supply for the antenna

to

the GPS splitter was dead, the data logging computer had rebooted and the
data logging computer monitor was dead. Other network hardware was dead
also.

This is a bit surprising since the tower itself is grounded with 4 ground
rods and bonded to a 150 foot deep well casing near by. The antenna is on
the end of 250 ft run of RG6. The GPS antenna cable shield has a

grounding

block bonded to two ground rods driven down below the basement foundation
where it enters the house. I'm guessing the surge ran the coax into the
splitter, then through everything connected to it, despite the grounding
block.

So, I'm wondering if there are better surge protectors for lightning
protection? Maybe something that actually protect the center conductor
also? Hopefully something that will pass GPS signal reasonably and let DC
power through. If so, can you recommend some starting points? Other
suggestions also welcome.

Also, If you are considering upgrading your own lightning protection,
hopefully this will be some inspiration to get started. As I said

earlier,

it's a bad day when you smell burnt electronics in the shop.

Thanks,
Dan


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to https://lists.febo.com/cgi-bin
/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to
https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

If you want to protect your installation from lightening, then there is a body of information that has been developed within the cellular industry that allows a properly installed cellular base site to take a direct hit and continue operating. An example of what they do is documented in "Motorola R56 2005 manual.pdf" Google that term to download the document. It is likely more than most individuals are willing to take on, but you can see the approach. In addition to good grounding and common Voltage points, it also involves making sure that there is not a Voltage differential across the equipment that you want to protect, during the event. There is an old folk saying that "Lightning never strikes twice." Why? Because it doesn't have to. --- Graham == On Mon, Jun 18, 2018 at 1:39 PM Chris Smith <chris.smith@alum.mit.edu> wrote: > I have purchased and deployed Huber+Suhner lightning protectors > < > https://www.hubersuhner.com/en/products/radio-frequency/lightning-emp-protectors/gas-discharge-tube-gdt-protectors > > > in the past but have thankfully never suffered an actual strike, so I can't > say how well they work under duress. > > I've heard it said that basically nothing can protect you from a direct > hit, but again, I haven't had the opportunity to test that theory that you > so recently suffered. > > On Mon, Jun 18, 2018 at 2:29 PM, Dan Kemppainen <dan@irtelemetrics.com> > wrote: > > > Hi, > > > > I have (or had, I guess) a GPS antenna on a tower that took a lightning > > hit yesterday. > > > > You can tell it's going to be a bad day when you walk into your shop, and > > smell burnt electronics. Still have to troubleshoot exactly what got hit, > > but the GPSDO was flashing no GPS signal, the 5V supply for the antenna > to > > the GPS splitter was dead, the data logging computer had rebooted and the > > data logging computer monitor was dead. Other network hardware was dead > > also. > > > > This is a bit surprising since the tower itself is grounded with 4 ground > > rods and bonded to a 150 foot deep well casing near by. The antenna is on > > the end of 250 ft run of RG6. The GPS antenna cable shield has a > grounding > > block bonded to two ground rods driven down below the basement foundation > > where it enters the house. I'm guessing the surge ran the coax into the > > splitter, then through everything connected to it, despite the grounding > > block. > > > > So, I'm wondering if there are better surge protectors for lightning > > protection? Maybe something that actually protect the center conductor > > also? Hopefully something that will pass GPS signal reasonably and let DC > > power through. If so, can you recommend some starting points? Other > > suggestions also welcome. > > > > > > Also, If you are considering upgrading your own lightning protection, > > hopefully this will be some inspiration to get started. As I said > earlier, > > it's a bad day when you smell burnt electronics in the shop. > > > > Thanks, > > Dan > > > > _______________________________________________ > > time-nuts mailing list -- time-nuts@lists.febo.com > > To unsubscribe, go to https://lists.febo.com/cgi-bin > > /mailman/listinfo/time-nuts > > and follow the instructions there. > > > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com > To unsubscribe, go to > https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
O
Oz-in-DFW
Mon, Jun 18, 2018 7:24 PM

Not sure I have much to specific offer, other than some observations.

