time-nuts@lists.febo.com

Discussion of precise time and frequency measurement

View all threads

UPS for my time rack

CW
Chris Waldrup
Sat, Oct 10, 2015 1:20 PM

Hi,

I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter. 
Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you. 

Chris
KD4PBJ


Sent from Mailbox

Hi, I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter.  Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you.  Chris KD4PBJ — Sent from Mailbox
PK
Poul-Henning Kamp
Sat, Oct 10, 2015 2:14 PM

In message 1444483218108.6a07c91c@Nodemailer, "Chris Waldrup" writes:

Has anyone had bad experience noise wise with the APC brand units
like are available on Amazon and at Staples? I'd like to get one
that doesn't generate lots of RFI. Thank you. 

Then don't.

Instead get 12 or 24 Volt sealed lead-acid batteries and a good
float-charger, and run your stuff from that.

You avoid a lot of conversion losses, and you get to decide what
quality batteries you want (As opposed to "the cheapest we can get
away with") and you get to decide how long hold-up time you want.

The important tricks are:

  1. ATO Fuse RIGHT NEXT TO THE BATTERY.  Not a meter away, but
    quite literally bolted right onto the terminal.

  2. Don't buy a shit charger, it will cost you battery life.

  3. Suitably sized fuse/polyfuses on all loads.

  4. Either put 0.010 Ohm current shunts in all over the place
    or buy a 1mA resolution clamp meter and prepare the wiring
    for measurement.

And that's it really...

I run all the always-on stuff in my lab from two 12V/105Ah telco-grade
sealed lead-acid batteries, and I'll never look back.

Presenty the load is 6.7A @ 24V, and that powers my ADSL lines,
firewalls (soekris), home server (ITX with mini-box.com PSU),
emergency lights (LED strips), GPS, GPSDO, HP5065 etc. etc.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

-------- In message <1444483218108.6a07c91c@Nodemailer>, "Chris Waldrup" writes: >Has anyone had bad experience noise wise with the APC brand units >like are available on Amazon and at Staples? I'd like to get one >that doesn't generate lots of RFI. Thank you.  Then don't. Instead get 12 or 24 Volt sealed lead-acid batteries and a good float-charger, and run your stuff from that. You avoid a lot of conversion losses, and you get to decide what quality batteries you want (As opposed to "the cheapest we can get away with") and you get to decide how long hold-up time you want. The important tricks are: 1. ATO Fuse *RIGHT NEXT TO THE BATTERY*. Not a meter away, but quite literally bolted right onto the terminal. 2. Don't buy a shit charger, it will cost you battery life. 3. Suitably sized fuse/polyfuses on all loads. 4. Either put 0.010 Ohm current shunts in all over the place or buy a 1mA resolution clamp meter and prepare the wiring for measurement. And that's it really... I run all the always-on stuff in my lab from two 12V/105Ah telco-grade sealed lead-acid batteries, and I'll never look back. Presenty the load is 6.7A @ 24V, and that powers my ADSL lines, firewalls (soekris), home server (ITX with mini-box.com PSU), emergency lights (LED strips), GPS, GPSDO, HP5065 etc. etc. -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.
BC
Bob Camp
Sat, Oct 10, 2015 2:51 PM

Hi

All of the UPS vendors these days make a wide range of products. They range from
low cost to mighty expensive. They also range a bit in terms of performance. Finding out
exactly what this or that model does do can be a major pain. The marketing guys apparently
don’t want you to figure out that the low cost gizmo does not have all the performance
of the one that costs 5 times as much.

First thing to avoid - the pure square wave output versions. These may or may not
generate RFI in this or that UHF band. They will take out big chunks of HF and mess up 10 MHz
distribution. I suspect that the filters on some are better than the filters on others. The bigger issue
is that they do not play nice with modern power factor corrected power supplies. These supplies
seem to expect a sine wave and a (possibly ringing) square wave may get them confused.

Next thing to avoid - The stepped square wave / modified square wave versions. Theses aren’t
quite as bad as the centuries old square wave units. It’s more likely you will find these than a
pure square. They still have the same issues on RFI. They may or may not antagonize a PFC
supply to the same extent.

The target is a “pure sine wave” output. That keeps a PFC supply happy. As with any verbal spec,
“pure” likely has a few qualifiers on it. It’s not guaranteed to take out the RFI. It at least will reduce
the spikes on your 1 pps lines. If you look at the output on a ’scope the waveform at least looks like
a sine wave.

All of these gizmos run a switcher in the “few hundred KHz” range to generate the output. They run
a similar switcher to charge the battery. None of them are compatible with an indoor antenna in the same
room trying to listen to MF. None of the ones I have tried are nasty enough to bother GPS, either indoor or
outdoor. Put another way, I’ve had more trouble from LED lights than from sine wave UPS’s.

Cyber Power (via Amazon) seems to make some pretty good stuff at a price point a bit below APC. As
with everybody else, it’s a pain to figure out what’s what. Are you after a “big” rack mount unit (as in $500
and up) or something smaller?

Bob

On Oct 10, 2015, at 9:20 AM, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter.
Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you.

Chris
KD4PBJ


Sent from Mailbox


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi All of the UPS vendors these days make a wide range of products. They range from low cost to mighty expensive. They also range a bit in terms of performance. Finding out exactly what this or that model *does* do can be a major pain. The marketing guys apparently don’t want you to figure out that the low cost gizmo does not have all the performance of the one that costs 5 times as much. First thing to avoid - the pure square wave output versions. These may or may not generate RFI in this or that UHF band. They will take out big chunks of HF and mess up 10 MHz distribution. I suspect that the filters on some are better than the filters on others. The bigger issue is that they do not play nice with modern power factor corrected power supplies. These supplies seem to expect a sine wave and a (possibly ringing) square wave may get them confused. Next thing to avoid - The stepped square wave / modified square wave versions. Theses aren’t quite as bad as the centuries old square wave units. It’s more likely you will find these than a pure square. They still have the same issues on RFI. They may or may not antagonize a PFC supply to the same extent. The target is a “pure sine wave” output. That keeps a PFC supply happy. As with any verbal spec, “pure” likely has a few qualifiers on it. It’s not guaranteed to take out the RFI. It at least will reduce the spikes on your 1 pps lines. If you look at the output on a ’scope the waveform at least *looks* like a sine wave. All of these gizmos run a switcher in the “few hundred KHz” range to generate the output. They run a similar switcher to charge the battery. None of them are compatible with an indoor antenna in the same room trying to listen to MF. None of the ones I have tried are nasty enough to bother GPS, either indoor or outdoor. Put another way, I’ve had more trouble from LED lights than from sine wave UPS’s. Cyber Power (via Amazon) seems to make some pretty good stuff at a price point a bit below APC. As with everybody else, it’s a pain to figure out what’s what. Are you after a “big” rack mount unit (as in $500 and up) or something smaller? Bob > On Oct 10, 2015, at 9:20 AM, Chris Waldrup <kd4pbj@gmail.com> wrote: > > Hi, > > > I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter. > Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you. > > > Chris > KD4PBJ > > — > Sent from Mailbox > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
MS
Mark Spencer
Sat, Oct 10, 2015 3:02 PM

Hi over the last 10 years or so I've purchased several consumer / small office grade UPS's from sources such as Staples and Costco.  I've never noted any RFI from them but I live in a (rf) noisy urban neighbourhood so any noise they put out is probably hard to notice.

Other than occasionally turning some of them off and on and seeing if I can see or hear any (additional) RFI on frequencies of interest I've never really looked for RFI from them.

Several years ago I started putting ferrite chokes on the feed lines for my antennas and have almost completely  switched to double shielded cables for my amateur radio and time nuts activities.

Hope these comments are of some interest.

Mark S
VE7AFZ

Sent from my iPhone

On Oct 10, 2015, at 6:20 AM, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter.
Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you.

Chris
KD4PBJ


Sent from Mailbox


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi over the last 10 years or so I've purchased several consumer / small office grade UPS's from sources such as Staples and Costco. I've never noted any RFI from them but I live in a (rf) noisy urban neighbourhood so any noise they put out is probably hard to notice. Other than occasionally turning some of them off and on and seeing if I can see or hear any (additional) RFI on frequencies of interest I've never really looked for RFI from them. Several years ago I started putting ferrite chokes on the feed lines for my antennas and have almost completely switched to double shielded cables for my amateur radio and time nuts activities. Hope these comments are of some interest. Mark S VE7AFZ Sent from my iPhone > On Oct 10, 2015, at 6:20 AM, Chris Waldrup <kd4pbj@gmail.com> wrote: > > Hi, > > > I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter. > Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you. > > > Chris > KD4PBJ > > — > Sent from Mailbox > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
MS
Mark Spencer
Sat, Oct 10, 2015 3:26 PM

A quick comment about "pure sine" devices.

At times I operate a portable VHF and up radio system from rf quiet out of the way places.  I run almost all the equipment from lead acid storage batteries.  I have small 30 dollar inverter I use to occasionally  power some equipment that needs 120 volts AC.  It puts out very little RFI.  I figured I'd upgrade to a much more expensive pure sine Inverter (I also wanted to run some linear power supplies from the inverter as well to get better voltage regulation for some of the equipment.)  It was a disaster from an RFI perspective.

Your mileage may vary.

Mark S
VE7AFZ

Sent from my iPad

On 2015-10-10, at 7:51 AM, Bob Camp kb8tq@n1k.org wrote:

Hi

All of the UPS vendors these days make a wide range of products. They range from
low cost to mighty expensive. They also range a bit in terms of performance. Finding out
exactly what this or that model does do can be a major pain. The marketing guys apparently
don’t want you to figure out that the low cost gizmo does not have all the performance
of the one that costs 5 times as much.

First thing to avoid - the pure square wave output versions. These may or may not
generate RFI in this or that UHF band. They will take out big chunks of HF and mess up 10 MHz
distribution. I suspect that the filters on some are better than the filters on others. The bigger issue
is that they do not play nice with modern power factor corrected power supplies. These supplies
seem to expect a sine wave and a (possibly ringing) square wave may get them confused.

Next thing to avoid - The stepped square wave / modified square wave versions. Theses aren’t
quite as bad as the centuries old square wave units. It’s more likely you will find these than a
pure square. They still have the same issues on RFI. They may or may not antagonize a PFC
supply to the same extent.

The target is a “pure sine wave” output. That keeps a PFC supply happy. As with any verbal spec,
“pure” likely has a few qualifiers on it. It’s not guaranteed to take out the RFI. It at least will reduce
the spikes on your 1 pps lines. If you look at the output on a ’scope the waveform at least looks like
a sine wave.

All of these gizmos run a switcher in the “few hundred KHz” range to generate the output. They run
a similar switcher to charge the battery. None of them are compatible with an indoor antenna in the same
room trying to listen to MF. None of the ones I have tried are nasty enough to bother GPS, either indoor or
outdoor. Put another way, I’ve had more trouble from LED lights than from sine wave UPS’s.

Cyber Power (via Amazon) seems to make some pretty good stuff at a price point a bit below APC. As
with everybody else, it’s a pain to figure out what’s what. Are you after a “big” rack mount unit (as in $500
and up) or something smaller?

Bob

On Oct 10, 2015, at 9:20 AM, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter.
Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you.

Chris
KD4PBJ


Sent from Mailbox


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

A quick comment about "pure sine" devices. At times I operate a portable VHF and up radio system from rf quiet out of the way places. I run almost all the equipment from lead acid storage batteries. I have small 30 dollar inverter I use to occasionally power some equipment that needs 120 volts AC. It puts out very little RFI. I figured I'd upgrade to a much more expensive pure sine Inverter (I also wanted to run some linear power supplies from the inverter as well to get better voltage regulation for some of the equipment.) It was a disaster from an RFI perspective. Your mileage may vary. Mark S VE7AFZ Sent from my iPad On 2015-10-10, at 7:51 AM, Bob Camp <kb8tq@n1k.org> wrote: > Hi > > All of the UPS vendors these days make a wide range of products. They range from > low cost to mighty expensive. They also range a bit in terms of performance. Finding out > exactly what this or that model *does* do can be a major pain. The marketing guys apparently > don’t want you to figure out that the low cost gizmo does not have all the performance > of the one that costs 5 times as much. > > First thing to avoid - the pure square wave output versions. These may or may not > generate RFI in this or that UHF band. They will take out big chunks of HF and mess up 10 MHz > distribution. I suspect that the filters on some are better than the filters on others. The bigger issue > is that they do not play nice with modern power factor corrected power supplies. These supplies > seem to expect a sine wave and a (possibly ringing) square wave may get them confused. > > Next thing to avoid - The stepped square wave / modified square wave versions. Theses aren’t > quite as bad as the centuries old square wave units. It’s more likely you will find these than a > pure square. They still have the same issues on RFI. They may or may not antagonize a PFC > supply to the same extent. > > The target is a “pure sine wave” output. That keeps a PFC supply happy. As with any verbal spec, > “pure” likely has a few qualifiers on it. It’s not guaranteed to take out the RFI. It at least will reduce > the spikes on your 1 pps lines. If you look at the output on a ’scope the waveform at least *looks* like > a sine wave. > > All of these gizmos run a switcher in the “few hundred KHz” range to generate the output. They run > a similar switcher to charge the battery. None of them are compatible with an indoor antenna in the same > room trying to listen to MF. None of the ones I have tried are nasty enough to bother GPS, either indoor or > outdoor. Put another way, I’ve had more trouble from LED lights than from sine wave UPS’s. > > Cyber Power (via Amazon) seems to make some pretty good stuff at a price point a bit below APC. As > with everybody else, it’s a pain to figure out what’s what. Are you after a “big” rack mount unit (as in $500 > and up) or something smaller? > > Bob > > >> On Oct 10, 2015, at 9:20 AM, Chris Waldrup <kd4pbj@gmail.com> wrote: >> >> Hi, >> >> >> I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter. >> Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you. >> >> >> Chris >> KD4PBJ >> >> — >> Sent from Mailbox >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
CW
Chris Waldrup
Sat, Oct 10, 2015 3:59 PM

Hi,

Thanks for the comments this morning. 

