I've also seen inverter systems that are designed for stand by power use in service at commercial sites in third world countries.  Within reason they basically let you run what ever reasonable arrangement of rechargeable lead acid based batteries you want that will supply the required voltage and current.  They handle the conversion of dc to ac and the switch over from commercial to inverter power.  They usually also feature a basic battery charger with settings to charge various types of batteries (ie, gel or conventional lead acid.)

Typically I've seen them used with a number of automotive style batteries.

The users would need to sort out the necessary cables, fuses, batteries, deal with safety considerations etc.

I've never seen these devices in Canada or the U.S.  Sort of a value engineered UPS system for price conscious markets.  Might be a nice starting point for those who want to role their own system and can deal with the safety aspects of this.  I'm not sure what the transfer time from utility to inverter power would be.

In the U.S. and Canada the typical practice seems to be to use packaged UPS systems that include their own batteries.

Sent from my iPhone

On Oct 11, 2015, at 10:36 AM, Bob Benward rbenward@verizon.net wrote:

Dave,
You could use a 120V relay and switch the high capacity battery from its own
charger to the battery pack in the UPS.  When power comes back, the relay
automatically switches the battery out and back to its own charger.

Bob

-----Original Message-----
From: time-nuts [mailto:time-nuts-bounces@febo.com] On Behalf Of Dr.
David Kirkby (Kirkby Microwave Ltd)
Sent: Saturday, October 10, 2015 6:07 PM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] UPS for my time rack

On 10 October 2015 at 14:20, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my
Thunderbolt, the laptop that runs Lady Heather, and frequency counter.

There's one issue with them that I don't see anyone mention.

I was thinking of doing the same a while back, and intended getting a

UPS

and adding a large external battery pack, so if the mains failed late at

night, I

could run the GPS receiver and a few other things overnight, and

consider

starting the generator in the morning.  I contacted a dealer on eBay,

who

specilaises in UPSs. He told me that the smaller units with built in

batteries

will die if you put large external batteries on them.
Essentially the charging circuits are not designed to run as long as

needed to

charge big batteries. Even on ones designed for external batteries,

there's a

recommended limit on the size of them. So if you think you might want to
increase runtime by adding some batteries, buy one designed for that

service.

I've had two here which were HP/Compaq 5 kW units. These were different
to the normal, in that the batteries added up to over 300 V, so could

produce

240 VAC with no need to step it up. Both these blew up on me, for

reasons I

never worked out. The load was never anywhere near 5 kW.

Lots of people mention sine wave. Of course, if you keen enough, you

could

make a class A amplifier and sine wave oscillator. The problem is that

the

pure sine wave inverters tend to be very inefficient.

As with most things, there are a lot of things to balance - runtime,

cost,

quality of output, audio noise, RFI  etc etc.

Dave


time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.6140 / Virus Database: 4435/10788 - Release Date:
10/09/15


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

I've also seen inverter systems that are designed for stand by power use in service at commercial sites in third world countries. Within reason they basically let you run what ever reasonable arrangement of rechargeable lead acid based batteries you want that will supply the required voltage and current. They handle the conversion of dc to ac and the switch over from commercial to inverter power. They usually also feature a basic battery charger with settings to charge various types of batteries (ie, gel or conventional lead acid.) Typically I've seen them used with a number of automotive style batteries. The users would need to sort out the necessary cables, fuses, batteries, deal with safety considerations etc. I've never seen these devices in Canada or the U.S. Sort of a value engineered UPS system for price conscious markets. Might be a nice starting point for those who want to role their own system and can deal with the safety aspects of this. I'm not sure what the transfer time from utility to inverter power would be. In the U.S. and Canada the typical practice seems to be to use packaged UPS systems that include their own batteries. Sent from my iPhone > On Oct 11, 2015, at 10:36 AM, Bob Benward <rbenward@verizon.net> wrote: > > Dave, > You could use a 120V relay and switch the high capacity battery from its own > charger to the battery pack in the UPS. When power comes back, the relay > automatically switches the battery out and back to its own charger. > > Bob > >>>> -----Original Message----- >>>> From: time-nuts [mailto:time-nuts-bounces@febo.com] On Behalf Of Dr. >>>> David Kirkby (Kirkby Microwave Ltd) >>>> Sent: Saturday, October 10, 2015 6:07 PM >>>> To: Discussion of precise time and frequency measurement >>>> Subject: Re: [time-nuts] UPS for my time rack >>>> >>>>> On 10 October 2015 at 14:20, Chris Waldrup <kd4pbj@gmail.com> wrote: >>>>> >>>>> Hi, >>>>> >>>>> >>>>> I have decided I'd like to get a UPS to put on the rack containing my >>>>> Thunderbolt, the laptop that runs Lady Heather, and frequency counter. >>>> >>>> There's one issue with them that I don't see anyone mention. >>>> >>>> I was thinking of doing the same a while back, and intended getting a > UPS >>>> and adding a large external battery pack, so if the mains failed late at > night, I >>>> could run the GPS receiver and a few other things overnight, and > consider >>>> starting the generator in the morning. I contacted a dealer on eBay, > who >>>> specilaises in UPSs. He told me that the smaller units with built in > batteries >>>> will die if you put large external batteries on them. >>>> Essentially the charging circuits are not designed to run as long as > needed to >>>> charge big batteries. Even on ones designed for external batteries, > there's a >>>> recommended limit on the size of them. So if you think you might want to >>>> increase runtime by adding some batteries, buy one designed for that > service. >>>> >>>> I've had two here which were HP/Compaq 5 kW units. These were different >>>> to the normal, in that the batteries added up to over 300 V, so could > produce >>>> 240 VAC with no need to step it up. Both these blew up on me, for > reasons I >>>> never worked out. The load was never anywhere near 5 kW. >>>> >>>> Lots of people mention sine wave. Of course, if you keen enough, you > could >>>> make a class A amplifier and sine wave oscillator. The problem is that > the >>>> pure sine wave inverters tend to be very inefficient. >>>> >>>> As with most things, there are a lot of things to balance - runtime, > cost, >>>> quality of output, audio noise, RFI etc etc. >>>> >>>> Dave >>>> _______________________________________________ >>>> time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to >>>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>>> and follow the instructions there. >>>> ----- >>>> No virus found in this message. >>>> Checked by AVG - www.avg.com >>>> Version: 2015.0.6140 / Virus Database: 4435/10788 - Release Date: >>>> 10/09/15 > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
MS
Mark Spencer
Sun, Oct 11, 2015 8:22 PM