  1. A path to ground is only a small part of the story.  What's really
    important is the ground reference of all equipment to all other
    equipment. The huge currents and substantial risetimes can cause
    large voltage spikes across even large conductors (>8 AWG.) You want
    everything to stay at the same voltage reference, and you'd really
    like to keep that close enough to ground to prevent arcs from that
    equipment to ground and other equipment.
  2. Long wire runs of even large gauge wire are inductors and can be of
    little value during an event.
  3. No matter what you do, it's unlikely you can do anything within
    economical reason to survive a direct strike and the 10's to 100's
    of kiloamps involved. The real question is how close of a near miss
    can you survive.
  4. Most of the non-telecom smoking fails I've seen have been power line
    transients. If you took a direct tower hit it's more likely than not
    that your RG-6 would now be plating on a tower leg. An old tower can
    be a pretty poor ground for the microseconds (or sometimes
    milliseconds when you consider return strokes) it takes the
    corrosion in the leg joints to flashover and fuse, or resistance
    heat and weld.
  5. The large currents of a direct strike have predictable but less than
    obvious physical effects like conductor shortening (if they don't
    fuse,) and other significant forces caused by magnetic attraction of
    conductors. One failure case I saw years ago collapsed the conduit
    around a ground conductor. Made no sense until we discovered that
    the conduit was the actual ground path. I'll see if I can find the
    pictures.
  6. Even near misses can induce huge currents (kiloamps) on their own,
    particularly in long vertical cable runs.  I've seen solder joints
    in small empty copper water pipes melt and reflow from a strike a
    100 feet away.
  7. The best coax lightning suppression units I have seen are
    essentially 1/4 wave grounded stubs. These are common is cell site
    installations (and the top /AND/ bottom of the lines.) These are
    always at DC ground and the coax is a the weak point (and ultimately
    the fuse.)  I've seen them surplus and at hamfests and some cover
    GPS freqs.
  8. A near strike will induce some really impressive voltages on
    Ethernet cable runs. Most residential buildings are
    electromagnetically transparent and the protection on most Ethernet
    interfaces is oriented toward ESD.

Oz (in DFW)

On 6/18/2018 1:29 PM, Dan Kemppainen wrote:

Hi,

I have (or had, I guess) a GPS antenna on a tower that took a
lightning hit yesterday.

You can tell it's going to be a bad day when you walk into your shop,
and smell burnt electronics. Still have to troubleshoot exactly what
got hit, but the GPSDO was flashing no GPS signal, the 5V supply for
the antenna to the GPS splitter was dead, the data logging computer
had rebooted and the data logging computer monitor was dead. Other
network hardware was dead also.

This is a bit surprising since the tower itself is grounded with 4
ground rods and bonded to a 150 foot deep well casing near by. The
antenna is on the end of 250 ft run of RG6. The GPS antenna cable
shield has a grounding block bonded to two ground rods driven down
below the basement foundation where it enters the house. I'm guessing
the surge ran the coax into the splitter, then through everything
connected to it, despite the grounding block.

So, I'm wondering if there are better surge protectors for lightning
protection? Maybe something that actually protect the center conductor
also? Hopefully something that will pass GPS signal reasonably and let
DC power through. If so, can you recommend some starting points? Other
suggestions also welcome.

Also, If you are considering upgrading your own lightning protection,
hopefully this will be some inspiration to get started. As I said
earlier, it's a bad day when you smell burnt electronics in the shop.

Thanks,
Dan


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to
https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
mailto:oz@ozindfw.net
Oz
POB 93167
Southlake, TX 76092 (Near DFW Airport)

Not sure I have much to specific offer, other than some observations. 1. A path to ground is only a small part of the story.  What's really important is the ground reference of all equipment to all other equipment. The huge currents and substantial risetimes can cause large voltage spikes across even large conductors (>8 AWG.) You want everything to stay at the same voltage reference, and you'd really like to keep that close enough to ground to prevent arcs from that equipment to ground and other equipment. 2. Long wire runs of even large gauge wire are inductors and can be of little value during an event. 3. No matter what you do, it's unlikely you can do anything within economical reason to survive a direct strike and the 10's to 100's of kiloamps involved. The real question is how close of a near miss can you survive. 4. Most of the non-telecom smoking fails I've seen have been power line transients. If you took a direct tower hit it's more likely than not that your RG-6 would now be plating on a tower leg. An old tower can be a pretty poor ground for the microseconds (or sometimes milliseconds when you consider return strokes) it takes the corrosion in the leg joints to flashover and fuse, or resistance heat and weld. 5. The large currents of a direct strike have predictable but less than obvious physical effects like conductor shortening (if they don't fuse,) and other significant forces caused by magnetic attraction of conductors. One failure case I saw years ago collapsed the conduit around a ground conductor. Made no sense until we discovered that the conduit was the actual ground path. I'll see if I can find the pictures. 6. Even near misses can induce huge currents (kiloamps) on their own, particularly in long vertical cable runs.  I've seen solder joints in small empty copper water pipes melt and reflow from a strike a 100 feet away. 7. The best coax lightning suppression units I have seen are essentially 1/4 wave grounded stubs. These are common is cell site installations (and the top /AND/ bottom of the lines.) These are always at DC ground and the coax is a the weak point (and ultimately the fuse.)  I've seen them surplus and at hamfests and some cover GPS freqs. 8. A near strike will induce some really impressive voltages on Ethernet cable runs. Most residential buildings are electromagnetically transparent and the protection on most Ethernet interfaces is oriented toward ESD. Oz (in DFW) On 6/18/2018 1:29 PM, Dan Kemppainen wrote: > Hi, > > I have (or had, I guess) a GPS antenna on a tower that took a > lightning hit yesterday. > > You can tell it's going to be a bad day when you walk into your shop, > and smell burnt electronics. Still have to troubleshoot exactly what > got hit, but the GPSDO was flashing no GPS signal, the 5V supply for > the antenna to the GPS splitter was dead, the data logging computer > had rebooted and the data logging computer monitor was dead. Other > network hardware was dead also. > > This is a bit surprising since the tower itself is grounded with 4 > ground rods and bonded to a 150 foot deep well casing near by. The > antenna is on the end of 250 ft run of RG6. The GPS antenna cable > shield has a grounding block bonded to two ground rods driven down > below the basement foundation where it enters the house. I'm guessing > the surge ran the coax into the splitter, then through everything > connected to it, despite the grounding block. > > So, I'm wondering if there are better surge protectors for lightning > protection? Maybe something that actually protect the center conductor > also? Hopefully something that will pass GPS signal reasonably and let > DC power through. If so, can you recommend some starting points? Other > suggestions also welcome. > > > Also, If you are considering upgrading your own lightning protection, > hopefully this will be some inspiration to get started. As I said > earlier, it's a bad day when you smell burnt electronics in the shop. > > Thanks, > Dan > > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com > To unsubscribe, go to > https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. -- mailto:oz@ozindfw.net Oz POB 93167 Southlake, TX 76092 (Near DFW Airport)
BH
Bill Hawkins
Mon, Jun 18, 2018 9:15 PM