I'm not looking for something huge, maybe in the under $200 range. Just enough for the Thunderbolt, laptop, and Agilent 53131A counter. I'd like a little headroom though, as I may add another Thunderbolt or a rubidium standard someday. 

I do like the 12 V battery idea. I run my ham gear off a 12 V gel cell (I'm mainly QRP so a 32 Ah cell works for me) and I have a 12 V distribution system with Anderson Power Poles on my operating bench. 

I do a lot of VLF and LF listening but my antennas are outside.  Nothing at this time above 2 meters. 

 I live in a very quiet rural area on top of a mountain in Tennessee. So not much man made noise at all and I wanted to keep it quiet emission wise. 

Thanks for all your help.

Chris

KD4PBJ


Sent from Mailbox

On Sat, Oct 10, 2015 at 10:05 AM, Mark Spencer mark@alignedsolutions.com
wrote:

Hi over the last 10 years or so I've purchased several consumer / small office grade UPS's from sources such as Staples and Costco.  I've never noted any RFI from them but I live in a (rf) noisy urban neighbourhood so any noise they put out is probably hard to notice.
Other than occasionally turning some of them off and on and seeing if I can see or hear any (additional) RFI on frequencies of interest I've never really looked for RFI from them.
Several years ago I started putting ferrite chokes on the feed lines for my antennas and have almost completely  switched to double shielded cables for my amateur radio and time nuts activities.
Hope these comments are of some interest.
Mark S
VE7AFZ
Sent from my iPhone

On Oct 10, 2015, at 6:20 AM, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter.
Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you.

Chris
KD4PBJ


Sent from Mailbox


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi, Thanks for the comments this morning.  I'm not looking for something huge, maybe in the under $200 range. Just enough for the Thunderbolt, laptop, and Agilent 53131A counter. I'd like a little headroom though, as I may add another Thunderbolt or a rubidium standard someday.  I do like the 12 V battery idea. I run my ham gear off a 12 V gel cell (I'm mainly QRP so a 32 Ah cell works for me) and I have a 12 V distribution system with Anderson Power Poles on my operating bench.  I do a lot of VLF and LF listening but my antennas are outside.  Nothing at this time above 2 meters.   I live in a very quiet rural area on top of a mountain in Tennessee. So not much man made noise at all and I wanted to keep it quiet emission wise.  Thanks for all your help. Chris KD4PBJ — Sent from Mailbox On Sat, Oct 10, 2015 at 10:05 AM, Mark Spencer <mark@alignedsolutions.com> wrote: > Hi over the last 10 years or so I've purchased several consumer / small office grade UPS's from sources such as Staples and Costco. I've never noted any RFI from them but I live in a (rf) noisy urban neighbourhood so any noise they put out is probably hard to notice. > Other than occasionally turning some of them off and on and seeing if I can see or hear any (additional) RFI on frequencies of interest I've never really looked for RFI from them. > Several years ago I started putting ferrite chokes on the feed lines for my antennas and have almost completely switched to double shielded cables for my amateur radio and time nuts activities. > Hope these comments are of some interest. > Mark S > VE7AFZ > Sent from my iPhone >> On Oct 10, 2015, at 6:20 AM, Chris Waldrup <kd4pbj@gmail.com> wrote: >> >> Hi, >> >> >> I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter. >> Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you. >> >> >> Chris >> KD4PBJ >> >> — >> Sent from Mailbox >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. >> > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
AP
Alex Pummer
Sat, Oct 10, 2015 4:31 PM

for a very similar application I am using a solar panel to charge the
battery, but I have a vented NiFe battery, which is not sensitive of
over charging or deep discharging, and has almost unlimited life time --
I have seen some in forklifts which were 60 years old and working...
73
KJ6UHN
Alex

On 10/10/2015 7:14 AM, Poul-Henning Kamp wrote:


In message 1444483218108.6a07c91c@Nodemailer, "Chris Waldrup" writes:

Has anyone had bad experience noise wise with the APC brand units
like are available on Amazon and at Staples? I'd like to get one
that doesn't generate lots of RFI. Thank you.

Then don't.

Instead get 12 or 24 Volt sealed lead-acid batteries and a good
float-charger, and run your stuff from that.

You avoid a lot of conversion losses, and you get to decide what
quality batteries you want (As opposed to "the cheapest we can get
away with") and you get to decide how long hold-up time you want.

The important tricks are:

1. ATO Fuse *RIGHT NEXT TO THE BATTERY*.  Not a meter away, but
   quite literally bolted right onto the terminal.

2. Don't buy a shit charger, it will cost you battery life.

3. Suitably sized fuse/polyfuses on all loads.

4. Either put 0.010 Ohm current shunts in all over the place
   or buy a 1mA resolution clamp meter and prepare the wiring
   for measurement.

And that's it really...

I run all the always-on stuff in my lab from two 12V/105Ah telco-grade
sealed lead-acid batteries, and I'll never look back.

Presenty the load is 6.7A @ 24V, and that powers my ADSL lines,
firewalls (soekris), home server (ITX with mini-box.com PSU),
emergency lights (LED strips), GPS, GPSDO, HP5065 etc. etc.

for a very similar application I am using a solar panel to charge the battery, but I have a vented NiFe battery, which is not sensitive of over charging or deep discharging, and has almost unlimited life time -- I have seen some in forklifts which were 60 years old and working... 73 KJ6UHN Alex On 10/10/2015 7:14 AM, Poul-Henning Kamp wrote: > -------- > In message <1444483218108.6a07c91c@Nodemailer>, "Chris Waldrup" writes: > > >> Has anyone had bad experience noise wise with the APC brand units >> like are available on Amazon and at Staples? I'd like to get one >> that doesn't generate lots of RFI. Thank you. > Then don't. > > Instead get 12 or 24 Volt sealed lead-acid batteries and a good > float-charger, and run your stuff from that. > > You avoid a lot of conversion losses, and you get to decide what > quality batteries you want (As opposed to "the cheapest we can get > away with") and you get to decide how long hold-up time you want. > > The important tricks are: > > 1. ATO Fuse *RIGHT NEXT TO THE BATTERY*. Not a meter away, but > quite literally bolted right onto the terminal. > > 2. Don't buy a shit charger, it will cost you battery life. > > 3. Suitably sized fuse/polyfuses on all loads. > > 4. Either put 0.010 Ohm current shunts in all over the place > or buy a 1mA resolution clamp meter and prepare the wiring > for measurement. > > And that's it really... > > I run all the always-on stuff in my lab from two 12V/105Ah telco-grade > sealed lead-acid batteries, and I'll never look back. > > Presenty the load is 6.7A @ 24V, and that powers my ADSL lines, > firewalls (soekris), home server (ITX with mini-box.com PSU), > emergency lights (LED strips), GPS, GPSDO, HP5065 etc. etc. > >
BC
Bob Camp
Sat, Oct 10, 2015 5:17 PM

Hi

If you do any VLF, then anything with an inverter in it is going to be a potential disaster. It
will purely be a case of the inverter being at a frequency that bugs you right now. None of
the ones I have seen are tightly controlled in frequency. What they do today probably will not
be what they do tomorrow.

Indoors vs outdoors does not matter as much when a tenth wavelength is into the next county.
The inverter in one of these gizmos is effectively a 1KW transmitter at (say) 60 KHz. Yes filters
can help. They will rarely do the trick when you are trying to listen to something at 60, 120, 180,
240 or 360 KHz. Since that’s 60 KHz +/- lots, those “wiped out” segments are also pretty wide.

Bob

On Oct 10, 2015, at 11:59 AM, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

Thanks for the comments this morning.

I'm not looking for something huge, maybe in the under $200 range. Just enough for the Thunderbolt, laptop, and Agilent 53131A counter. I'd like a little headroom though, as I may add another Thunderbolt or a rubidium standard someday.

I do like the 12 V battery idea. I run my ham gear off a 12 V gel cell (I'm mainly QRP so a 32 Ah cell works for me) and I have a 12 V distribution system with Anderson Power Poles on my operating bench.

I do a lot of VLF and LF listening but my antennas are outside.  Nothing at this time above 2 meters.

I live in a very quiet rural area on top of a mountain in Tennessee. So not much man made noise at all and I wanted to keep it quiet emission wise.

Thanks for all your help.

Chris

KD4PBJ


Sent from Mailbox

On Sat, Oct 10, 2015 at 10:05 AM, Mark Spencer mark@alignedsolutions.com
wrote:

Hi over the last 10 years or so I've purchased several consumer / small office grade UPS's from sources such as Staples and Costco.  I've never noted any RFI from them but I live in a (rf) noisy urban neighbourhood so any noise they put out is probably hard to notice.
Other than occasionally turning some of them off and on and seeing if I can see or hear any (additional) RFI on frequencies of interest I've never really looked for RFI from them.
Several years ago I started putting ferrite chokes on the feed lines for my antennas and have almost completely  switched to double shielded cables for my amateur radio and time nuts activities.
Hope these comments are of some interest.
Mark S
VE7AFZ
Sent from my iPhone

On Oct 10, 2015, at 6:20 AM, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter.
Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you.

Chris
KD4PBJ


Sent from Mailbox


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi If you do *any* VLF, then anything with an inverter in it is going to be a potential disaster. It will purely be a case of the inverter being at a frequency that bugs you right now. None of the ones I have seen are tightly controlled in frequency. What they do today probably will not be what they do tomorrow. Indoors vs outdoors does not matter as much when a tenth wavelength is into the next county. The inverter in one of these gizmos is effectively a 1KW transmitter at (say) 60 KHz. Yes filters can help. They will rarely do the trick when you are trying to listen to something at 60, 120, 180, 240 or 360 KHz. Since that’s 60 KHz +/- lots, those “wiped out” segments are also pretty wide. Bob > On Oct 10, 2015, at 11:59 AM, Chris Waldrup <kd4pbj@gmail.com> wrote: > > Hi, > > Thanks for the comments this morning. > > I'm not looking for something huge, maybe in the under $200 range. Just enough for the Thunderbolt, laptop, and Agilent 53131A counter. I'd like a little headroom though, as I may add another Thunderbolt or a rubidium standard someday. > > I do like the 12 V battery idea. I run my ham gear off a 12 V gel cell (I'm mainly QRP so a 32 Ah cell works for me) and I have a 12 V distribution system with Anderson Power Poles on my operating bench. > > I do a lot of VLF and LF listening but my antennas are outside. Nothing at this time above 2 meters. > > I live in a very quiet rural area on top of a mountain in Tennessee. So not much man made noise at all and I wanted to keep it quiet emission wise. > > Thanks for all your help. > > > > > Chris > > KD4PBJ > > > > — > Sent from Mailbox > > On Sat, Oct 10, 2015 at 10:05 AM, Mark Spencer <mark@alignedsolutions.com> > wrote: > >> Hi over the last 10 years or so I've purchased several consumer / small office grade UPS's from sources such as Staples and Costco. I've never noted any RFI from them but I live in a (rf) noisy urban neighbourhood so any noise they put out is probably hard to notice. >> Other than occasionally turning some of them off and on and seeing if I can see or hear any (additional) RFI on frequencies of interest I've never really looked for RFI from them. >> Several years ago I started putting ferrite chokes on the feed lines for my antennas and have almost completely switched to double shielded cables for my amateur radio and time nuts activities. >> Hope these comments are of some interest. >> Mark S >> VE7AFZ >> Sent from my iPhone >>> On Oct 10, 2015, at 6:20 AM, Chris Waldrup <kd4pbj@gmail.com> wrote: >>> >>> Hi, >>> >>> >>> I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter. >>> Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you. >>> >>> >>> Chris >>> KD4PBJ >>> >>> — >>> Sent from Mailbox >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com >>> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>> and follow the instructions there. >>> >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
EH
Esa Heikkinen
Sat, Oct 10, 2015 6:32 PM

Chris Waldrup kirjoitti:

I have decided I'd like to get a UPS to put on the rack containing my
Thunderbolt, the laptop that runs Lady Heather, and frequency
counter. Has anyone had bad experience noise wise with the APC brand
units like are available on Amazon and at Staples? I'd like to get
one that doesn't generate lots of RFI. Thank you.