I'm fortunate that several of pieces of my time nuts gear (including two of my ocxo's) feature backup 24 volt dc power inputs.  They were the only things in my house that stayed running during a recent 2 day power outage while I was away.

I have two large 12 volt gel cells in series that I re charge from time to time with a power supply via a blocking diode.

I agree about the importance of the fusing.  I've also found it's easy to buy fuses rated to work on 12 and 24 volt dc systems, fuses for 48 volt and higher dc systems are harder to find.

I also bolt the fuses directly to the battery terminals.

Sent from my iPhone

On Oct 10, 2015, at 9:31 AM, Alex Pummer alex@pcscons.com wrote:

for a very similar application I am using a solar panel to charge the battery, but I have a vented NiFe battery, which is not sensitive of over charging or deep discharging, and has almost unlimited life time -- I have seen some in forklifts which were 60 years old and working...
73
KJ6UHN
Alex

On 10/10/2015 7:14 AM, Poul-Henning Kamp wrote:

In message 1444483218108.6a07c91c@Nodemailer, "Chris Waldrup" writes:

Has anyone had bad experience noise wise with the APC brand units
like are available on Amazon and at Staples? I'd like to get one
that doesn't generate lots of RFI. Thank you.

Then don't.

Instead get 12 or 24 Volt sealed lead-acid batteries and a good
float-charger, and run your stuff from that.

You avoid a lot of conversion losses, and you get to decide what
quality batteries you want (As opposed to "the cheapest we can get
away with") and you get to decide how long hold-up time you want.

The important tricks are:

  1. ATO Fuse RIGHT NEXT TO THE BATTERY.  Not a meter away, but
    quite literally bolted right onto the terminal.

  2. Don't buy a shit charger, it will cost you battery life.

  3. Suitably sized fuse/polyfuses on all loads.

  4. Either put 0.010 Ohm current shunts in all over the place
    or buy a 1mA resolution clamp meter and prepare the wiring
    for measurement.

And that's it really...

I run all the always-on stuff in my lab from two 12V/105Ah telco-grade
sealed lead-acid batteries, and I'll never look back.

Presenty the load is 6.7A @ 24V, and that powers my ADSL lines,
firewalls (soekris), home server (ITX with mini-box.com PSU),
emergency lights (LED strips), GPS, GPSDO, HP5065 etc. etc.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

I'm fortunate that several of pieces of my time nuts gear (including two of my ocxo's) feature backup 24 volt dc power inputs. They were the only things in my house that stayed running during a recent 2 day power outage while I was away. I have two large 12 volt gel cells in series that I re charge from time to time with a power supply via a blocking diode. I agree about the importance of the fusing. I've also found it's easy to buy fuses rated to work on 12 and 24 volt dc systems, fuses for 48 volt and higher dc systems are harder to find. I also bolt the fuses directly to the battery terminals. Sent from my iPhone > On Oct 10, 2015, at 9:31 AM, Alex Pummer <alex@pcscons.com> wrote: > > for a very similar application I am using a solar panel to charge the battery, but I have a vented NiFe battery, which is not sensitive of over charging or deep discharging, and has almost unlimited life time -- I have seen some in forklifts which were 60 years old and working... > 73 > KJ6UHN > Alex > > > >> On 10/10/2015 7:14 AM, Poul-Henning Kamp wrote: >> -------- >> In message <1444483218108.6a07c91c@Nodemailer>, "Chris Waldrup" writes: >> >> >>> Has anyone had bad experience noise wise with the APC brand units >>> like are available on Amazon and at Staples? I'd like to get one >>> that doesn't generate lots of RFI. Thank you. >> Then don't. >> >> Instead get 12 or 24 Volt sealed lead-acid batteries and a good >> float-charger, and run your stuff from that. >> >> You avoid a lot of conversion losses, and you get to decide what >> quality batteries you want (As opposed to "the cheapest we can get >> away with") and you get to decide how long hold-up time you want. >> >> The important tricks are: >> >> 1. ATO Fuse *RIGHT NEXT TO THE BATTERY*. Not a meter away, but >> quite literally bolted right onto the terminal. >> >> 2. Don't buy a shit charger, it will cost you battery life. >> >> 3. Suitably sized fuse/polyfuses on all loads. >> >> 4. Either put 0.010 Ohm current shunts in all over the place >> or buy a 1mA resolution clamp meter and prepare the wiring >> for measurement. >> >> And that's it really... >> >> I run all the always-on stuff in my lab from two 12V/105Ah telco-grade >> sealed lead-acid batteries, and I'll never look back. >> >> Presenty the load is 6.7A @ 24V, and that powers my ADSL lines, >> firewalls (soekris), home server (ITX with mini-box.com PSU), >> emergency lights (LED strips), GPS, GPSDO, HP5065 etc. etc. > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
JH
Jim Harman
Sun, Oct 11, 2015 8:54 PM