Oz has some useful observations.

I've worked on a 50 foot ocean-going fishing party boat that had a 10
foot aluminum mast on top of the wheel house. That will be the shortest
path to ground on the open sea. The best you can do is to connect a 4"
wide copper strap from the mast to the keel, with as few bends as
possible and none greater than 45 degrees. This seems to work.

I've also worked at a blasting cap plant where 50 foot masts were
erected at both ends of an earth-covered powder magazine. They provide a
"cone of protection" that prevents a direct hit on the magazine. The
mast grounds were measured quarterly with a hand-cranked device
specifically made for ground resistance. It had to be less than 100
milliohms.

But if you really want protection from a direct hit, you must disconnect
the tower device(s) before the storm hits. The coaxial cable must have
only one ground point. The other end should be far from a metallic
ground. You'll probably lose any electronics in the antenna, but there
are far more expensive things in your lab.

You will also have to deal with the electromagnetic pulse, so all of
your equipment, including the computers, must have a common ground
point. This provides a ground plane that can change potential relative
to the Earth without inducing potentials between devices. Every
connection to/from the ground plane must have a surge arrestor. If the
risk of nearby direct hits is high enough, isolate the ground plane from
all external connections before the storm. You'll need battery backup on
the ground plane for all temperature controlled ovens and crystal
oscillators. Maybe the Cs and Rb packages also need to keep running.

It would help to move away from Florida, or high hilltops.

Bill Hawkins

-----Original Message-----
From: time-nuts [mailto:time-nuts-bounces@lists.febo.com] On Behalf Of
Oz-in-DFW
Sent: Monday, June 18, 2018 2:25 PM
To: time-nuts@lists.febo.com
Subject: Re: [time-nuts] GPS Antenna Grounding/Lightning protection.

Not sure I have much to specific offer, other than some observations.

  1. A path to ground is only a small part of the story.  What's really
    important is the ground reference of all equipment to all other
    equipment. The huge currents and substantial risetimes can cause
    large voltage spikes across even large conductors (>8 AWG.) You want
    everything to stay at the same voltage reference, and you'd really
    like to keep that close enough to ground to prevent arcs from that
    equipment to ground and other equipment.
  2. Long wire runs of even large gauge wire are inductors and can be of
    little value during an event.
  3. No matter what you do, it's unlikely you can do anything within
    economical reason to survive a direct strike and the 10's to 100's
    of kiloamps involved. The real question is how close of a near miss
    can you survive.
  4. Most of the non-telecom smoking fails I've seen have been power line
    transients. If you took a direct tower hit it's more likely than not
    that your RG-6 would now be plating on a tower leg. An old tower can
    be a pretty poor ground for the microseconds (or sometimes
    milliseconds when you consider return strokes) it takes the
    corrosion in the leg joints to flashover and fuse, or resistance
    heat and weld.
  5. The large currents of a direct strike have predictable but less than
    obvious physical effects like conductor shortening (if they don't
    fuse,) and other significant forces caused by magnetic attraction of
    conductors. One failure case I saw years ago collapsed the conduit
    around a ground conductor. Made no sense until we discovered that
    the conduit was the actual ground path. I'll see if I can find the
    pictures.
  6. Even near misses can induce huge currents (kiloamps) on their own,
    particularly in long vertical cable runs.  I've seen solder joints
    in small empty copper water pipes melt and reflow from a strike a
    100 feet away.
  7. The best coax lightning suppression units I have seen are
    essentially 1/4 wave grounded stubs. These are common is cell site
    installations (and the top /AND/ bottom of the lines.) These are
    always at DC ground and the coax is a the weak point (and ultimately
    the fuse.)  I've seen them surplus and at hamfests and some cover
    GPS freqs.
  8. A near strike will induce some really impressive voltages on
    Ethernet cable runs. Most residential buildings are
    electromagnetically transparent and the protection on most Ethernet
    interfaces is oriented toward ESD.