Get a line-interactive model which has inverter with classic iron
transformer. Line-interactive means that the inverter is not
continuously on when the mains voltage is OK, but the mais voltage is
routed thru multitap transformer which gives some filtering and enables
to fix under/overvoltage errors without turning on the inverter. When
there's blackout and inverter is really started the transformer will act
as a filter which reduces the HF interference caused by sine wave inverter.

You can recognize this kind of ups from treir weight. For example 2 kVA
model should weight more than 25 kg without batteries and more than 50
kg with batteries. You could look for example old APC SmartUPSes or APC
Matrix UPS, which has separate inverter unit, transformer unit and
battery units. Old SmartUPS'es may require float voltage modification
because their charging voltage tends to increase when aging. Without fix
it will kill the batteries too soon.

Worst case to buy is double conversion on-line model without any kind of
transformer. These are cheap but the inverter is on all the time and
it's output is not filtered. I have measured the output of these kind of
UPSes with spectrum analyzer and they are really horrible interference
sources. Not recommended if there's any kind of sensitive electronics.

Regards,

--
73s!
Esa
OH4KJU

Chris Waldrup kirjoitti: > I have decided I'd like to get a UPS to put on the rack containing my > Thunderbolt, the laptop that runs Lady Heather, and frequency > counter. Has anyone had bad experience noise wise with the APC brand > units like are available on Amazon and at Staples? I'd like to get > one that doesn't generate lots of RFI. Thank you. Get a line-interactive model which has inverter with classic iron transformer. Line-interactive means that the inverter is not continuously on when the mains voltage is OK, but the mais voltage is routed thru multitap transformer which gives some filtering and enables to fix under/overvoltage errors without turning on the inverter. When there's blackout and inverter is really started the transformer will act as a filter which reduces the HF interference caused by sine wave inverter. You can recognize this kind of ups from treir weight. For example 2 kVA model should weight more than 25 kg without batteries and more than 50 kg with batteries. You could look for example old APC SmartUPSes or APC Matrix UPS, which has separate inverter unit, transformer unit and battery units. Old SmartUPS'es may require float voltage modification because their charging voltage tends to increase when aging. Without fix it will kill the batteries too soon. Worst case to buy is double conversion on-line model without any kind of transformer. These are cheap but the inverter is on all the time and it's output is not filtered. I have measured the output of these kind of UPSes with spectrum analyzer and they are really horrible interference sources. Not recommended if there's any kind of sensitive electronics. Regards, -- 73s! Esa OH4KJU
JS
Jim Sanford
Sat, Oct 10, 2015 9:26 PM

I have 3 APC SmartUPS2200NET UPSs.  I have detected no interference to
my HF ham station from these.  One antenna is several hundred feet away;
another passes less than 10 feet away.  I have listened to these with an
IC-R10, and not found much noise.

I get much more from noise radiated by ethernet cables, unless I have
choked them (which is effective).

I bought a sun-power (I think) 1KW sine wave inverter for ham radio
field day use, to run antenna rotors, etc.  While not a disaster, it
will have to be in a shielded box and all cables in and out choked, to
not interfere with HF communications.  Based on rough measurements, I
don't think much of a problem at 1 GHz.

Good luck!
Jim
wb4gcs@amsat.org

On 10/10/2015 2:32 PM, Esa Heikkinen wrote:

Chris Waldrup kirjoitti:

I have decided I'd like to get a UPS to put on the rack containing my
Thunderbolt, the laptop that runs Lady Heather, and frequency
counter. Has anyone had bad experience noise wise with the APC brand
units like are available on Amazon and at Staples? I'd like to get
one that doesn't generate lots of RFI. Thank you.

Get a line-interactive model which has inverter with classic iron
transformer. Line-interactive means that the inverter is not
continuously on when the mains voltage is OK, but the mais voltage is
routed thru multitap transformer which gives some filtering and
enables to fix under/overvoltage errors without turning on the
inverter. When there's blackout and inverter is really started the
transformer will act as a filter which reduces the HF interference
caused by sine wave inverter.

You can recognize this kind of ups from treir weight. For example 2
kVA model should weight more than 25 kg without batteries and more
than 50 kg with batteries. You could look for example old APC
SmartUPSes or APC Matrix UPS, which has separate inverter unit,
transformer unit and battery units. Old SmartUPS'es may require float
voltage modification because their charging voltage tends to increase
when aging. Without fix it will kill the batteries too soon.

Worst case to buy is double conversion on-line model without any kind
of transformer. These are cheap but the inverter is on all the time
and it's output is not filtered. I have measured the output of these
kind of UPSes with spectrum analyzer and they are really horrible
interference sources. Not recommended if there's any kind of sensitive
electronics.

Regards,


This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

I have 3 APC SmartUPS2200NET UPSs. I have detected no interference to my HF ham station from these. One antenna is several hundred feet away; another passes less than 10 feet away. I have listened to these with an IC-R10, and not found much noise. I get much more from noise radiated by ethernet cables, unless I have choked them (which is effective). I bought a sun-power (I think) 1KW sine wave inverter for ham radio field day use, to run antenna rotors, etc. While not a disaster, it will have to be in a shielded box and all cables in and out choked, to not interfere with HF communications. Based on rough measurements, I don't think much of a problem at 1 GHz. Good luck! Jim wb4gcs@amsat.org On 10/10/2015 2:32 PM, Esa Heikkinen wrote: > Chris Waldrup kirjoitti: > >> I have decided I'd like to get a UPS to put on the rack containing my >> Thunderbolt, the laptop that runs Lady Heather, and frequency >> counter. Has anyone had bad experience noise wise with the APC brand >> units like are available on Amazon and at Staples? I'd like to get >> one that doesn't generate lots of RFI. Thank you. > > Get a line-interactive model which has inverter with classic iron > transformer. Line-interactive means that the inverter is not > continuously on when the mains voltage is OK, but the mais voltage is > routed thru multitap transformer which gives some filtering and > enables to fix under/overvoltage errors without turning on the > inverter. When there's blackout and inverter is really started the > transformer will act as a filter which reduces the HF interference > caused by sine wave inverter. > > You can recognize this kind of ups from treir weight. For example 2 > kVA model should weight more than 25 kg without batteries and more > than 50 kg with batteries. You could look for example old APC > SmartUPSes or APC Matrix UPS, which has separate inverter unit, > transformer unit and battery units. Old SmartUPS'es may require float > voltage modification because their charging voltage tends to increase > when aging. Without fix it will kill the batteries too soon. > > Worst case to buy is double conversion on-line model without any kind > of transformer. These are cheap but the inverter is on all the time > and it's output is not filtered. I have measured the output of these > kind of UPSes with spectrum analyzer and they are really horrible > interference sources. Not recommended if there's any kind of sensitive > electronics. > > Regards, > --- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus
DD
Dr. David Kirkby (Kirkby Microwave Ltd)
Sat, Oct 10, 2015 10:07 PM

On 10 October 2015 at 14:20, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my
Thunderbolt, the laptop that runs Lady Heather, and frequency counter.

There's one issue with them that I don't see anyone mention.

I was thinking of doing the same a while back, and intended getting a UPS
and adding a large external battery pack, so if the mains failed late at
night, I could run the GPS receiver and a few other things overnight, and
consider starting the generator in the morning.  I contacted a dealer on
eBay, who specilaises in UPSs. He told me that the smaller units with built
in batteries will die if you put large external batteries on them.
Essentially the charging circuits are not designed to run as long as needed
to charge big batteries. Even on ones designed for external batteries,
there's a recommended limit on the size of them. So if you think you might
want to increase runtime by adding some batteries, buy one designed for
that service.

I've had two here which were HP/Compaq 5 kW units. These were different to
the normal, in that the batteries added up to over 300 V, so could produce
240 VAC with no need to step it up. Both these blew up on me, for reasons I
never worked out. The load was never anywhere near 5 kW.

Lots of people mention sine wave. Of course, if you keen enough, you could
make a class A amplifier and sine wave oscillator. The problem is that the
pure sine wave inverters tend to be very inefficient.

As with most things, there are a lot of things to balance - runtime, cost,
quality of output, audio noise, RFI  etc etc.

Dave

On 10 October 2015 at 14:20, Chris Waldrup <kd4pbj@gmail.com> wrote: > Hi, > > > I have decided I'd like to get a UPS to put on the rack containing my > Thunderbolt, the laptop that runs Lady Heather, and frequency counter. > There's one issue with them that I don't see anyone mention. I was thinking of doing the same a while back, and intended getting a UPS and adding a large external battery pack, so if the mains failed late at night, I could run the GPS receiver and a few other things overnight, and consider starting the generator in the morning. I contacted a dealer on eBay, who specilaises in UPSs. He told me that the smaller units with built in batteries will die if you put large external batteries on them. Essentially the charging circuits are not designed to run as long as needed to charge big batteries. Even on ones designed for external batteries, there's a recommended limit on the size of them. So if you think you might want to increase runtime by adding some batteries, buy one designed for that service. I've had two here which were HP/Compaq 5 kW units. These were different to the normal, in that the batteries added up to over 300 V, so could produce 240 VAC with no need to step it up. Both these blew up on me, for reasons I never worked out. The load was never anywhere near 5 kW. Lots of people mention sine wave. Of course, if you keen enough, you could make a class A amplifier and sine wave oscillator. The problem is that the pure sine wave inverters tend to be very inefficient. As with most things, there are a lot of things to balance - runtime, cost, quality of output, audio noise, RFI etc etc. Dave
BH
Bill Hawkins
Sat, Oct 10, 2015 11:13 PM

From experience, here's a story about a very quiet (RF-wise) pretty good

sine wave UPS device.

I acquired a Liebert 2KVA UPS for data centers in 1999 when our division
was declared redundant. The cost when new would be prohibitive, but this
one was junked when it stopped working. I got it, found a bad
electrolytic cap (from the stains) and replaced it. Worked well. Never
did get a manual, had to trace the switching stuff.

This was from the days when data centers could afford the best in
immortal power. The line feeds a regulated DC supply that runs the sine
wave inverter and maintains battery charge. The inverter runs in sync
with the line, but a relay connects the line to the load while the
inverter idles. When the line fails, batteries supply the inverter and
the relay switches it to the load. Then a cooling fan starts up.

This machine required eight 12 volt batteries for 96 VDC nominal, higher
on float charge. I bought 15 amp-hour batteries and wired them to a
connector on the back intended for external batteries. Lethal voltage,
of course. Requires proper protection.

Also had a line voltage relay and toggle switch that would bypass the
UPS and connect the time rack directly to the line. This allowed the UPS
to be replaced when its warranty ran out. Batteries lasted six years,
did not invest another $500 in them.

Good luck.

Bill Hawkins

-----Original Message-----
From: Chris Waldrup
Sent: Saturday, October 10, 2015 8:20 AM
To: TIme Nuts
Subject: [time-nuts] UPS for my time rack

Hi,

I have decided I'd like to get a UPS to put on the rack containing my
Thunderbolt, the laptop that runs Lady Heather, and frequency counter.
Has anyone had bad experience noise wise with the APC brand units like
are available on Amazon and at Staples? I'd like to get one that doesn't
generate lots of RFI. Thank you. 

Chris
KD4PBJ

>From experience, here's a story about a very quiet (RF-wise) pretty good sine wave UPS device. I acquired a Liebert 2KVA UPS for data centers in 1999 when our division was declared redundant. The cost when new would be prohibitive, but this one was junked when it stopped working. I got it, found a bad electrolytic cap (from the stains) and replaced it. Worked well. Never did get a manual, had to trace the switching stuff. This was from the days when data centers could afford the best in immortal power. The line feeds a regulated DC supply that runs the sine wave inverter and maintains battery charge. The inverter runs in sync with the line, but a relay connects the line to the load while the inverter idles. When the line fails, batteries supply the inverter and the relay switches it to the load. Then a cooling fan starts up. This machine required eight 12 volt batteries for 96 VDC nominal, higher on float charge. I bought 15 amp-hour batteries and wired them to a connector on the back intended for external batteries. Lethal voltage, of course. Requires proper protection. Also had a line voltage relay and toggle switch that would bypass the UPS and connect the time rack directly to the line. This allowed the UPS to be replaced when its warranty ran out. Batteries lasted six years, did not invest another $500 in them. Good luck. Bill Hawkins -----Original Message----- From: Chris Waldrup Sent: Saturday, October 10, 2015 8:20 AM To: TIme Nuts Subject: [time-nuts] UPS for my time rack Hi, I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter. Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you.  Chris KD4PBJ
MS
Mark Spencer
Sat, Oct 10, 2015 11:24 PM

Just to add to this.  I've also been told that other pure sine inverters have worked well for others in similar applications.