On Sat, Oct 10, 2015 at 9:20 AM, Chris Waldrup kd4pbj@gmail.com wrote:

Has anyone had bad experience noise wise with the APC brand units like are
available on Amazon and at Staples? I'd like to get one that doesn't
generate lots of RFI.

I have an inexpensive CyberPower 825 AVR UPS, The UPS does the job of
keeping my computer and time-nuts gear running, but it causes an annoying
amount of RFI in the AM broadcast band. The noise is radiated from the
circuit that feeds the UPS. I found that plugging the UPS into a Belkin
outlet strip, which presumably includes some line filtering,reduced the
interference significantly.

--

--Jim Harman

On Sat, Oct 10, 2015 at 9:20 AM, Chris Waldrup <kd4pbj@gmail.com> wrote: > Has anyone had bad experience noise wise with the APC brand units like are > available on Amazon and at Staples? I'd like to get one that doesn't > generate lots of RFI. I have an inexpensive CyberPower 825 AVR UPS, The UPS does the job of keeping my computer and time-nuts gear running, but it causes an annoying amount of RFI in the AM broadcast band. The noise is radiated from the circuit that feeds the UPS. I found that plugging the UPS into a Belkin outlet strip, which presumably includes some line filtering,reduced the interference significantly. -- --Jim Harman
MS
Mark Spencer
Sun, Oct 11, 2015 8:58 PM

Yes this is a complex topic.  At one point in my career when I was responsible for the up time of several data centres for a high tech firm I had an Electrical Engineer on my team to (amongst other roles) work thru the various issues pertaining to UPS systems.  I recall there were significant differences between the various UPS designs.

Getting out of high tech and into an industry where data centres were out sourced was a nice change for me (:

To relate this to time nuts, those of us looking at making significant investments in this type of equipment would do well to seek out the advice of those who are knowledgable.

Sent from my iPhone

On Oct 10, 2015, at 7:51 AM, Bob Camp kb8tq@n1k.org wrote:

Hi

All of the UPS vendors these days make a wide range of products. They range from
low cost to mighty expensive. They also range a bit in terms of performance. Finding out
exactly what this or that model does do can be a major pain. The marketing guys apparently
don’t want you to figure out that the low cost gizmo does not have all the performance
of the one that costs 5 times as much.

First thing to avoid - the pure square wave output versions. These may or may not
generate RFI in this or that UHF band. They will take out big chunks of HF and mess up 10 MHz
distribution. I suspect that the filters on some are better than the filters on others. The bigger issue
is that they do not play nice with modern power factor corrected power supplies. These supplies
seem to expect a sine wave and a (possibly ringing) square wave may get them confused.

Next thing to avoid - The stepped square wave / modified square wave versions. Theses aren’t
quite as bad as the centuries old square wave units. It’s more likely you will find these than a
pure square. They still have the same issues on RFI. They may or may not antagonize a PFC
supply to the same extent.

The target is a “pure sine wave” output. That keeps a PFC supply happy. As with any verbal spec,
“pure” likely has a few qualifiers on it. It’s not guaranteed to take out the RFI. It at least will reduce
the spikes on your 1 pps lines. If you look at the output on a ’scope the waveform at least looks like
a sine wave.

All of these gizmos run a switcher in the “few hundred KHz” range to generate the output. They run
a similar switcher to charge the battery. None of them are compatible with an indoor antenna in the same
room trying to listen to MF. None of the ones I have tried are nasty enough to bother GPS, either indoor or
outdoor. Put another way, I’ve had more trouble from LED lights than from sine wave UPS’s.

Cyber Power (via Amazon) seems to make some pretty good stuff at a price point a bit below APC. As
with everybody else, it’s a pain to figure out what’s what. Are you after a “big” rack mount unit (as in $500
and up) or something smaller?

Bob

On Oct 10, 2015, at 9:20 AM, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter.
Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you.