Oz (in DFW)

On 6/18/2018 1:29 PM, Dan Kemppainen wrote:

Hi,

I have (or had, I guess) a GPS antenna on a tower that took a
lightning hit yesterday.

You can tell it's going to be a bad day when you walk into your shop,
and smell burnt electronics. Still have to troubleshoot exactly what
got hit, but the GPSDO was flashing no GPS signal, the 5V supply for
the antenna to the GPS splitter was dead, the data logging computer
had rebooted and the data logging computer monitor was dead. Other
network hardware was dead also.

This is a bit surprising since the tower itself is grounded with 4
ground rods and bonded to a 150 foot deep well casing near by. The
antenna is on the end of 250 ft run of RG6. The GPS antenna cable
shield has a grounding block bonded to two ground rods driven down
below the basement foundation where it enters the house. I'm guessing
the surge ran the coax into the splitter, then through everything
connected to it, despite the grounding block.

So, I'm wondering if there are better surge protectors for lightning
protection? Maybe something that actually protect the center conductor

also? Hopefully something that will pass GPS signal reasonably and let

DC power through. If so, can you recommend some starting points? Other

suggestions also welcome.

Also, If you are considering upgrading your own lightning protection,
hopefully this will be some inspiration to get started. As I said
earlier, it's a bad day when you smell burnt electronics in the shop.

Thanks,
Dan


time-nuts mailing list -- time-nuts@lists.febo.com To unsubscribe, go
to https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
mailto:oz@ozindfw.net
Oz
POB 93167
Southlake, TX 76092 (Near DFW Airport)


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to
https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Oz has some useful observations. I've worked on a 50 foot ocean-going fishing party boat that had a 10 foot aluminum mast on top of the wheel house. That will be the shortest path to ground on the open sea. The best you can do is to connect a 4" wide copper strap from the mast to the keel, with as few bends as possible and none greater than 45 degrees. This seems to work. I've also worked at a blasting cap plant where 50 foot masts were erected at both ends of an earth-covered powder magazine. They provide a "cone of protection" that prevents a direct hit on the magazine. The mast grounds were measured quarterly with a hand-cranked device specifically made for ground resistance. It had to be less than 100 milliohms. But if you really want protection from a direct hit, you must disconnect the tower device(s) before the storm hits. The coaxial cable must have only one ground point. The other end should be far from a metallic ground. You'll probably lose any electronics in the antenna, but there are far more expensive things in your lab. You will also have to deal with the electromagnetic pulse, so all of your equipment, including the computers, must have a common ground point. This provides a ground plane that can change potential relative to the Earth without inducing potentials between devices. Every connection to/from the ground plane must have a surge arrestor. If the risk of nearby direct hits is high enough, isolate the ground plane from all external connections before the storm. You'll need battery backup on the ground plane for all temperature controlled ovens and crystal oscillators. Maybe the Cs and Rb packages also need to keep running. It would help to move away from Florida, or high hilltops. Bill Hawkins -----Original Message----- From: time-nuts [mailto:time-nuts-bounces@lists.febo.com] On Behalf Of Oz-in-DFW Sent: Monday, June 18, 2018 2:25 PM To: time-nuts@lists.febo.com Subject: Re: [time-nuts] GPS Antenna Grounding/Lightning protection. Not sure I have much to specific offer, other than some observations. 1. A path to ground is only a small part of the story.  What's really important is the ground reference of all equipment to all other equipment. The huge currents and substantial risetimes can cause large voltage spikes across even large conductors (>8 AWG.) You want everything to stay at the same voltage reference, and you'd really like to keep that close enough to ground to prevent arcs from that equipment to ground and other equipment. 2. Long wire runs of even large gauge wire are inductors and can be of little value during an event. 3. No matter what you do, it's unlikely you can do anything within economical reason to survive a direct strike and the 10's to 100's of kiloamps involved. The real question is how close of a near miss can you survive. 4. Most of the non-telecom smoking fails I've seen have been power line transients. If you took a direct tower hit it's more likely than not that your RG-6 would now be plating on a tower leg. An old tower can be a pretty poor ground for the microseconds (or sometimes milliseconds when you consider return strokes) it takes the corrosion in the leg joints to flashover and fuse, or resistance heat and weld. 5. The large currents of a direct strike have predictable but less than obvious physical effects like conductor shortening (if they don't fuse,) and other significant forces caused by magnetic attraction of conductors. One failure case I saw years ago collapsed the conduit around a ground conductor. Made no sense until we discovered that the conduit was the actual ground path. I'll see if I can find the pictures. 6. Even near misses can induce huge currents (kiloamps) on their own, particularly in long vertical cable runs.  I've seen solder joints in small empty copper water pipes melt and reflow from a strike a 100 feet away. 7. The best coax lightning suppression units I have seen are essentially 1/4 wave grounded stubs. These are common is cell site installations (and the top /AND/ bottom of the lines.) These are always at DC ground and the coax is a the weak point (and ultimately the fuse.)  I've seen them surplus and at hamfests and some cover GPS freqs. 8. A near strike will induce some really impressive voltages on Ethernet cable runs. Most residential buildings are electromagnetically transparent and the protection on most Ethernet interfaces is oriented toward ESD. Oz (in DFW) On 6/18/2018 1:29 PM, Dan Kemppainen wrote: > Hi, > > I have (or had, I guess) a GPS antenna on a tower that took a > lightning hit yesterday. > > You can tell it's going to be a bad day when you walk into your shop, > and smell burnt electronics. Still have to troubleshoot exactly what > got hit, but the GPSDO was flashing no GPS signal, the 5V supply for > the antenna to the GPS splitter was dead, the data logging computer > had rebooted and the data logging computer monitor was dead. Other > network hardware was dead also. > > This is a bit surprising since the tower itself is grounded with 4 > ground rods and bonded to a 150 foot deep well casing near by. The > antenna is on the end of 250 ft run of RG6. The GPS antenna cable > shield has a grounding block bonded to two ground rods driven down > below the basement foundation where it enters the house. I'm guessing > the surge ran the coax into the splitter, then through everything > connected to it, despite the grounding block. > > So, I'm wondering if there are better surge protectors for lightning > protection? Maybe something that actually protect the center conductor > also? Hopefully something that will pass GPS signal reasonably and let > DC power through. If so, can you recommend some starting points? Other > suggestions also welcome. > > > Also, If you are considering upgrading your own lightning protection, > hopefully this will be some inspiration to get started. As I said > earlier, it's a bad day when you smell burnt electronics in the shop. > > Thanks, > Dan > > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com To unsubscribe, go > to https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. -- mailto:oz@ozindfw.net Oz POB 93167 Southlake, TX 76092 (Near DFW Airport) _______________________________________________ time-nuts mailing list -- time-nuts@lists.febo.com To unsubscribe, go to https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts and follow the instructions there.
CS
Charles Steinmetz
Mon, Jun 18, 2018 9:51 PM