Not sure if mine was unusually bad or the frequencies it operated on happened to be related to the frequencies I was using.

Your success may vary.

Best regards
Mark S

Sent from my iPhone

On Oct 10, 2015, at 8:26 AM, Mark Spencer mark@alignedsolutions.com wrote:

A quick comment about "pure sine" devices.

At times I operate a portable VHF and up radio system from rf quiet out of the way places.  I run almost all the equipment from lead acid storage batteries.  I have small 30 dollar inverter I use to occasionally  power some equipment that needs 120 volts AC.  It puts out very little RFI.  I figured I'd upgrade to a much more expensive pure sine Inverter (I also wanted to run some linear power supplies from the inverter as well to get better voltage regulation for some of the equipment.)  It was a disaster from an RFI perspective.

Your mileage may vary.

Mark S
VE7AFZ

Sent from my iPad

On 2015-10-10, at 7:51 AM, Bob Camp kb8tq@n1k.org wrote:

Hi

All of the UPS vendors these days make a wide range of products. They range from
low cost to mighty expensive. They also range a bit in terms of performance. Finding out
exactly what this or that model does do can be a major pain. The marketing guys apparently
don’t want you to figure out that the low cost gizmo does not have all the performance
of the one that costs 5 times as much.

First thing to avoid - the pure square wave output versions. These may or may not
generate RFI in this or that UHF band. They will take out big chunks of HF and mess up 10 MHz
distribution. I suspect that the filters on some are better than the filters on others. The bigger issue
is that they do not play nice with modern power factor corrected power supplies. These supplies
seem to expect a sine wave and a (possibly ringing) square wave may get them confused.

Next thing to avoid - The stepped square wave / modified square wave versions. Theses aren’t
quite as bad as the centuries old square wave units. It’s more likely you will find these than a
pure square. They still have the same issues on RFI. They may or may not antagonize a PFC
supply to the same extent.

The target is a “pure sine wave” output. That keeps a PFC supply happy. As with any verbal spec,
“pure” likely has a few qualifiers on it. It’s not guaranteed to take out the RFI. It at least will reduce
the spikes on your 1 pps lines. If you look at the output on a ’scope the waveform at least looks like
a sine wave.

All of these gizmos run a switcher in the “few hundred KHz” range to generate the output. They run
a similar switcher to charge the battery. None of them are compatible with an indoor antenna in the same
room trying to listen to MF. None of the ones I have tried are nasty enough to bother GPS, either indoor or
outdoor. Put another way, I’ve had more trouble from LED lights than from sine wave UPS’s.

Cyber Power (via Amazon) seems to make some pretty good stuff at a price point a bit below APC. As
with everybody else, it’s a pain to figure out what’s what. Are you after a “big” rack mount unit (as in $500
and up) or something smaller?

Bob

On Oct 10, 2015, at 9:20 AM, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter.
Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you.

Chris
KD4PBJ


Sent from Mailbox


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Just to add to this. I've also been told that other pure sine inverters have worked well for others in similar applications. Not sure if mine was unusually bad or the frequencies it operated on happened to be related to the frequencies I was using. Your success may vary. Best regards Mark S Sent from my iPhone > On Oct 10, 2015, at 8:26 AM, Mark Spencer <mark@alignedsolutions.com> wrote: > > A quick comment about "pure sine" devices. > > At times I operate a portable VHF and up radio system from rf quiet out of the way places. I run almost all the equipment from lead acid storage batteries. I have small 30 dollar inverter I use to occasionally power some equipment that needs 120 volts AC. It puts out very little RFI. I figured I'd upgrade to a much more expensive pure sine Inverter (I also wanted to run some linear power supplies from the inverter as well to get better voltage regulation for some of the equipment.) It was a disaster from an RFI perspective. > > > Your mileage may vary. > > Mark S > VE7AFZ > > Sent from my iPad > >> On 2015-10-10, at 7:51 AM, Bob Camp <kb8tq@n1k.org> wrote: >> >> Hi >> >> All of the UPS vendors these days make a wide range of products. They range from >> low cost to mighty expensive. They also range a bit in terms of performance. Finding out >> exactly what this or that model *does* do can be a major pain. The marketing guys apparently >> don’t want you to figure out that the low cost gizmo does not have all the performance >> of the one that costs 5 times as much. >> >> First thing to avoid - the pure square wave output versions. These may or may not >> generate RFI in this or that UHF band. They will take out big chunks of HF and mess up 10 MHz >> distribution. I suspect that the filters on some are better than the filters on others. The bigger issue >> is that they do not play nice with modern power factor corrected power supplies. These supplies >> seem to expect a sine wave and a (possibly ringing) square wave may get them confused. >> >> Next thing to avoid - The stepped square wave / modified square wave versions. Theses aren’t >> quite as bad as the centuries old square wave units. It’s more likely you will find these than a >> pure square. They still have the same issues on RFI. They may or may not antagonize a PFC >> supply to the same extent. >> >> The target is a “pure sine wave” output. That keeps a PFC supply happy. As with any verbal spec, >> “pure” likely has a few qualifiers on it. It’s not guaranteed to take out the RFI. It at least will reduce >> the spikes on your 1 pps lines. If you look at the output on a ’scope the waveform at least *looks* like >> a sine wave. >> >> All of these gizmos run a switcher in the “few hundred KHz” range to generate the output. They run >> a similar switcher to charge the battery. None of them are compatible with an indoor antenna in the same >> room trying to listen to MF. None of the ones I have tried are nasty enough to bother GPS, either indoor or >> outdoor. Put another way, I’ve had more trouble from LED lights than from sine wave UPS’s. >> >> Cyber Power (via Amazon) seems to make some pretty good stuff at a price point a bit below APC. As >> with everybody else, it’s a pain to figure out what’s what. Are you after a “big” rack mount unit (as in $500 >> and up) or something smaller? >> >> Bob >> >> >>> On Oct 10, 2015, at 9:20 AM, Chris Waldrup <kd4pbj@gmail.com> wrote: >>> >>> Hi, >>> >>> >>> I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter. >>> Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you. >>> >>> >>> Chris >>> KD4PBJ >>> >>> — >>> Sent from Mailbox >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com >>> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>> and follow the instructions there. >> >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
KP
Kasper Pedersen
Sun, Oct 11, 2015 8:57 AM

On 10/11/2015 12:07 AM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote:

Essentially the charging circuits are not designed to run as long as needed
to charge big batteries. Even on ones designed for external batteries,
there's a recommended limit on the size of them. So if you think you might
want to increase runtime by adding some batteries, buy one designed for
that service.

I have gone down that route, so I have some real data to share:

My (soon to be replaced) backup is an old back-ups CS 500, with a
rewired battery pack out of an RT3000 UPS. So instead of 7Ah, the UPS
has 40Ah. With plenty of fuses.

When charging the standard 7Ah battery, the UPS delivers about 0.7A
(from memory) for many hours, and sits at about 14C above ambient.

When charging the 40Ah, the current is the same, the temperature is the
same, just for longer, as it should be, since the thermal time constant
is much shorter than the time it takes to charge the 7Ah.

Where this has problems is during discharge:
I have about 55W load on it, which in turn is at least 5A on the
battery. After 2 hours a timer in the UPS shuts it off, regardless of
battery voltage.
Also, if you run the UPS at high load where the standard battery lasts
shorter than the thermal time constant, then there might well be trouble.

The replacement, a back-ups pro 1500 behaves differently.
It has support for external battery packs, and will happily run for at
least 5 hours, even when the external-pack-present signal is not connected.
The external-pack-present signal does make a difference when charging;
Without it, it charges at 0.7A. with it, it charges at 1.5A, and the fan
is on continuously.

/Kasper Pedersen

On 10/11/2015 12:07 AM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote: > Essentially the charging circuits are not designed to run as long as needed > to charge big batteries. Even on ones designed for external batteries, > there's a recommended limit on the size of them. So if you think you might > want to increase runtime by adding some batteries, buy one designed for > that service. I have gone down that route, so I have some real data to share: My (soon to be replaced) backup is an old back-ups CS 500, with a rewired battery pack out of an RT3000 UPS. So instead of 7Ah, the UPS has 40Ah. With plenty of fuses. When charging the standard 7Ah battery, the UPS delivers about 0.7A (from memory) for many hours, and sits at about 14C above ambient. When charging the 40Ah, the current is the same, the temperature is the same, just for longer, as it should be, since the thermal time constant is much shorter than the time it takes to charge the 7Ah. Where this has problems is during discharge: I have about 55W load on it, which in turn is at least 5A on the battery. After 2 hours a timer in the UPS shuts it off, regardless of battery voltage. Also, if you run the UPS at high load where the standard battery lasts shorter than the thermal time constant, then there might well be trouble. The replacement, a back-ups pro 1500 behaves differently. It has support for external battery packs, and will happily run for at least 5 hours, even when the external-pack-present signal is not connected. The external-pack-present signal does make a difference when charging; Without it, it charges at 0.7A. with it, it charges at 1.5A, and the fan is on continuously. /Kasper Pedersen
BC
Bob Camp
Sun, Oct 11, 2015 1:05 PM

Hi

Unless you live in an unusual location, long term power outages are going to be pretty
rare. At the house I’m now in, we had a high voltage feed that was on it’s last legs. We
had short outages on a “many times a week” basis if the wind was blowing at all. We had
rare outages in the > 5 minute range. The short / frequent blip stuff is what most light weight UPS’s
are designed to handle. Not everybody has this problem. I no longer have it, they
ripped out 10 miles of old feeder and the new one works fine.

Indeed there are locations that experience multi hour outages on a fairly regular basis.
The combination of bars closing late on Saturday and a long straight road with an abrupt
turn in it was particularly hard on a feed line I once had to cope with. In that case gas turbine
generators were the answer.

If you have a case where long outages are common, rotary machines are often the better
answer than batteries. In the case above, the power company was the one footing the bill
for the gear. Fair in this case since they were the ones that could have moved the line.

If a > 10 minute outage is a “less than once a year” sort of thing, and OCXO’s are your only concern,
let them shut down. The net impact to your lab will be relatively small. The cost to fix the problem will
be relatively large. Short blips often, are well worth fixing.

The hidden issue with running a UPS is the relatively short life of the batteries.
Sealed lead acid is low cost up front, but they simply do not last when charged the way
a typical UPS charges them. Before you go into “can’t be true” mode … plug a 100W light
bulb  load into your UPS and see how long it runs. Battery still shows as good on the indicator.
Gizmo only runs for 1/4 the time it should … hmmmm …. It’s very common to go into these
projects with a  reasonable budget, and then find out that the budget to keep it going is
not quite so generous.

Bob

On Oct 11, 2015, at 4:57 AM, Kasper Pedersen time-nuts@kasperkp.dk wrote:

On 10/11/2015 12:07 AM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote:

Essentially the charging circuits are not designed to run as long as needed
to charge big batteries. Even on ones designed for external batteries,
there's a recommended limit on the size of them. So if you think you might
want to increase runtime by adding some batteries, buy one designed for
that service.

I have gone down that route, so I have some real data to share:

My (soon to be replaced) backup is an old back-ups CS 500, with a
rewired battery pack out of an RT3000 UPS. So instead of 7Ah, the UPS
has 40Ah. With plenty of fuses.

When charging the standard 7Ah battery, the UPS delivers about 0.7A
(from memory) for many hours, and sits at about 14C above ambient.

When charging the 40Ah, the current is the same, the temperature is the
same, just for longer, as it should be, since the thermal time constant
is much shorter than the time it takes to charge the 7Ah.

Where this has problems is during discharge:
I have about 55W load on it, which in turn is at least 5A on the
battery. After 2 hours a timer in the UPS shuts it off, regardless of
battery voltage.
Also, if you run the UPS at high load where the standard battery lasts
shorter than the thermal time constant, then there might well be trouble.

The replacement, a back-ups pro 1500 behaves differently.
It has support for external battery packs, and will happily run for at
least 5 hours, even when the external-pack-present signal is not connected.
The external-pack-present signal does make a difference when charging;
Without it, it charges at 0.7A. with it, it charges at 1.5A, and the fan
is on continuously.