Chris
KD4PBJ


Sent from Mailbox


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Yes this is a complex topic. At one point in my career when I was responsible for the up time of several data centres for a high tech firm I had an Electrical Engineer on my team to (amongst other roles) work thru the various issues pertaining to UPS systems. I recall there were significant differences between the various UPS designs. Getting out of high tech and into an industry where data centres were out sourced was a nice change for me (: To relate this to time nuts, those of us looking at making significant investments in this type of equipment would do well to seek out the advice of those who are knowledgable. Sent from my iPhone > On Oct 10, 2015, at 7:51 AM, Bob Camp <kb8tq@n1k.org> wrote: > > Hi > > All of the UPS vendors these days make a wide range of products. They range from > low cost to mighty expensive. They also range a bit in terms of performance. Finding out > exactly what this or that model *does* do can be a major pain. The marketing guys apparently > don’t want you to figure out that the low cost gizmo does not have all the performance > of the one that costs 5 times as much. > > First thing to avoid - the pure square wave output versions. These may or may not > generate RFI in this or that UHF band. They will take out big chunks of HF and mess up 10 MHz > distribution. I suspect that the filters on some are better than the filters on others. The bigger issue > is that they do not play nice with modern power factor corrected power supplies. These supplies > seem to expect a sine wave and a (possibly ringing) square wave may get them confused. > > Next thing to avoid - The stepped square wave / modified square wave versions. Theses aren’t > quite as bad as the centuries old square wave units. It’s more likely you will find these than a > pure square. They still have the same issues on RFI. They may or may not antagonize a PFC > supply to the same extent. > > The target is a “pure sine wave” output. That keeps a PFC supply happy. As with any verbal spec, > “pure” likely has a few qualifiers on it. It’s not guaranteed to take out the RFI. It at least will reduce > the spikes on your 1 pps lines. If you look at the output on a ’scope the waveform at least *looks* like > a sine wave. > > All of these gizmos run a switcher in the “few hundred KHz” range to generate the output. They run > a similar switcher to charge the battery. None of them are compatible with an indoor antenna in the same > room trying to listen to MF. None of the ones I have tried are nasty enough to bother GPS, either indoor or > outdoor. Put another way, I’ve had more trouble from LED lights than from sine wave UPS’s. > > Cyber Power (via Amazon) seems to make some pretty good stuff at a price point a bit below APC. As > with everybody else, it’s a pain to figure out what’s what. Are you after a “big” rack mount unit (as in $500 > and up) or something smaller? > > Bob > > >> On Oct 10, 2015, at 9:20 AM, Chris Waldrup <kd4pbj@gmail.com> wrote: >> >> Hi, >> >> >> I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter. >> Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you. >> >> >> Chris >> KD4PBJ >> >> — >> Sent from Mailbox >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
BC
Bob Camp
Sun, Oct 11, 2015 11:55 PM

Hi

In the US, you dig those systems up either via R/V outfits or from the guys who set up big boats
(think water borne RVs rather than super tankers). The other source are the off grid solar guys.
A lot depends on just how fancy a system you are after. With reasonable effort you can pick up systems
up into the several 100 KW range.

Bob

On Oct 11, 2015, at 4:11 PM, Mark Spencer mark@alignedsolutions.com wrote:

I've also seen inverter systems that are designed for stand by power use in service at commercial sites in third world countries.  Within reason they basically let you run what ever reasonable arrangement of rechargeable lead acid based batteries you want that will supply the required voltage and current.  They handle the conversion of dc to ac and the switch over from commercial to inverter power.  They usually also feature a basic battery charger with settings to charge various types of batteries (ie, gel or conventional lead acid.)

Typically I've seen them used with a number of automotive style batteries.

The users would need to sort out the necessary cables, fuses, batteries, deal with safety considerations etc.

I've never seen these devices in Canada or the U.S.  Sort of a value engineered UPS system for price conscious markets.  Might be a nice starting point for those who want to role their own system and can deal with the safety aspects of this.  I'm not sure what the transfer time from utility to inverter power would be.

In the U.S. and Canada the typical practice seems to be to use packaged UPS systems that include their own batteries.

Sent from my iPhone

On Oct 11, 2015, at 10:36 AM, Bob Benward rbenward@verizon.net wrote:

Dave,
You could use a 120V relay and switch the high capacity battery from its own
charger to the battery pack in the UPS.  When power comes back, the relay
automatically switches the battery out and back to its own charger.

Bob

-----Original Message-----
From: time-nuts [mailto:time-nuts-bounces@febo.com] On Behalf Of Dr.
David Kirkby (Kirkby Microwave Ltd)
Sent: Saturday, October 10, 2015 6:07 PM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] UPS for my time rack

On 10 October 2015 at 14:20, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my
Thunderbolt, the laptop that runs Lady Heather, and frequency counter.

There's one issue with them that I don't see anyone mention.