Graham wrote:

If you want to protect your installation from lightening, then there is a
body of information that has been developed within the cellular industry
that allows a properly installed cellular base site to take a direct hit
and continue operating.

An example of what they do is documented in "Motorola R56 2005 manual.pdf"

Google that term to download the document.

Oz and Bill also provided good information.

PolyPhaser is the generally-accepted gold standard for lightning
protection, and has many technical notes available.

Tisha Hayes has a big fat folder full of good stuff relating to
"Grounding Surge and Filtering" at her dropbox site, and another one
full of "Transient Protection Documents."  See:

https://www.dropbox.com/sh/qjnu6cp03ahajpc/AAABcWVmOZdyPWquiz3az58Ha?dl=0

Best regards,

Charles

Graham wrote: > If you want to protect your installation from lightening, then there is a > body of information that has been developed within the cellular industry > that allows a properly installed cellular base site to take a direct hit > and continue operating. > > An example of what they do is documented in "Motorola R56 2005 manual.pdf" > > Google that term to download the document. Oz and Bill also provided good information. PolyPhaser is the generally-accepted gold standard for lightning protection, and has many technical notes available. Tisha Hayes has a big fat folder full of good stuff relating to "Grounding Surge and Filtering" at her dropbox site, and another one full of "Transient Protection Documents." See: <https://www.dropbox.com/sh/qjnu6cp03ahajpc/AAABcWVmOZdyPWquiz3az58Ha?dl=0> Best regards, Charles
GL
Glenn Little WB4UIV
Tue, Jun 19, 2018 1:39 AM

Unless all of your ground rods are bonded together, you are inviting
disaster.

If you have two ground systems, one at the tower and the other at the
house, you have a very dangerous situation.

If you have a unified (bonded) ground system and take a lightning strike
every thing elevates to to same level, be it 10 Volts or 100 KV.
There is no difference in potential between equipments and everything is
happy.
If there are two ground systems, they will not elevate to the same level
at the same rate.
In this case, you have differences in potential between equipments and
damage.

MIL-HDBL-419 is a very good grounding reference and is available for
free download.

To do the grounding correctly, all connections exterior to the building
are to be welded.
The cable to ground rod welds are to be 18 inches below grade.
The exterior cable is to be number 2 copper or larger.
To bond numerous ground systems together, a number 2 copper cable is to
be buried at 18 inches and welded to each ground system.
If using eight foot ground rods, a ground rod is to be driven every 16
feet along the connecting cable and the cable welded to the rod.

I did lightning mitigation for seven years for a tower site monitoring
company.
When these steps were followed, lightning damage was very minimal or
non-existent.

You stated that the GPS antenna was on a tower.
To correctly install an antenna on a tower the feedline is to be bonded
to the tower near the base of the antenna.
The feedline is again bonded to the tower where to leaves the tower
heading for the building.
Prior to entering the building, the feedline is bonded to a copper plate
called a ground window.
This ground window is bonded to the ground system.
The feedline goes through a surge suppressor the is bonded to the ground
window prior to entering the building.