/Kasper Pedersen


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi Unless you live in an unusual location, long term power outages are going to be pretty rare. At the house I’m now in, we had a high voltage feed that was on it’s last legs. We had short outages on a “many times a week” basis if the wind was blowing at all. We had rare outages in the > 5 minute range. The short / frequent blip stuff is what most light weight UPS’s are designed to handle. Not everybody has this problem. I no longer have it, they ripped out 10 miles of old feeder and the new one works fine. Indeed there are locations that experience multi hour outages on a fairly regular basis. The combination of bars closing late on Saturday and a long straight road with an abrupt turn in it was particularly hard on a feed line I once had to cope with. In that case gas turbine generators were the answer. If you have a case where long outages are common, rotary machines are often the better answer than batteries. In the case above, the power company was the one footing the bill for the gear. Fair in this case since they were the ones that *could* have moved the line. If a > 10 minute outage is a “less than once a year” sort of thing, and OCXO’s are your only concern, let them shut down. The net impact to your lab will be relatively small. The cost to fix the problem will be relatively large. Short blips often, are well worth fixing. The hidden issue with running a UPS is the relatively short life of the batteries. Sealed lead acid is low cost up front, but they simply do not last when charged the way a typical UPS charges them. Before you go into “can’t be true” mode … plug a 100W light bulb load into your UPS and see how long it runs. Battery still *shows* as good on the indicator. Gizmo only runs for 1/4 the time it should … hmmmm …. It’s very common to go into these projects with a reasonable budget, and then find out that the budget to keep it going is not quite so generous. Bob > On Oct 11, 2015, at 4:57 AM, Kasper Pedersen <time-nuts@kasperkp.dk> wrote: > > On 10/11/2015 12:07 AM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote: >> Essentially the charging circuits are not designed to run as long as needed >> to charge big batteries. Even on ones designed for external batteries, >> there's a recommended limit on the size of them. So if you think you might >> want to increase runtime by adding some batteries, buy one designed for >> that service. > > I have gone down that route, so I have some real data to share: > > My (soon to be replaced) backup is an old back-ups CS 500, with a > rewired battery pack out of an RT3000 UPS. So instead of 7Ah, the UPS > has 40Ah. With plenty of fuses. > > When charging the standard 7Ah battery, the UPS delivers about 0.7A > (from memory) for many hours, and sits at about 14C above ambient. > > When charging the 40Ah, the current is the same, the temperature is the > same, just for longer, as it should be, since the thermal time constant > is much shorter than the time it takes to charge the 7Ah. > > Where this has problems is during discharge: > I have about 55W load on it, which in turn is at least 5A on the > battery. After 2 hours a timer in the UPS shuts it off, regardless of > battery voltage. > Also, if you run the UPS at high load where the standard battery lasts > shorter than the thermal time constant, then there might well be trouble. > > > > The replacement, a back-ups pro 1500 behaves differently. > It has support for external battery packs, and will happily run for at > least 5 hours, even when the external-pack-present signal is not connected. > The external-pack-present signal does make a difference when charging; > Without it, it charges at 0.7A. with it, it charges at 1.5A, and the fan > is on continuously. > > > /Kasper Pedersen > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
BH
Ben Hall
Sun, Oct 11, 2015 1:16 PM

Good morning all,

On 10/10/2015 5:07 PM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote:

I was thinking of doing the same a while back, and intended getting a UPS
and adding a large external battery pack, so if the mains failed late at
night, I could run the GPS receiver and a few other things overnight, and
consider starting the generator in the morning.  I contacted a dealer on
eBay, who specilaises in UPSs. He told me that the smaller units with built
in batteries will die if you put large external batteries on them.

Years ago, I used to work at a place that would give me all their
cast-off computer parts, including old UPS'.  I've taken probably opened
up about 20 of them, from various manufacturers.

The problem is that most don't have good heat-sinking on the power
transistors.  One unit of a brand I can't remember, all it had for a
heat sink was an aluminum bar!  Clearly, it was only designed to be run
for a small length of time.

(It's the same case for the transformers - on several removed
transformers, I've tried to use them backwards to get 12 VAC from 120
VAC, and they overheat quickly at more than 50% load.)

If you add external batteries, likely you will overheat and fry the
electronics as they get far hotter than they ever intended.

thanks much and 73,
ben, kd5byb

Good morning all, On 10/10/2015 5:07 PM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote: > I was thinking of doing the same a while back, and intended getting a UPS > and adding a large external battery pack, so if the mains failed late at > night, I could run the GPS receiver and a few other things overnight, and > consider starting the generator in the morning. I contacted a dealer on > eBay, who specilaises in UPSs. He told me that the smaller units with built > in batteries will die if you put large external batteries on them. Years ago, I used to work at a place that would give me all their cast-off computer parts, including old UPS'. I've taken probably opened up about 20 of them, from various manufacturers. The problem is that most don't have good heat-sinking on the power transistors. One unit of a brand I can't remember, all it had for a heat sink was an aluminum bar! Clearly, it was only designed to be run for a small length of time. (It's the same case for the transformers - on several removed transformers, I've tried to use them backwards to get 12 VAC from 120 VAC, and they overheat quickly at more than 50% load.) If you add external batteries, likely you will overheat and fry the electronics as they get far hotter than they ever intended. thanks much and 73, ben, kd5byb
JS
Jim Sanford
Sun, Oct 11, 2015 2:44 PM

Where I live, there are two problems.  Frequent long outages. Solved
with a natural gas standby generator, which has run several times in
anger for extended periods since installed.  (Vulnerable supply, low
priority for restoration.)

The bigger problem is transients.  On a good night, my computer UPS
activates at least once an hour.  SOmetimes you can see the lights
blink, some times not.

In the last 6 months, I have had problems with a UPS (recovered by
extended shutdown), an Astron Power supply for amateur radio equipment,
a spectrum analyzer, two signal generators, a network analyzer, and an
oscilloscope.  All were power supply failures, not all repairable.  My
lab is now protected from the power company by a SmartUPS 2200NET.

I expect the grid to get /less/ reliable.
-- In 2007, DOE published a grid study which said there did not
exist sufficient generation capacity over load to maintain grid
stability.  Insufficient additional generation was booked for
construction, so they predicted widespread rotating blackouts by 2010.
-- The 2008 recession greatly suppressed aggregate load, which is
probably why the rotating blackouts did not happen.  I read recently
that demand has not yet recovered above the suppressed levels following
the precipitous drop in 2008.  (Which generates interesting other
questions . . . .)
-- I have lost track of the number of GigaWatts of generation which
has been shut down.

If the load ever recovers . . ..

Good luck!

Jim
wb4gcs@amsast.org

On 10/11/2015 9:05 AM, Bob Camp wrote:

Hi

Unless you live in an unusual location, long term power outages are going to be pretty
rare. At the house I’m now in, we had a high voltage feed that was on it’s last legs. We
had short outages on a “many times a week” basis if the wind was blowing at all. We had
rare outages in the > 5 minute range. The short / frequent blip stuff is what most light weight UPS’s
are designed to handle. Not everybody has this problem. I no longer have it, they
ripped out 10 miles of old feeder and the new one works fine.

Indeed there are locations that experience multi hour outages on a fairly regular basis.
The combination of bars closing late on Saturday and a long straight road with an abrupt
turn in it was particularly hard on a feed line I once had to cope with. In that case gas turbine
generators were the answer.

If you have a case where long outages are common, rotary machines are often the better
answer than batteries. In the case above, the power company was the one footing the bill
for the gear. Fair in this case since they were the ones that could have moved the line.

If a > 10 minute outage is a “less than once a year” sort of thing, and OCXO’s are your only concern,
let them shut down. The net impact to your lab will be relatively small. The cost to fix the problem will
be relatively large. Short blips often, are well worth fixing.

The hidden issue with running a UPS is the relatively short life of the batteries.
Sealed lead acid is low cost up front, but they simply do not last when charged the way
a typical UPS charges them. Before you go into “can’t be true” mode … plug a 100W light
bulb  load into your UPS and see how long it runs. Battery still shows as good on the indicator.
Gizmo only runs for 1/4 the time it should … hmmmm …. It’s very common to go into these
projects with a  reasonable budget, and then find out that the budget to keep it going is
not quite so generous.

Bob

On Oct 11, 2015, at 4:57 AM, Kasper Pedersen time-nuts@kasperkp.dk wrote:

On 10/11/2015 12:07 AM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote:

Essentially the charging circuits are not designed to run as long as needed
to charge big batteries. Even on ones designed for external batteries,
there's a recommended limit on the size of them. So if you think you might
want to increase runtime by adding some batteries, buy one designed for
that service.

I have gone down that route, so I have some real data to share:

My (soon to be replaced) backup is an old back-ups CS 500, with a
rewired battery pack out of an RT3000 UPS. So instead of 7Ah, the UPS
has 40Ah. With plenty of fuses.

When charging the standard 7Ah battery, the UPS delivers about 0.7A
(from memory) for many hours, and sits at about 14C above ambient.

When charging the 40Ah, the current is the same, the temperature is the
same, just for longer, as it should be, since the thermal time constant
is much shorter than the time it takes to charge the 7Ah.

Where this has problems is during discharge:
I have about 55W load on it, which in turn is at least 5A on the
battery. After 2 hours a timer in the UPS shuts it off, regardless of
battery voltage.
Also, if you run the UPS at high load where the standard battery lasts
shorter than the thermal time constant, then there might well be trouble.

The replacement, a back-ups pro 1500 behaves differently.
It has support for external battery packs, and will happily run for at
least 5 hours, even when the external-pack-present signal is not connected.
The external-pack-present signal does make a difference when charging;
Without it, it charges at 0.7A. with it, it charges at 1.5A, and the fan
is on continuously.

/Kasper Pedersen


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

Where I live, there are two problems. Frequent long outages. Solved with a natural gas standby generator, which has run several times in anger for extended periods since installed. (Vulnerable supply, low priority for restoration.) The bigger problem is transients. On a good night, my computer UPS activates at least once an hour. SOmetimes you can see the lights blink, some times not. In the last 6 months, I have had problems with a UPS (recovered by extended shutdown), an Astron Power supply for amateur radio equipment, a spectrum analyzer, two signal generators, a network analyzer, and an oscilloscope. All were power supply failures, not all repairable. My lab is now protected from the power company by a SmartUPS 2200NET. I expect the grid to get /less/ reliable. -- In 2007, DOE published a grid study which said there did not exist sufficient generation capacity over load to maintain grid stability. Insufficient additional generation was booked for construction, so they predicted widespread rotating blackouts by 2010. -- The 2008 recession greatly suppressed aggregate load, which is probably why the rotating blackouts did not happen. I read recently that demand has not yet recovered above the suppressed levels following the precipitous drop in 2008. (Which generates interesting other questions . . . .) -- I have lost track of the number of GigaWatts of generation which has been shut down. If the load ever recovers . . .. Good luck! Jim wb4gcs@amsast.org On 10/11/2015 9:05 AM, Bob Camp wrote: > Hi > > Unless you live in an unusual location, long term power outages are going to be pretty > rare. At the house I’m now in, we had a high voltage feed that was on it’s last legs. We > had short outages on a “many times a week” basis if the wind was blowing at all. We had > rare outages in the > 5 minute range. The short / frequent blip stuff is what most light weight UPS’s > are designed to handle. Not everybody has this problem. I no longer have it, they > ripped out 10 miles of old feeder and the new one works fine. > > Indeed there are locations that experience multi hour outages on a fairly regular basis. > The combination of bars closing late on Saturday and a long straight road with an abrupt > turn in it was particularly hard on a feed line I once had to cope with. In that case gas turbine > generators were the answer. > > If you have a case where long outages are common, rotary machines are often the better > answer than batteries. In the case above, the power company was the one footing the bill > for the gear. Fair in this case since they were the ones that *could* have moved the line. > > If a > 10 minute outage is a “less than once a year” sort of thing, and OCXO’s are your only concern, > let them shut down. The net impact to your lab will be relatively small. The cost to fix the problem will > be relatively large. Short blips often, are well worth fixing. > > The hidden issue with running a UPS is the relatively short life of the batteries. > Sealed lead acid is low cost up front, but they simply do not last when charged the way > a typical UPS charges them. Before you go into “can’t be true” mode … plug a 100W light > bulb load into your UPS and see how long it runs. Battery still *shows* as good on the indicator. > Gizmo only runs for 1/4 the time it should … hmmmm …. It’s very common to go into these > projects with a reasonable budget, and then find out that the budget to keep it going is > not quite so generous. > > Bob > > > >> On Oct 11, 2015, at 4:57 AM, Kasper Pedersen <time-nuts@kasperkp.dk> wrote: >> >> On 10/11/2015 12:07 AM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote: >>> Essentially the charging circuits are not designed to run as long as needed >>> to charge big batteries. Even on ones designed for external batteries, >>> there's a recommended limit on the size of them. So if you think you might >>> want to increase runtime by adding some batteries, buy one designed for >>> that service. >> I have gone down that route, so I have some real data to share: >> >> My (soon to be replaced) backup is an old back-ups CS 500, with a >> rewired battery pack out of an RT3000 UPS. So instead of 7Ah, the UPS >> has 40Ah. With plenty of fuses. >> >> When charging the standard 7Ah battery, the UPS delivers about 0.7A >> (from memory) for many hours, and sits at about 14C above ambient. >> >> When charging the 40Ah, the current is the same, the temperature is the >> same, just for longer, as it should be, since the thermal time constant >> is much shorter than the time it takes to charge the 7Ah. >> >> Where this has problems is during discharge: >> I have about 55W load on it, which in turn is at least 5A on the >> battery. After 2 hours a timer in the UPS shuts it off, regardless of >> battery voltage. >> Also, if you run the UPS at high load where the standard battery lasts >> shorter than the thermal time constant, then there might well be trouble. >> >> >> >> The replacement, a back-ups pro 1500 behaves differently. >> It has support for external battery packs, and will happily run for at >> least 5 hours, even when the external-pack-present signal is not connected. >> The external-pack-present signal does make a difference when charging; >> Without it, it charges at 0.7A. with it, it charges at 1.5A, and the fan >> is on continuously. >> >> >> /Kasper Pedersen >> >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > --- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus
BC
Bob Camp
Sun, Oct 11, 2015 4:24 PM