I was thinking of doing the same a while back, and intended getting a

UPS

and adding a large external battery pack, so if the mains failed late at

night, I

could run the GPS receiver and a few other things overnight, and

consider

starting the generator in the morning.  I contacted a dealer on eBay,

who

specilaises in UPSs. He told me that the smaller units with built in

batteries

will die if you put large external batteries on them.
Essentially the charging circuits are not designed to run as long as

needed to

charge big batteries. Even on ones designed for external batteries,

there's a

recommended limit on the size of them. So if you think you might want to
increase runtime by adding some batteries, buy one designed for that

service.

I've had two here which were HP/Compaq 5 kW units. These were different
to the normal, in that the batteries added up to over 300 V, so could

produce

240 VAC with no need to step it up. Both these blew up on me, for

reasons I

never worked out. The load was never anywhere near 5 kW.

Lots of people mention sine wave. Of course, if you keen enough, you

could

make a class A amplifier and sine wave oscillator. The problem is that

the

pure sine wave inverters tend to be very inefficient.

As with most things, there are a lot of things to balance - runtime,

cost,

quality of output, audio noise, RFI  etc etc.

Dave


time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.6140 / Virus Database: 4435/10788 - Release Date:
10/09/15


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi In the US, you dig those systems up either via R/V outfits or from the guys who set up big boats (think water borne RVs rather than super tankers). The other source are the off grid solar guys. A lot depends on just how fancy a system you are after. With reasonable effort you can pick up systems up into the several 100 KW range. Bob > On Oct 11, 2015, at 4:11 PM, Mark Spencer <mark@alignedsolutions.com> wrote: > > I've also seen inverter systems that are designed for stand by power use in service at commercial sites in third world countries. Within reason they basically let you run what ever reasonable arrangement of rechargeable lead acid based batteries you want that will supply the required voltage and current. They handle the conversion of dc to ac and the switch over from commercial to inverter power. They usually also feature a basic battery charger with settings to charge various types of batteries (ie, gel or conventional lead acid.) > > Typically I've seen them used with a number of automotive style batteries. > > The users would need to sort out the necessary cables, fuses, batteries, deal with safety considerations etc. > > I've never seen these devices in Canada or the U.S. Sort of a value engineered UPS system for price conscious markets. Might be a nice starting point for those who want to role their own system and can deal with the safety aspects of this. I'm not sure what the transfer time from utility to inverter power would be. > > In the U.S. and Canada the typical practice seems to be to use packaged UPS systems that include their own batteries. > > > Sent from my iPhone > >> On Oct 11, 2015, at 10:36 AM, Bob Benward <rbenward@verizon.net> wrote: >> >> Dave, >> You could use a 120V relay and switch the high capacity battery from its own >> charger to the battery pack in the UPS. When power comes back, the relay >> automatically switches the battery out and back to its own charger. >> >> Bob >> >>>>> -----Original Message----- >>>>> From: time-nuts [mailto:time-nuts-bounces@febo.com] On Behalf Of Dr. >>>>> David Kirkby (Kirkby Microwave Ltd) >>>>> Sent: Saturday, October 10, 2015 6:07 PM >>>>> To: Discussion of precise time and frequency measurement >>>>> Subject: Re: [time-nuts] UPS for my time rack >>>>> >>>>>> On 10 October 2015 at 14:20, Chris Waldrup <kd4pbj@gmail.com> wrote: >>>>>> >>>>>> Hi, >>>>>> >>>>>> >>>>>> I have decided I'd like to get a UPS to put on the rack containing my >>>>>> Thunderbolt, the laptop that runs Lady Heather, and frequency counter. >>>>> >>>>> There's one issue with them that I don't see anyone mention. >>>>> >>>>> I was thinking of doing the same a while back, and intended getting a >> UPS >>>>> and adding a large external battery pack, so if the mains failed late at >> night, I >>>>> could run the GPS receiver and a few other things overnight, and >> consider >>>>> starting the generator in the morning. I contacted a dealer on eBay, >> who >>>>> specilaises in UPSs. He told me that the smaller units with built in >> batteries >>>>> will die if you put large external batteries on them. >>>>> Essentially the charging circuits are not designed to run as long as >> needed to >>>>> charge big batteries. Even on ones designed for external batteries, >> there's a >>>>> recommended limit on the size of them. So if you think you might want to >>>>> increase runtime by adding some batteries, buy one designed for that >> service. >>>>> >>>>> I've had two here which were HP/Compaq 5 kW units. These were different >>>>> to the normal, in that the batteries added up to over 300 V, so could >> produce >>>>> 240 VAC with no need to step it up. Both these blew up on me, for >> reasons I >>>>> never worked out. The load was never anywhere near 5 kW. >>>>> >>>>> Lots of people mention sine wave. Of course, if you keen enough, you >> could >>>>> make a class A amplifier and sine wave oscillator. The problem is that >> the >>>>> pure sine wave inverters tend to be very inefficient. >>>>> >>>>> As with most things, there are a lot of things to balance - runtime, >> cost, >>>>> quality of output, audio noise, RFI etc etc. >>>>> >>>>> Dave >>>>> _______________________________________________ >>>>> time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to >>>>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>>>> and follow the instructions there. >>>>> ----- >>>>> No virus found in this message. >>>>> Checked by AVG - www.avg.com >>>>> Version: 2015.0.6140 / Virus Database: 4435/10788 - Release Date: >>>>> 10/09/15 >> >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. >> > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
BH
Bill Hawkins
Mon, Oct 12, 2015 6:28 AM

My apologies in advance for further putting tension on this OT thread,
but one of the great stories from the early days of Usenet concerned a
really large UPS system for a data center. In the late 80s the Digital
Equipment Corp VAX computer was among the most powerful you could buy.
If you can accept that amount of time travel, follow this link:

http://www.hactrn.net/sra/vaxen.html

or Google "vaxen immortal power"

The reference to October 19, 1987, is to the first computer failure to
have a major effect on the stock market.