All equipment in the building should be bonded to a ground buss made of
number 6 copper and bonded to the ground window.

A lot of work, but, cheaper, in the long run, than continuing to
repair/replace equipment.

73
Glenn
WB4UIV

On 6/18/2018 2:29 PM, Dan Kemppainen wrote:

Hi,

I have (or had, I guess) a GPS antenna on a tower that took a
lightning hit yesterday.

You can tell it's going to be a bad day when you walk into your shop,
and smell burnt electronics. Still have to troubleshoot exactly what
got hit, but the GPSDO was flashing no GPS signal, the 5V supply for
the antenna to the GPS splitter was dead, the data logging computer
had rebooted and the data logging computer monitor was dead. Other
network hardware was dead also.

This is a bit surprising since the tower itself is grounded with 4
ground rods and bonded to a 150 foot deep well casing near by. The
antenna is on the end of 250 ft run of RG6. The GPS antenna cable
shield has a grounding block bonded to two ground rods driven down
below the basement foundation where it enters the house. I'm guessing
the surge ran the coax into the splitter, then through everything
connected to it, despite the grounding block.

So, I'm wondering if there are better surge protectors for lightning
protection? Maybe something that actually protect the center conductor
also? Hopefully something that will pass GPS signal reasonably and let
DC power through. If so, can you recommend some starting points? Other
suggestions also welcome.

Also, If you are considering upgrading your own lightning protection,
hopefully this will be some inspiration to get started. As I said
earlier, it's a bad day when you smell burnt electronics in the shop.

Thanks,
Dan


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to
https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--

Glenn Little                ARRL Technical Specialist  QCWA  LM 28417
Amateur Callsign:  WB4UIV            wb4uiv@arrl.net    AMSAT LM 2178
QTH:  Goose Creek, SC USA (EM92xx)  USSVI LM  NRA LM  SBE ARRL TAPR
"It is not the class of license that the Amateur holds but the class
of the Amateur that holds the license"

Unless all of your ground rods are bonded together, you are inviting disaster. If you have two ground systems, one at the tower and the other at the house, you have a very dangerous situation. If you have a unified (bonded) ground system and take a lightning strike every thing elevates to to same level, be it 10 Volts or 100 KV. There is no difference in potential between equipments and everything is happy. If there are two ground systems, they will not elevate to the same level at the same rate. In this case, you have differences in potential between equipments and damage. MIL-HDBL-419 is a very good grounding reference and is available for free download. To do the grounding correctly, all connections exterior to the building are to be welded. The cable to ground rod welds are to be 18 inches below grade. The exterior cable is to be number 2 copper or larger. To bond numerous ground systems together, a number 2 copper cable is to be buried at 18 inches and welded to each ground system. If using eight foot ground rods, a ground rod is to be driven every 16 feet along the connecting cable and the cable welded to the rod. I did lightning mitigation for seven years for a tower site monitoring company. When these steps were followed, lightning damage was very minimal or non-existent. You stated that the GPS antenna was on a tower. To correctly install an antenna on a tower the feedline is to be bonded to the tower near the base of the antenna. The feedline is again bonded to the tower where to leaves the tower heading for the building. Prior to entering the building, the feedline is bonded to a copper plate called a ground window. This ground window is bonded to the ground system. The feedline goes through a surge suppressor the is bonded to the ground window prior to entering the building. All equipment in the building should be bonded to a ground buss made of number 6 copper and bonded to the ground window. A lot of work, but, cheaper, in the long run, than continuing to repair/replace equipment. 73 Glenn WB4UIV On 6/18/2018 2:29 PM, Dan Kemppainen wrote: > Hi, > > I have (or had, I guess) a GPS antenna on a tower that took a > lightning hit yesterday. > > You can tell it's going to be a bad day when you walk into your shop, > and smell burnt electronics. Still have to troubleshoot exactly what > got hit, but the GPSDO was flashing no GPS signal, the 5V supply for > the antenna to the GPS splitter was dead, the data logging computer > had rebooted and the data logging computer monitor was dead. Other > network hardware was dead also. > > This is a bit surprising since the tower itself is grounded with 4 > ground rods and bonded to a 150 foot deep well casing near by. The > antenna is on the end of 250 ft run of RG6. The GPS antenna cable > shield has a grounding block bonded to two ground rods driven down > below the basement foundation where it enters the house. I'm guessing > the surge ran the coax into the splitter, then through everything > connected to it, despite the grounding block. > > So, I'm wondering if there are better surge protectors for lightning > protection? Maybe something that actually protect the center conductor > also? Hopefully something that will pass GPS signal reasonably and let > DC power through. If so, can you recommend some starting points? Other > suggestions also welcome. > > > Also, If you are considering upgrading your own lightning protection, > hopefully this will be some inspiration to get started. As I said > earlier, it's a bad day when you smell burnt electronics in the shop. > > Thanks, > Dan > > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com > To unsubscribe, go to > https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > -- ----------------------------------------------------------------------- Glenn Little ARRL Technical Specialist QCWA LM 28417 Amateur Callsign: WB4UIV wb4uiv@arrl.net AMSAT LM 2178 QTH: Goose Creek, SC USA (EM92xx) USSVI LM NRA LM SBE ARRL TAPR "It is not the class of license that the Amateur holds but the class of the Amateur that holds the license"
SM
Scott McGrath
Tue, Jun 19, 2018 2:21 AM