Hi

If your problem is transients, from lousy power companies or from lighting on your power line, there are ways to address that.
High voltage at the service line into the building should be fixed at the point the line comes in. If you don’t, then you get into
all sorts of neat “transient went here, then there, then nuked the gizmo”. For things like time or frequency distribution this
is a very real thing. The power to one set of gear may / may not be on the same UPS as the power to another set of gear.

The best answer is a whole house protection device. These can range from < $100 at your big box store to > $1K. They can be
a wire it in on a spare breaker or a call out a pro sort of thing. A lot depends on just how bad your problem is. The net effect is that
your line is fully clamped to local ground at the panel. The phases are both clamped to a level that should not affect properly
designed gear that’s in good condition. There is always a tradeoff between how tight to clamp and how fast the gizmo wears out.
There is the usual  “get what you pay for” in terms of knowing the current degree of wear out of the device.

The alternative is to get your entire lab (and all the devices that feed it) onto a good isolation transformer. . Everything then ties to
a single “lab ground”. What ever bounce you get is now all on everything at once. Each time I’ve done this, keeping all the standard
lines, antenna feeds, ethernet cables, GPIB cables, cable TV feeds, and the rest of it correct has become impossible after a year or two.
There’s just to much going all over the place.

We are already more than just a bit  off topic for this list. There is another twist this can take, that heads over to talking to
your power company and the people who regulate it. I have seen that work (as in the nice new line that feeds this side of town).

Bob

On Oct 11, 2015, at 10:44 AM, Jim Sanford wb4gcs@wb4gcs.org wrote:

Where I live, there are two problems.  Frequent long outages. Solved with a natural gas standby generator, which has run several times in anger for extended periods since installed.  (Vulnerable supply, low priority for restoration.)

The bigger problem is transients.  On a good night, my computer UPS activates at least once an hour.  SOmetimes you can see the lights blink, some times not.

In the last 6 months, I have had problems with a UPS (recovered by extended shutdown), an Astron Power supply for amateur radio equipment, a spectrum analyzer, two signal generators, a network analyzer, and an oscilloscope.  All were power supply failures, not all repairable.  My lab is now protected from the power company by a SmartUPS 2200NET.

I expect the grid to get /less/ reliable.
-- In 2007, DOE published a grid study which said there did not exist sufficient generation capacity over load to maintain grid stability.  Insufficient additional generation was booked for construction, so they predicted widespread rotating blackouts by 2010.
-- The 2008 recession greatly suppressed aggregate load, which is probably why the rotating blackouts did not happen.  I read recently that demand has not yet recovered above the suppressed levels following the precipitous drop in 2008.  (Which generates interesting other questions . . . .)
-- I have lost track of the number of GigaWatts of generation which has been shut down.

If the load ever recovers . . ..

Good luck!

Jim
wb4gcs@amsast.org

On 10/11/2015 9:05 AM, Bob Camp wrote:

Hi

Unless you live in an unusual location, long term power outages are going to be pretty
rare. At the house I’m now in, we had a high voltage feed that was on it’s last legs. We
had short outages on a “many times a week” basis if the wind was blowing at all. We had
rare outages in the > 5 minute range. The short / frequent blip stuff is what most light weight UPS’s
are designed to handle. Not everybody has this problem. I no longer have it, they
ripped out 10 miles of old feeder and the new one works fine.

Indeed there are locations that experience multi hour outages on a fairly regular basis.
The combination of bars closing late on Saturday and a long straight road with an abrupt
turn in it was particularly hard on a feed line I once had to cope with. In that case gas turbine
generators were the answer.

If you have a case where long outages are common, rotary machines are often the better
answer than batteries. In the case above, the power company was the one footing the bill
for the gear. Fair in this case since they were the ones that could have moved the line.

If a > 10 minute outage is a “less than once a year” sort of thing, and OCXO’s are your only concern,
let them shut down. The net impact to your lab will be relatively small. The cost to fix the problem will
be relatively large. Short blips often, are well worth fixing.

The hidden issue with running a UPS is the relatively short life of the batteries.
Sealed lead acid is low cost up front, but they simply do not last when charged the way
a typical UPS charges them. Before you go into “can’t be true” mode … plug a 100W light
bulb  load into your UPS and see how long it runs. Battery still shows as good on the indicator.
Gizmo only runs for 1/4 the time it should … hmmmm …. It’s very common to go into these
projects with a  reasonable budget, and then find out that the budget to keep it going is
not quite so generous.

Bob

On Oct 11, 2015, at 4:57 AM, Kasper Pedersen time-nuts@kasperkp.dk wrote:

On 10/11/2015 12:07 AM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote:

Essentially the charging circuits are not designed to run as long as needed
to charge big batteries. Even on ones designed for external batteries,
there's a recommended limit on the size of them. So if you think you might
want to increase runtime by adding some batteries, buy one designed for
that service.

I have gone down that route, so I have some real data to share:

My (soon to be replaced) backup is an old back-ups CS 500, with a
rewired battery pack out of an RT3000 UPS. So instead of 7Ah, the UPS
has 40Ah. With plenty of fuses.

When charging the standard 7Ah battery, the UPS delivers about 0.7A
(from memory) for many hours, and sits at about 14C above ambient.

When charging the 40Ah, the current is the same, the temperature is the
same, just for longer, as it should be, since the thermal time constant
is much shorter than the time it takes to charge the 7Ah.

Where this has problems is during discharge:
I have about 55W load on it, which in turn is at least 5A on the
battery. After 2 hours a timer in the UPS shuts it off, regardless of
battery voltage.
Also, if you run the UPS at high load where the standard battery lasts
shorter than the thermal time constant, then there might well be trouble.

The replacement, a back-ups pro 1500 behaves differently.
It has support for external battery packs, and will happily run for at
least 5 hours, even when the external-pack-present signal is not connected.
The external-pack-present signal does make a difference when charging;
Without it, it charges at 0.7A. with it, it charges at 1.5A, and the fan
is on continuously.

/Kasper Pedersen


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi If your problem is transients, from lousy power companies or from lighting on your power line, there are ways to address that. High voltage at the service line into the building should be fixed at the point the line comes in. If you don’t, then you get into all sorts of neat “transient went here, then there, then nuked the gizmo”. For things like time or frequency distribution this is a very real thing. The power to one set of gear may / may not be on the same UPS as the power to another set of gear. The best answer is a whole house protection device. These can range from < $100 at your big box store to > $1K. They can be a wire it in on a spare breaker or a call out a pro sort of thing. A lot depends on just how bad your problem is. The net effect is that your line is fully clamped to local ground at the panel. The phases are both clamped to a level that should not affect properly designed gear that’s in good condition. There is always a tradeoff between how tight to clamp and how fast the gizmo wears out. There is the usual “get what you pay for” in terms of knowing the current degree of wear out of the device. The alternative is to get your entire lab (and all the devices that feed it) onto a good isolation transformer. . Everything then ties to a single “lab ground”. What ever bounce you get is now all on everything at once. Each time I’ve done this, keeping all the standard lines, antenna feeds, ethernet cables, GPIB cables, cable TV feeds, and the rest of it correct has become impossible after a year or two. There’s just to much going all over the place. We are already more than just a bit off topic for this list. There is another twist this can take, that heads over to talking to your power company and the people who regulate it. I have seen that work (as in the nice new line that feeds this side of town). Bob > On Oct 11, 2015, at 10:44 AM, Jim Sanford <wb4gcs@wb4gcs.org> wrote: > > Where I live, there are two problems. Frequent long outages. Solved with a natural gas standby generator, which has run several times in anger for extended periods since installed. (Vulnerable supply, low priority for restoration.) > > The bigger problem is transients. On a good night, my computer UPS activates at least once an hour. SOmetimes you can see the lights blink, some times not. > > In the last 6 months, I have had problems with a UPS (recovered by extended shutdown), an Astron Power supply for amateur radio equipment, a spectrum analyzer, two signal generators, a network analyzer, and an oscilloscope. All were power supply failures, not all repairable. My lab is now protected from the power company by a SmartUPS 2200NET. > > I expect the grid to get /less/ reliable. > -- In 2007, DOE published a grid study which said there did not exist sufficient generation capacity over load to maintain grid stability. Insufficient additional generation was booked for construction, so they predicted widespread rotating blackouts by 2010. > -- The 2008 recession greatly suppressed aggregate load, which is probably why the rotating blackouts did not happen. I read recently that demand has not yet recovered above the suppressed levels following the precipitous drop in 2008. (Which generates interesting other questions . . . .) > -- I have lost track of the number of GigaWatts of generation which has been shut down. > > If the load ever recovers . . .. > > Good luck! > > Jim > wb4gcs@amsast.org > > > On 10/11/2015 9:05 AM, Bob Camp wrote: >> Hi >> >> Unless you live in an unusual location, long term power outages are going to be pretty >> rare. At the house I’m now in, we had a high voltage feed that was on it’s last legs. We >> had short outages on a “many times a week” basis if the wind was blowing at all. We had >> rare outages in the > 5 minute range. The short / frequent blip stuff is what most light weight UPS’s >> are designed to handle. Not everybody has this problem. I no longer have it, they >> ripped out 10 miles of old feeder and the new one works fine. >> >> Indeed there are locations that experience multi hour outages on a fairly regular basis. >> The combination of bars closing late on Saturday and a long straight road with an abrupt >> turn in it was particularly hard on a feed line I once had to cope with. In that case gas turbine >> generators were the answer. >> >> If you have a case where long outages are common, rotary machines are often the better >> answer than batteries. In the case above, the power company was the one footing the bill >> for the gear. Fair in this case since they were the ones that *could* have moved the line. >> >> If a > 10 minute outage is a “less than once a year” sort of thing, and OCXO’s are your only concern, >> let them shut down. The net impact to your lab will be relatively small. The cost to fix the problem will >> be relatively large. Short blips often, are well worth fixing. >> >> The hidden issue with running a UPS is the relatively short life of the batteries. >> Sealed lead acid is low cost up front, but they simply do not last when charged the way >> a typical UPS charges them. Before you go into “can’t be true” mode … plug a 100W light >> bulb load into your UPS and see how long it runs. Battery still *shows* as good on the indicator. >> Gizmo only runs for 1/4 the time it should … hmmmm …. It’s very common to go into these >> projects with a reasonable budget, and then find out that the budget to keep it going is >> not quite so generous. >> >> Bob >> >> >> >>> On Oct 11, 2015, at 4:57 AM, Kasper Pedersen <time-nuts@kasperkp.dk> wrote: >>> >>> On 10/11/2015 12:07 AM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote: >>>> Essentially the charging circuits are not designed to run as long as needed >>>> to charge big batteries. Even on ones designed for external batteries, >>>> there's a recommended limit on the size of them. So if you think you might >>>> want to increase runtime by adding some batteries, buy one designed for >>>> that service. >>> I have gone down that route, so I have some real data to share: >>> >>> My (soon to be replaced) backup is an old back-ups CS 500, with a >>> rewired battery pack out of an RT3000 UPS. So instead of 7Ah, the UPS >>> has 40Ah. With plenty of fuses. >>> >>> When charging the standard 7Ah battery, the UPS delivers about 0.7A >>> (from memory) for many hours, and sits at about 14C above ambient. >>> >>> When charging the 40Ah, the current is the same, the temperature is the >>> same, just for longer, as it should be, since the thermal time constant >>> is much shorter than the time it takes to charge the 7Ah. >>> >>> Where this has problems is during discharge: >>> I have about 55W load on it, which in turn is at least 5A on the >>> battery. After 2 hours a timer in the UPS shuts it off, regardless of >>> battery voltage. >>> Also, if you run the UPS at high load where the standard battery lasts >>> shorter than the thermal time constant, then there might well be trouble. >>> >>> >>> >>> The replacement, a back-ups pro 1500 behaves differently. >>> It has support for external battery packs, and will happily run for at >>> least 5 hours, even when the external-pack-present signal is not connected. >>> The external-pack-present signal does make a difference when charging; >>> Without it, it charges at 0.7A. with it, it charges at 1.5A, and the fan >>> is on continuously. >>> >>> >>> /Kasper Pedersen >>> >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com >>> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>> and follow the instructions there. >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. >> > > > > --- > This email has been checked for viruses by Avast antivirus software. > https://www.avast.com/antivirus > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
BB
Bob Benward
Sun, Oct 11, 2015 5:36 PM

Dave,
You could use a 120V relay and switch the high capacity battery from its own
charger to the battery pack in the UPS.  When power comes back, the relay
automatically switches the battery out and back to its own charger.