Enjoy, as they say

Bill Hawkins

My apologies in advance for further putting tension on this OT thread, but one of the great stories from the early days of Usenet concerned a really large UPS system for a data center. In the late 80s the Digital Equipment Corp VAX computer was among the most powerful you could buy. If you can accept that amount of time travel, follow this link: http://www.hactrn.net/sra/vaxen.html or Google "vaxen immortal power" The reference to October 19, 1987, is to the first computer failure to have a major effect on the stock market. Enjoy, as they say Bill Hawkins
BB
Bill Byrom
Tue, Oct 13, 2015 2:05 AM

HA! That was good. I started working at Tektronix in September 1987 and
we used VAX computers in our major field offices for order processing in
the late 80's and early 90s. They batched their daily results to our
headquarters in Oregon every night on "high speed" modems on special
phone lines. We had daily and weekly backups at each office onto open
reel tape.

The UPS horror story I can relate was at a major airline underground
computer center in the 90's. I was waiting to train a group on a high
power curve tracer they had purchased to test SCR's every time one of
their UPS inverters blew up (which must have been moderately often). I
was waiting in the supervisor's office, which had two telephones. One of
the was fire engine red, which I thought was reserved for the Hot Line
with Russia in Washington. The supervisor told me that if the red phone
rang it would be a call directly from the well-known CEO of the airline.
It seems that sometime before a worker was using a large wrench (which
was not conformally coated) directly above the critical location where
the switch between the UPS output nd city power was located. When the
wrench fell it shorted the single point of failure in their system,
stopping their reservation and flight system operation systems. So the
maintenance department suddenly received a red hotline phone for the CEO
to call when the UPS failed.

Anything can (and will) fail, and as your story about the VAX improper
manual reboot shows good intentions can turn into epic fails. When I
owned a small business in the mid-80's I was contacted by a local
company in central Texas with a small VAX and CDC disk drive who had a
major failure at his data entry company. He knew he wasn't perfroming
backups so thought it was a good time to perform preventative
maintenance on the physically large CDC removable disk pack drive (with
a huge magnet and large voice coil actuator). The company owner decided
to clean the "sock" disk drive air filter, so he removed it and vacuumed
it off.

He then made a command decision that he should use the clean side of the
filter now (since one side had been filthy) and inverted the sock filter
before reinstalling it. Gasp!! Shortly after the drive spun up a large
dust particle was sucked off the dirty side of the filter (now in the
previously clean drive chamber) and he heard a disk head bouncing around
the inside of the drive. It was (of course) the servo head. Remember
that they had no backups.

The drive was transported to CDC headquarters and they declared it a
lost cause. The small company owner asked me (and probably others) if I
would help him strap a good drive to the bad one and fabricate an arm
between the good and bad drive head acuators so the good drive servo
track would move the bad drive heads (with other required rewiring to
get the drives to work "together"). I told him NO and walked out without
wasting my time explaining how servo tracks really worked and the
mechanical and electrical engineering fallacies in this crazy scheme.
No, I would not take a penny of his money to try any portion any of that
scheme! His company soon went bankrupt, I believe.

--
Bill Byrom N5BB

On Mon, Oct 12, 2015, at 01:28 AM, Bill Hawkins wrote:

My apologies in advance for further putting tension on this OT thread,
but one of the great stories from the early days of Usenet concerned a
really large UPS system for a data center. In the late 80s the Digital
Equipment Corp VAX computer was among the most powerful you could buy.
If you can accept that amount of time travel, follow this link:

http://www.hactrn.net/sra/vaxen.html

or Google "vaxen immortal power"

The reference to October 19, 1987, is to the first computer failure to
have a major effect on the stock market.