You might want to look at your grounding system.  Your tower ground is probably not connected to your building ground.  So when a nearby strike occurred there was a potential difference between your grounds and a current flowed as a result.

My house/shack/tower is within a ‘halo’ ground with rods every 20’ or so this means in the event of a nearby strike all grounds are at SAME potential.    And yes during intense storms i do see ‘St Elmo’s Fire’ up on the tower which tells me system is working as intended by preventing potential buildup.

Content by Scott
Typos by Siri

On Jun 18, 2018, at 2:38 PM, Chris Smith chris.smith@alum.mit.edu wrote:

I have purchased and deployed Huber+Suhner lightning protectors
https://www.hubersuhner.com/en/products/radio-frequency/lightning-emp-protectors/gas-discharge-tube-gdt-protectors
in the past but have thankfully never suffered an actual strike, so I can't
say how well they work under duress.

I've heard it said that basically nothing can protect you from a direct
hit, but again, I haven't had the opportunity to test that theory that you
so recently suffered.

On Mon, Jun 18, 2018 at 2:29 PM, Dan Kemppainen dan@irtelemetrics.com
wrote:

Hi,

I have (or had, I guess) a GPS antenna on a tower that took a lightning
hit yesterday.

You can tell it's going to be a bad day when you walk into your shop, and
smell burnt electronics. Still have to troubleshoot exactly what got hit,
but the GPSDO was flashing no GPS signal, the 5V supply for the antenna to
the GPS splitter was dead, the data logging computer had rebooted and the
data logging computer monitor was dead. Other network hardware was dead
also.

This is a bit surprising since the tower itself is grounded with 4 ground
rods and bonded to a 150 foot deep well casing near by. The antenna is on
the end of 250 ft run of RG6. The GPS antenna cable shield has a grounding
block bonded to two ground rods driven down below the basement foundation
where it enters the house. I'm guessing the surge ran the coax into the
splitter, then through everything connected to it, despite the grounding
block.

So, I'm wondering if there are better surge protectors for lightning
protection? Maybe something that actually protect the center conductor
also? Hopefully something that will pass GPS signal reasonably and let DC
power through. If so, can you recommend some starting points? Other
suggestions also welcome.

Also, If you are considering upgrading your own lightning protection,
hopefully this will be some inspiration to get started. As I said earlier,
it's a bad day when you smell burnt electronics in the shop.

Thanks,
Dan


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to https://lists.febo.com/cgi-bin
/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

You might want to look at your grounding system. Your tower ground is probably not connected to your building ground. So when a nearby strike occurred there was a potential difference between your grounds and a current flowed as a result. My house/shack/tower is within a ‘halo’ ground with rods every 20’ or so this means in the event of a nearby strike all grounds are at SAME potential. And yes during intense storms i do see ‘St Elmo’s Fire’ up on the tower which tells me system is working as intended by preventing potential buildup. Content by Scott Typos by Siri On Jun 18, 2018, at 2:38 PM, Chris Smith <chris.smith@alum.mit.edu> wrote: I have purchased and deployed Huber+Suhner lightning protectors <https://www.hubersuhner.com/en/products/radio-frequency/lightning-emp-protectors/gas-discharge-tube-gdt-protectors> in the past but have thankfully never suffered an actual strike, so I can't say how well they work under duress. I've heard it said that basically nothing can protect you from a direct hit, but again, I haven't had the opportunity to test that theory that you so recently suffered. On Mon, Jun 18, 2018 at 2:29 PM, Dan Kemppainen <dan@irtelemetrics.com> wrote: > Hi, > > I have (or had, I guess) a GPS antenna on a tower that took a lightning > hit yesterday. > > You can tell it's going to be a bad day when you walk into your shop, and > smell burnt electronics. Still have to troubleshoot exactly what got hit, > but the GPSDO was flashing no GPS signal, the 5V supply for the antenna to > the GPS splitter was dead, the data logging computer had rebooted and the > data logging computer monitor was dead. Other network hardware was dead > also. > > This is a bit surprising since the tower itself is grounded with 4 ground > rods and bonded to a 150 foot deep well casing near by. The antenna is on > the end of 250 ft run of RG6. The GPS antenna cable shield has a grounding > block bonded to two ground rods driven down below the basement foundation > where it enters the house. I'm guessing the surge ran the coax into the > splitter, then through everything connected to it, despite the grounding > block. > > So, I'm wondering if there are better surge protectors for lightning > protection? Maybe something that actually protect the center conductor > also? Hopefully something that will pass GPS signal reasonably and let DC > power through. If so, can you recommend some starting points? Other > suggestions also welcome. > > > Also, If you are considering upgrading your own lightning protection, > hopefully this will be some inspiration to get started. As I said earlier, > it's a bad day when you smell burnt electronics in the shop. > > Thanks, > Dan > > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com > To unsubscribe, go to https://lists.febo.com/cgi-bin > /mailman/listinfo/time-nuts > and follow the instructions there. > _______________________________________________ time-nuts mailing list -- time-nuts@lists.febo.com To unsubscribe, go to https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts and follow the instructions there.
SM
Scott McGrath
Tue, Jun 19, 2018 2:27 AM