Bob

-----Original Message-----
From: time-nuts [mailto:time-nuts-bounces@febo.com] On Behalf Of Dr.
David Kirkby (Kirkby Microwave Ltd)
Sent: Saturday, October 10, 2015 6:07 PM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] UPS for my time rack

On 10 October 2015 at 14:20, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my
Thunderbolt, the laptop that runs Lady Heather, and frequency counter.

There's one issue with them that I don't see anyone mention.

I was thinking of doing the same a while back, and intended getting a

UPS

and adding a large external battery pack, so if the mains failed late at

night, I

could run the GPS receiver and a few other things overnight, and

consider

starting the generator in the morning.  I contacted a dealer on eBay,

who

specilaises in UPSs. He told me that the smaller units with built in

batteries

will die if you put large external batteries on them.
Essentially the charging circuits are not designed to run as long as

needed to

charge big batteries. Even on ones designed for external batteries,

there's a

recommended limit on the size of them. So if you think you might want to
increase runtime by adding some batteries, buy one designed for that

service.

I've had two here which were HP/Compaq 5 kW units. These were different
to the normal, in that the batteries added up to over 300 V, so could

produce

240 VAC with no need to step it up. Both these blew up on me, for

reasons I

never worked out. The load was never anywhere near 5 kW.

Lots of people mention sine wave. Of course, if you keen enough, you

could

make a class A amplifier and sine wave oscillator. The problem is that

the

pure sine wave inverters tend to be very inefficient.

As with most things, there are a lot of things to balance - runtime,

cost,

quality of output, audio noise, RFI  etc etc.

Dave


time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.6140 / Virus Database: 4435/10788 - Release Date:
10/09/15

Dave, You could use a 120V relay and switch the high capacity battery from its own charger to the battery pack in the UPS. When power comes back, the relay automatically switches the battery out and back to its own charger. Bob >>> -----Original Message----- >>> From: time-nuts [mailto:time-nuts-bounces@febo.com] On Behalf Of Dr. >>> David Kirkby (Kirkby Microwave Ltd) >>> Sent: Saturday, October 10, 2015 6:07 PM >>> To: Discussion of precise time and frequency measurement >>> Subject: Re: [time-nuts] UPS for my time rack >>> >>> On 10 October 2015 at 14:20, Chris Waldrup <kd4pbj@gmail.com> wrote: >>> >>> > Hi, >>> > >>> > >>> > I have decided I'd like to get a UPS to put on the rack containing my >>> > Thunderbolt, the laptop that runs Lady Heather, and frequency counter. >>> > >>> >>> There's one issue with them that I don't see anyone mention. >>> >>> I was thinking of doing the same a while back, and intended getting a UPS >>> and adding a large external battery pack, so if the mains failed late at night, I >>> could run the GPS receiver and a few other things overnight, and consider >>> starting the generator in the morning. I contacted a dealer on eBay, who >>> specilaises in UPSs. He told me that the smaller units with built in batteries >>> will die if you put large external batteries on them. >>> Essentially the charging circuits are not designed to run as long as needed to >>> charge big batteries. Even on ones designed for external batteries, there's a >>> recommended limit on the size of them. So if you think you might want to >>> increase runtime by adding some batteries, buy one designed for that service. >>> >>> I've had two here which were HP/Compaq 5 kW units. These were different >>> to the normal, in that the batteries added up to over 300 V, so could produce >>> 240 VAC with no need to step it up. Both these blew up on me, for reasons I >>> never worked out. The load was never anywhere near 5 kW. >>> >>> Lots of people mention sine wave. Of course, if you keen enough, you could >>> make a class A amplifier and sine wave oscillator. The problem is that the >>> pure sine wave inverters tend to be very inefficient. >>> >>> As with most things, there are a lot of things to balance - runtime, cost, >>> quality of output, audio noise, RFI etc etc. >>> >>> Dave >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to >>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>> and follow the instructions there. >>> ----- >>> No virus found in this message. >>> Checked by AVG - www.avg.com >>> Version: 2015.0.6140 / Virus Database: 4435/10788 - Release Date: >>> 10/09/15
JS
Jim Sanford
Sun, Oct 11, 2015 7:12 PM

Did the transient suppressors, too.

A few years ago in a severe winter storm, after we got the neighbor's
house on generator, his furnace still wouldn't work -- furnace brain
fried.  Took the repair guy 4 hours to make 20 minute trip . . . . my
surge suppressors went in a week later.

One thing I left out of my earlier post:  ANYTHING I care about is on a UPS.

Good luck!

Jim

On 10/11/2015 12:24 PM, Bob Camp wrote:

Hi

If your problem is transients, from lousy power companies or from lighting on your power line, there are ways to address that.
High voltage at the service line into the building should be fixed at the point the line comes in. If you don’t, then you get into
all sorts of neat “transient went here, then there, then nuked the gizmo”. For things like time or frequency distribution this
is a very real thing. The power to one set of gear may / may not be on the same UPS as the power to another set of gear.

The best answer is a whole house protection device. These can range from < $100 at your big box store to > $1K. They can be
a wire it in on a spare breaker or a call out a pro sort of thing. A lot depends on just how bad your problem is. The net effect is that
your line is fully clamped to local ground at the panel. The phases are both clamped to a level that should not affect properly
designed gear that’s in good condition. There is always a tradeoff between how tight to clamp and how fast the gizmo wears out.
There is the usual  “get what you pay for” in terms of knowing the current degree of wear out of the device.

The alternative is to get your entire lab (and all the devices that feed it) onto a good isolation transformer. . Everything then ties to
a single “lab ground”. What ever bounce you get is now all on everything at once. Each time I’ve done this, keeping all the standard
lines, antenna feeds, ethernet cables, GPIB cables, cable TV feeds, and the rest of it correct has become impossible after a year or two.
There’s just to much going all over the place.

We are already more than just a bit  off topic for this list. There is another twist this can take, that heads over to talking to
your power company and the people who regulate it. I have seen that work (as in the nice new line that feeds this side of town).

Bob

On Oct 11, 2015, at 10:44 AM, Jim Sanford wb4gcs@wb4gcs.org wrote:

Where I live, there are two problems.  Frequent long outages. Solved with a natural gas standby generator, which has run several times in anger for extended periods since installed.  (Vulnerable supply, low priority for restoration.)

The bigger problem is transients.  On a good night, my computer UPS activates at least once an hour.  SOmetimes you can see the lights blink, some times not.

In the last 6 months, I have had problems with a UPS (recovered by extended shutdown), an Astron Power supply for amateur radio equipment, a spectrum analyzer, two signal generators, a network analyzer, and an oscilloscope.  All were power supply failures, not all repairable.  My lab is now protected from the power company by a SmartUPS 2200NET.

I expect the grid to get /less/ reliable.
-- In 2007, DOE published a grid study which said there did not exist sufficient generation capacity over load to maintain grid stability.  Insufficient additional generation was booked for construction, so they predicted widespread rotating blackouts by 2010.
-- The 2008 recession greatly suppressed aggregate load, which is probably why the rotating blackouts did not happen.  I read recently that demand has not yet recovered above the suppressed levels following the precipitous drop in 2008.  (Which generates interesting other questions . . . .)
-- I have lost track of the number of GigaWatts of generation which has been shut down.

If the load ever recovers . . ..

Good luck!

Jim
wb4gcs@amsast.org

On 10/11/2015 9:05 AM, Bob Camp wrote:

Hi

Unless you live in an unusual location, long term power outages are going to be pretty
rare. At the house I’m now in, we had a high voltage feed that was on it’s last legs. We
had short outages on a “many times a week” basis if the wind was blowing at all. We had
rare outages in the > 5 minute range. The short / frequent blip stuff is what most light weight UPS’s
are designed to handle. Not everybody has this problem. I no longer have it, they
ripped out 10 miles of old feeder and the new one works fine.

Indeed there are locations that experience multi hour outages on a fairly regular basis.
The combination of bars closing late on Saturday and a long straight road with an abrupt
turn in it was particularly hard on a feed line I once had to cope with. In that case gas turbine
generators were the answer.

If you have a case where long outages are common, rotary machines are often the better
answer than batteries. In the case above, the power company was the one footing the bill
for the gear. Fair in this case since they were the ones that could have moved the line.

If a > 10 minute outage is a “less than once a year” sort of thing, and OCXO’s are your only concern,
let them shut down. The net impact to your lab will be relatively small. The cost to fix the problem will
be relatively large. Short blips often, are well worth fixing.

The hidden issue with running a UPS is the relatively short life of the batteries.
Sealed lead acid is low cost up front, but they simply do not last when charged the way
a typical UPS charges them. Before you go into “can’t be true” mode … plug a 100W light
bulb  load into your UPS and see how long it runs. Battery still shows as good on the indicator.
Gizmo only runs for 1/4 the time it should … hmmmm …. It’s very common to go into these
projects with a  reasonable budget, and then find out that the budget to keep it going is
not quite so generous.

Bob

On Oct 11, 2015, at 4:57 AM, Kasper Pedersen time-nuts@kasperkp.dk wrote:

On 10/11/2015 12:07 AM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote:

Essentially the charging circuits are not designed to run as long as needed
to charge big batteries. Even on ones designed for external batteries,
there's a recommended limit on the size of them. So if you think you might
want to increase runtime by adding some batteries, buy one designed for
that service.

I have gone down that route, so I have some real data to share:

My (soon to be replaced) backup is an old back-ups CS 500, with a
rewired battery pack out of an RT3000 UPS. So instead of 7Ah, the UPS
has 40Ah. With plenty of fuses.

When charging the standard 7Ah battery, the UPS delivers about 0.7A
(from memory) for many hours, and sits at about 14C above ambient.

When charging the 40Ah, the current is the same, the temperature is the
same, just for longer, as it should be, since the thermal time constant
is much shorter than the time it takes to charge the 7Ah.

Where this has problems is during discharge:
I have about 55W load on it, which in turn is at least 5A on the
battery. After 2 hours a timer in the UPS shuts it off, regardless of
battery voltage.
Also, if you run the UPS at high load where the standard battery lasts
shorter than the thermal time constant, then there might well be trouble.

The replacement, a back-ups pro 1500 behaves differently.
It has support for external battery packs, and will happily run for at
least 5 hours, even when the external-pack-present signal is not connected.
The external-pack-present signal does make a difference when charging;
Without it, it charges at 0.7A. with it, it charges at 1.5A, and the fan
is on continuously.