Enjoy, as they say

Bill Hawkins


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

HA! That was good. I started working at Tektronix in September 1987 and we used VAX computers in our major field offices for order processing in the late 80's and early 90s. They batched their daily results to our headquarters in Oregon every night on "high speed" modems on special phone lines. We had daily and weekly backups at each office onto open reel tape. The UPS horror story I can relate was at a major airline underground computer center in the 90's. I was waiting to train a group on a high power curve tracer they had purchased to test SCR's every time one of their UPS inverters blew up (which must have been moderately often). I was waiting in the supervisor's office, which had two telephones. One of the was fire engine red, which I thought was reserved for the Hot Line with Russia in Washington. The supervisor told me that if the red phone rang it would be a call directly from the well-known CEO of the airline. It seems that sometime before a worker was using a large wrench (which was not conformally coated) directly above the critical location where the switch between the UPS output nd city power was located. When the wrench fell it shorted the single point of failure in their system, stopping their reservation and flight system operation systems. So the maintenance department suddenly received a red hotline phone for the CEO to call when the UPS failed. Anything can (and will) fail, and as your story about the VAX improper manual reboot shows good intentions can turn into epic fails. When I owned a small business in the mid-80's I was contacted by a local company in central Texas with a small VAX and CDC disk drive who had a major failure at his data entry company. He knew he wasn't perfroming backups so thought it was a good time to perform preventative maintenance on the physically large CDC removable disk pack drive (with a huge magnet and large voice coil actuator). The company owner decided to clean the "sock" disk drive air filter, so he removed it and vacuumed it off. He then made a command decision that he should use the clean side of the filter now (since one side had been filthy) and inverted the sock filter before reinstalling it. Gasp!! Shortly after the drive spun up a large dust particle was sucked off the dirty side of the filter (now in the previously clean drive chamber) and he heard a disk head bouncing around the inside of the drive. It was (of course) the servo head. Remember that they had no backups. The drive was transported to CDC headquarters and they declared it a lost cause. The small company owner asked me (and probably others) if I would help him strap a good drive to the bad one and fabricate an arm between the good and bad drive head acuators so the good drive servo track would move the bad drive heads (with other required rewiring to get the drives to work "together"). I told him NO and walked out without wasting my time explaining how servo tracks really worked and the mechanical and electrical engineering fallacies in this crazy scheme. No, I would not take a penny of his money to try any portion any of that scheme! His company soon went bankrupt, I believe. -- Bill Byrom N5BB On Mon, Oct 12, 2015, at 01:28 AM, Bill Hawkins wrote: > My apologies in advance for further putting tension on this OT thread, > but one of the great stories from the early days of Usenet concerned a > really large UPS system for a data center. In the late 80s the Digital > Equipment Corp VAX computer was among the most powerful you could buy. > If you can accept that amount of time travel, follow this link: > > http://www.hactrn.net/sra/vaxen.html > > or Google "vaxen immortal power" > > The reference to October 19, 1987, is to the first computer failure to > have a major effect on the stock market. > > Enjoy, as they say > > Bill Hawkins > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
PK
Poul-Henning Kamp
Tue, Oct 13, 2015 6:44 AM

Anything can (and will) fail, [...]

The interesting thing is that several sources in that business have
reported to me that about 30-40% of all power related downtime is
caused by Battery, generator and UPS failure, in that order.

Many sites simply have lower uptime after they install UPS systems.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

-------- In message <1444701906.379459.408467601.5676DFA5@webmail.messagingengine.com>, Bill Byrom writes: >Anything can (and will) fail, [...] The interesting thing is that several sources in that business have reported to me that about 30-40% of all power related downtime is caused by Battery, generator and UPS failure, in that order. Many sites simply have lower uptime after they install UPS systems. -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.
TV
Tom Van Baak
Tue, Oct 13, 2015 6:07 PM

I found this UPS article fascinating, because it echoed what I eventually found in my own lab:

http://www.theplatform.net/2015/03/13/how-this-battery-cut-microsoft-datacenter-costs-by-a-quarter/

I used to rely on one massive UPS (along with natural gas generator) for my entire lab. Eventually I found it more reliable and convenient to have localized power backup. By local I mean backup for a single shelf, or even a single instrument.

Consider that many Rb/Cs standards and even some Qz standards have internal batteries. Even if one chooses not to use their internal batteries, most of these instruments still feature dual power inputs. In addition to power redundancy it also makes it easy to move equipment or cables around without power loss. Most importantly, local backup like this avoids the possibility of single-point lab-wide power failures.

Recently, as some of my gear works from 5 VDC, those ~2600 mAh mobile phone USB backup power bricks make an excellent mini-UPS. The ideal models are those without LEDs or on/off buttons so they discharge and charge/float seamlessly without manual intervention, even if fully drained.

Multiple units can be placed in series for additional, if slightly inefficient, capacity. A good self-test is:

http://leapsecond.com/images/perpetual-USB-power.jpg

/tvb

----- Original Message -----
From: "Poul-Henning Kamp" phk@phk.freebsd.dk
To: "Discussion of precise time and frequency measurement" time-nuts@febo.com; "Bill Byrom" time@radio.sent.com
Sent: Monday, October 12, 2015 11:44 PM
Subject: Re: [time-nuts] UPS for my time rack

Anything can (and will) fail, [...]

The interesting thing is that several sources in that business have
reported to me that about 30-40% of all power related downtime is
caused by Battery, generator and UPS failure, in that order.