Also see this

https://www.bicsi.org/uploadedfiles/bicsi_conferences/fall/2012/presentations/CONCSES_4C.pdf

Content by Scott
Typos by Siri

On Jun 18, 2018, at 5:51 PM, Charles Steinmetz csteinmetz@yandex.com wrote:

Graham wrote:

If you want to protect your installation from lightening, then there is a
body of information that has been developed within the cellular industry
that allows a properly installed cellular base site to take a direct hit
and continue operating.

An example of what they do is documented in "Motorola R56 2005 manual.pdf"

Google that term to download the document.

Oz and Bill also provided good information.

PolyPhaser is the generally-accepted gold standard for lightning protection, and has many technical notes available.

Tisha Hayes has a big fat folder full of good stuff relating to "Grounding Surge and Filtering" at her dropbox site, and another one full of "Transient Protection Documents."  See:

https://www.dropbox.com/sh/qjnu6cp03ahajpc/AAABcWVmOZdyPWquiz3az58Ha?dl=0

Best regards,

Charles


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Also see this https://www.bicsi.org/uploadedfiles/bicsi_conferences/fall/2012/presentations/CONCSES_4C.pdf Content by Scott Typos by Siri On Jun 18, 2018, at 5:51 PM, Charles Steinmetz <csteinmetz@yandex.com> wrote: Graham wrote: > If you want to protect your installation from lightening, then there is a > body of information that has been developed within the cellular industry > that allows a properly installed cellular base site to take a direct hit > and continue operating. > > An example of what they do is documented in "Motorola R56 2005 manual.pdf" > > Google that term to download the document. Oz and Bill also provided good information. PolyPhaser is the generally-accepted gold standard for lightning protection, and has many technical notes available. Tisha Hayes has a big fat folder full of good stuff relating to "Grounding Surge and Filtering" at her dropbox site, and another one full of "Transient Protection Documents." See: <https://www.dropbox.com/sh/qjnu6cp03ahajpc/AAABcWVmOZdyPWquiz3az58Ha?dl=0> Best regards, Charles _______________________________________________ time-nuts mailing list -- time-nuts@lists.febo.com To unsubscribe, go to https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts and follow the instructions there.
J
jimlux
Tue, Jun 19, 2018 2:50 PM

On 6/18/18 6:39 PM, Glenn Little WB4UIV wrote:

To do the grounding correctly, all connections exterior to the building
are to be welded.
The cable to ground rod welds are to be 18 inches below grade.
The exterior cable is to be number 2 copper or larger.
To bond numerous ground systems together, a number 2 copper cable is to
be buried at 18 inches and welded to each ground system.
If using eight foot ground rods, a ground rod is to be driven every 16
feet along the connecting cable and the cable welded to the rod.

It helps to know why some requirements exist - I suspect the 18"
burial requirement is to avoid accidentally digging it up or damaging
it. I can't think of an electrical reason for it.

A lot of work, but, cheaper, in the long run, than continuing to
repair/replace equipment.

It depends

Unless you're doing geodetic or precision timing work with a 2 or 3 band
GPS, replacement GPS antennas are cheap.
I'd worry about the receiver and related equipment, but the antenna
itself might be sacrificial.

As always, there's a risk/budget tradeoff

On 6/18/18 6:39 PM, Glenn Little WB4UIV wrote: > > To do the grounding correctly, all connections exterior to the building > are to be welded. > The cable to ground rod welds are to be 18 inches below grade. > The exterior cable is to be number 2 copper or larger. > To bond numerous ground systems together, a number 2 copper cable is to > be buried at 18 inches and welded to each ground system. > If using eight foot ground rods, a ground rod is to be driven every 16 > feet along the connecting cable and the cable welded to the rod. It helps to know *why* some requirements exist - I suspect the 18" burial requirement is to avoid accidentally digging it up or damaging it. I can't think of an electrical reason for it. > > A lot of work, but, cheaper, in the long run, than continuing to > repair/replace equipment. It depends Unless you're doing geodetic or precision timing work with a 2 or 3 band GPS, replacement GPS antennas are cheap. I'd worry about the receiver and related equipment, but the antenna itself might be sacrificial. As always, there's a risk/budget tradeoff