Many sites simply have lower uptime after they install UPS systems.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

I found this UPS article fascinating, because it echoed what I eventually found in my own lab: http://www.theplatform.net/2015/03/13/how-this-battery-cut-microsoft-datacenter-costs-by-a-quarter/ I used to rely on one massive UPS (along with natural gas generator) for my entire lab. Eventually I found it more reliable and convenient to have localized power backup. By local I mean backup for a single shelf, or even a single instrument. Consider that many Rb/Cs standards and even some Qz standards have internal batteries. Even if one chooses not to use their internal batteries, most of these instruments still feature dual power inputs. In addition to power redundancy it also makes it easy to move equipment or cables around without power loss. Most importantly, local backup like this avoids the possibility of single-point lab-wide power failures. Recently, as some of my gear works from 5 VDC, those ~2600 mAh mobile phone USB backup power bricks make an excellent mini-UPS. The ideal models are those without LEDs or on/off buttons so they discharge and charge/float seamlessly without manual intervention, even if fully drained. Multiple units can be placed in series for additional, if slightly inefficient, capacity. A good self-test is: http://leapsecond.com/images/perpetual-USB-power.jpg /tvb ----- Original Message ----- From: "Poul-Henning Kamp" <phk@phk.freebsd.dk> To: "Discussion of precise time and frequency measurement" <time-nuts@febo.com>; "Bill Byrom" <time@radio.sent.com> Sent: Monday, October 12, 2015 11:44 PM Subject: Re: [time-nuts] UPS for my time rack > -------- > In message <1444701906.379459.408467601.5676DFA5@webmail.messagingengine.com>, > Bill Byrom writes: > >>Anything can (and will) fail, [...] > > The interesting thing is that several sources in that business have > reported to me that about 30-40% of all power related downtime is > caused by Battery, generator and UPS failure, in that order. > > Many sites simply have lower uptime after they install UPS systems. > > -- > Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 > phk@FreeBSD.ORG | TCP/IP since RFC 956 > FreeBSD committer | BSD since 4.3-tahoe > Never attribute to malice what can adequately be explained by incompetence.
PK
Poul-Henning Kamp
Tue, Oct 13, 2015 6:54 PM

In message 4FD0F30EBAEF49609DF207E3EE61C15B@pc52, "Tom Van Baak" writes:

I used to rely on one massive UPS (along with natural gas generator)
for my entire lab. Eventually I found it more reliable and convenient
to have localized power backup. By local I mean backup for a single
shelf, or even a single instrument.

The big gain is avoiding the DC->AC conversions.

AC->DC conversions are covered under EnergyStar and similar programmes,
so they're generally 90% efficient or better.

But DC->AC conversions, for instance in inverters and UPS's are not
covered, the argument going that they are only run very seldomly,
and therefore capital cost would be wasted.

In the professional segment, UPS's which require a forklift,
efficiencies are good, in some cases very good, because power costs
money at that scale.

But anyting you can fit into a rack will typically have horrible
losses, the smaller the UPS the worse.  I've personally measured
sub 50% efficiency in one case.

The argument against running stuff on 12 or 24V DC is the short
circuit currents, and the absense of an affordable standarized
connector.

For the short circuit currents the only cure is fuses and caution,
and for connectors there seems to be no hope of a standard - ever.

China forced USB through as the standard for mobile phones, but
despite several valiant attempts nobody has ever managed to get
anything above 5V/5W standardized.

Here's the website of the IEEE WG which came out with a standard
(IEEE 1823:2015) this May:

http://grouper.ieee.org/groups/msc/upamd/

It will cost you $160 to see the full standard, which is a very
good and strong reason why adoption will be slow, and nobody
I've talked to expects it to go anywhere ever.

At the same time USB has come up with 100W power concept
which is not compatible, since IEEE uses CANbus and different
connectors.

I've not heard any rumours that China man nail this one.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

-------- In message <4FD0F30EBAEF49609DF207E3EE61C15B@pc52>, "Tom Van Baak" writes: >I used to rely on one massive UPS (along with natural gas generator) >for my entire lab. Eventually I found it more reliable and convenient >to have localized power backup. By local I mean backup for a single >shelf, or even a single instrument. The big gain is avoiding the DC->AC conversions. AC->DC conversions are covered under EnergyStar and similar programmes, so they're generally 90% efficient or better. But DC->AC conversions, for instance in inverters and UPS's are not covered, the argument going that they are only run very seldomly, and therefore capital cost would be wasted. In the professional segment, UPS's which require a forklift, efficiencies are good, in some cases very good, because power costs money at that scale. But anyting you can fit into a rack will typically have horrible losses, the smaller the UPS the worse. I've personally measured sub 50% efficiency in one case. The argument against running stuff on 12 or 24V DC is the short circuit currents, and the absense of an affordable standarized connector. For the short circuit currents the only cure is fuses and caution, and for connectors there seems to be no hope of a standard - ever. China forced USB through as the standard for mobile phones, but despite several valiant attempts nobody has ever managed to get anything above 5V/5W standardized. Here's the website of the IEEE WG which came out with a standard (IEEE 1823:2015) this May: http://grouper.ieee.org/groups/msc/upamd/ It will cost you $160 to see the full standard, which is a very good and strong reason why adoption will be slow, and nobody I've talked to expects it to go anywhere ever. At the same time USB has come up with 100W power concept which is not compatible, since IEEE uses CANbus and different connectors. I've not heard any rumours that China man nail this one. -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.