/Kasper Pedersen


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

Did the transient suppressors, too. A few years ago in a severe winter storm, after we got the neighbor's house on generator, his furnace still wouldn't work -- furnace brain fried. Took the repair guy 4 hours to make 20 minute trip . . . . my surge suppressors went in a week later. One thing I left out of my earlier post: ANYTHING I care about is on a UPS. Good luck! Jim On 10/11/2015 12:24 PM, Bob Camp wrote: > Hi > > If your problem is transients, from lousy power companies or from lighting on your power line, there are ways to address that. > High voltage at the service line into the building should be fixed at the point the line comes in. If you don’t, then you get into > all sorts of neat “transient went here, then there, then nuked the gizmo”. For things like time or frequency distribution this > is a very real thing. The power to one set of gear may / may not be on the same UPS as the power to another set of gear. > > The best answer is a whole house protection device. These can range from < $100 at your big box store to > $1K. They can be > a wire it in on a spare breaker or a call out a pro sort of thing. A lot depends on just how bad your problem is. The net effect is that > your line is fully clamped to local ground at the panel. The phases are both clamped to a level that should not affect properly > designed gear that’s in good condition. There is always a tradeoff between how tight to clamp and how fast the gizmo wears out. > There is the usual “get what you pay for” in terms of knowing the current degree of wear out of the device. > > The alternative is to get your entire lab (and all the devices that feed it) onto a good isolation transformer. . Everything then ties to > a single “lab ground”. What ever bounce you get is now all on everything at once. Each time I’ve done this, keeping all the standard > lines, antenna feeds, ethernet cables, GPIB cables, cable TV feeds, and the rest of it correct has become impossible after a year or two. > There’s just to much going all over the place. > > We are already more than just a bit off topic for this list. There is another twist this can take, that heads over to talking to > your power company and the people who regulate it. I have seen that work (as in the nice new line that feeds this side of town). > > Bob > > >> On Oct 11, 2015, at 10:44 AM, Jim Sanford <wb4gcs@wb4gcs.org> wrote: >> >> Where I live, there are two problems. Frequent long outages. Solved with a natural gas standby generator, which has run several times in anger for extended periods since installed. (Vulnerable supply, low priority for restoration.) >> >> The bigger problem is transients. On a good night, my computer UPS activates at least once an hour. SOmetimes you can see the lights blink, some times not. >> >> In the last 6 months, I have had problems with a UPS (recovered by extended shutdown), an Astron Power supply for amateur radio equipment, a spectrum analyzer, two signal generators, a network analyzer, and an oscilloscope. All were power supply failures, not all repairable. My lab is now protected from the power company by a SmartUPS 2200NET. >> >> I expect the grid to get /less/ reliable. >> -- In 2007, DOE published a grid study which said there did not exist sufficient generation capacity over load to maintain grid stability. Insufficient additional generation was booked for construction, so they predicted widespread rotating blackouts by 2010. >> -- The 2008 recession greatly suppressed aggregate load, which is probably why the rotating blackouts did not happen. I read recently that demand has not yet recovered above the suppressed levels following the precipitous drop in 2008. (Which generates interesting other questions . . . .) >> -- I have lost track of the number of GigaWatts of generation which has been shut down. >> >> If the load ever recovers . . .. >> >> Good luck! >> >> Jim >> wb4gcs@amsast.org >> >> >> On 10/11/2015 9:05 AM, Bob Camp wrote: >>> Hi >>> >>> Unless you live in an unusual location, long term power outages are going to be pretty >>> rare. At the house I’m now in, we had a high voltage feed that was on it’s last legs. We >>> had short outages on a “many times a week” basis if the wind was blowing at all. We had >>> rare outages in the > 5 minute range. The short / frequent blip stuff is what most light weight UPS’s >>> are designed to handle. Not everybody has this problem. I no longer have it, they >>> ripped out 10 miles of old feeder and the new one works fine. >>> >>> Indeed there are locations that experience multi hour outages on a fairly regular basis. >>> The combination of bars closing late on Saturday and a long straight road with an abrupt >>> turn in it was particularly hard on a feed line I once had to cope with. In that case gas turbine >>> generators were the answer. >>> >>> If you have a case where long outages are common, rotary machines are often the better >>> answer than batteries. In the case above, the power company was the one footing the bill >>> for the gear. Fair in this case since they were the ones that *could* have moved the line. >>> >>> If a > 10 minute outage is a “less than once a year” sort of thing, and OCXO’s are your only concern, >>> let them shut down. The net impact to your lab will be relatively small. The cost to fix the problem will >>> be relatively large. Short blips often, are well worth fixing. >>> >>> The hidden issue with running a UPS is the relatively short life of the batteries. >>> Sealed lead acid is low cost up front, but they simply do not last when charged the way >>> a typical UPS charges them. Before you go into “can’t be true” mode … plug a 100W light >>> bulb load into your UPS and see how long it runs. Battery still *shows* as good on the indicator. >>> Gizmo only runs for 1/4 the time it should … hmmmm …. It’s very common to go into these >>> projects with a reasonable budget, and then find out that the budget to keep it going is >>> not quite so generous. >>> >>> Bob >>> >>> >>> >>>> On Oct 11, 2015, at 4:57 AM, Kasper Pedersen <time-nuts@kasperkp.dk> wrote: >>>> >>>> On 10/11/2015 12:07 AM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote: >>>>> Essentially the charging circuits are not designed to run as long as needed >>>>> to charge big batteries. Even on ones designed for external batteries, >>>>> there's a recommended limit on the size of them. So if you think you might >>>>> want to increase runtime by adding some batteries, buy one designed for >>>>> that service. >>>> I have gone down that route, so I have some real data to share: >>>> >>>> My (soon to be replaced) backup is an old back-ups CS 500, with a >>>> rewired battery pack out of an RT3000 UPS. So instead of 7Ah, the UPS >>>> has 40Ah. With plenty of fuses. >>>> >>>> When charging the standard 7Ah battery, the UPS delivers about 0.7A >>>> (from memory) for many hours, and sits at about 14C above ambient. >>>> >>>> When charging the 40Ah, the current is the same, the temperature is the >>>> same, just for longer, as it should be, since the thermal time constant >>>> is much shorter than the time it takes to charge the 7Ah. >>>> >>>> Where this has problems is during discharge: >>>> I have about 55W load on it, which in turn is at least 5A on the >>>> battery. After 2 hours a timer in the UPS shuts it off, regardless of >>>> battery voltage. >>>> Also, if you run the UPS at high load where the standard battery lasts >>>> shorter than the thermal time constant, then there might well be trouble. >>>> >>>> >>>> >>>> The replacement, a back-ups pro 1500 behaves differently. >>>> It has support for external battery packs, and will happily run for at >>>> least 5 hours, even when the external-pack-present signal is not connected. >>>> The external-pack-present signal does make a difference when charging; >>>> Without it, it charges at 0.7A. with it, it charges at 1.5A, and the fan >>>> is on continuously. >>>> >>>> >>>> /Kasper Pedersen >>>> >>>> _______________________________________________ >>>> time-nuts mailing list -- time-nuts@febo.com >>>> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>>> and follow the instructions there. >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com >>> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>> and follow the instructions there. >>> >> >> >> --- >> This email has been checked for viruses by Avast antivirus software. >> https://www.avast.com/antivirus >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > --- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus
MS
Mark Spencer
Sun, Oct 11, 2015 8:11 PM

I've also seen inverter systems that are designed for stand by power use in service at commercial sites in third world countries.  Within reason they basically let you run what ever reasonable arrangement of rechargeable lead acid based batteries you want that will supply the required voltage and current.  They handle the conversion of dc to ac and the switch over from commercial to inverter power.  They usually also feature a basic battery charger with settings to charge various types of batteries (ie, gel or conventional lead acid.)

Typically I've seen them used with a number of automotive style batteries.

The users would need to sort out the necessary cables, fuses, batteries, deal with safety considerations etc.

I've never seen these devices in Canada or the U.S.  Sort of a value engineered UPS system for price conscious markets.  Might be a nice starting point for those who want to role their own system and can deal with the safety aspects of this.  I'm not sure what the transfer time from utility to inverter power would be.

In the U.S. and Canada the typical practice seems to be to use packaged UPS systems that include their own batteries.

Sent from my iPhone

On Oct 11, 2015, at 10:36 AM, Bob Benward rbenward@verizon.net wrote:

Dave,
You could use a 120V relay and switch the high capacity battery from its own
charger to the battery pack in the UPS.  When power comes back, the relay
automatically switches the battery out and back to its own charger.

Bob

-----Original Message-----
From: time-nuts [mailto:time-nuts-bounces@febo.com] On Behalf Of Dr.
David Kirkby (Kirkby Microwave Ltd)
Sent: Saturday, October 10, 2015 6:07 PM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] UPS for my time rack

On 10 October 2015 at 14:20, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my
Thunderbolt, the laptop that runs Lady Heather, and frequency counter.

There's one issue with them that I don't see anyone mention.

I was thinking of doing the same a while back, and intended getting a

UPS

and adding a large external battery pack, so if the mains failed late at

night, I

could run the GPS receiver and a few other things overnight, and

consider

starting the generator in the morning.  I contacted a dealer on eBay,

who

specilaises in UPSs. He told me that the smaller units with built in

batteries

will die if you put large external batteries on them.
Essentially the charging circuits are not designed to run as long as

needed to

charge big batteries. Even on ones designed for external batteries,

there's a

recommended limit on the size of them. So if you think you might want to
increase runtime by adding some batteries, buy one designed for that

service.

I've had two here which were HP/Compaq 5 kW units. These were different
to the normal, in that the batteries added up to over 300 V, so could

produce

240 VAC with no need to step it up. Both these blew up on me, for

reasons I

never worked out. The load was never anywhere near 5 kW.

Lots of people mention sine wave. Of course, if you keen enough, you

could

make a class A amplifier and sine wave oscillator. The problem is that

the

pure sine wave inverters tend to be very inefficient.

As with most things, there are a lot of things to balance - runtime,

cost,

quality of output, audio noise, RFI  etc etc.

Dave


time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.6140 / Virus Database: 4435/10788 - Release Date:
10/09/15


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

I've also seen inverter systems that are designed for stand by power use in service at commercial sites in third world countries. Within reason they basically let you run what ever reasonable arrangement of rechargeable lead acid based batteries you want that will supply the required voltage and current. They handle the conversion of dc to ac and the switch over from commercial to inverter power. They usually also feature a basic battery charger with settings to charge various types of batteries (ie, gel or conventional lead acid.) Typically I've seen them used with a number of automotive style batteries. The users would need to sort out the necessary cables, fuses, batteries, deal with safety considerations etc. I've never seen these devices in Canada or the U.S. Sort of a value engineered UPS system for price conscious markets. Might be a nice starting point for those who want to role their own system and can deal with the safety aspects of this. I'm not sure what the transfer time from utility to inverter power would be. In the U.S. and Canada the typical practice seems to be to use packaged UPS systems that include their own batteries. Sent from my iPhone > On Oct 11, 2015, at 10:36 AM, Bob Benward <rbenward@verizon.net> wrote: > > Dave, > You could use a 120V relay and switch the high capacity battery from its own > charger to the battery pack in the UPS. When power comes back, the relay > automatically switches the battery out and back to its own charger. > > Bob > >>>> -----Original Message----- >>>> From: time-nuts [mailto:time-nuts-bounces@febo.com] On Behalf Of Dr. >>>> David Kirkby (Kirkby Microwave Ltd) >>>> Sent: Saturday, October 10, 2015 6:07 PM >>>> To: Discussion of precise time and frequency measurement >>>> Subject: Re: [time-nuts] UPS for my time rack >>>> >>>>> On 10 October 2015 at 14:20, Chris Waldrup <kd4pbj@gmail.com> wrote: >>>>> >>>>> Hi, >>>>> >>>>> >>>>> I have decided I'd like to get a UPS to put on the rack containing my >>>>> Thunderbolt, the laptop that runs Lady Heather, and frequency counter. >>>> >>>> There's one issue with them that I don't see anyone mention. >>>> >>>> I was thinking of doing the same a while back, and intended getting a > UPS >>>> and adding a large external battery pack, so if the mains failed late at > night, I >>>> could run the GPS receiver and a few other things overnight, and > consider >>>> starting the generator in the morning. I contacted a dealer on eBay, > who >>>> specilaises in UPSs. He told me that the smaller units with built in > batteries >>>> will die if you put large external batteries on them. >>>> Essentially the charging circuits are not designed to run as long as > needed to >>>> charge big batteries. Even on ones designed for external batteries, > there's a >>>> recommended limit on the size of them. So if you think you might want to >>>> increase runtime by adding some batteries, buy one designed for that > service. >>>> >>>> I've had two here which were HP/Compaq 5 kW units. These were different >>>> to the normal, in that the batteries added up to over 300 V, so could > produce >>>> 240 VAC with no need to step it up. Both these blew up on me, for > reasons I >>>> never worked out. The load was never anywhere near 5 kW. >>>> >>>> Lots of people mention sine wave. Of course, if you keen enough, you > could >>>> make a class A amplifier and sine wave oscillator. The problem is that > the >>>> pure sine wave inverters tend to be very inefficient. >>>> >>>> As with most things, there are a lot of things to balance - runtime, > cost, >>>> quality of output, audio noise, RFI etc etc. >>>> >>>> Dave >>>> _______________________________________________ >>>> time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to >>>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>>> and follow the instructions there. >>>> ----- >>>> No virus found in this message. >>>> Checked by AVG - www.avg.com >>>> Version: 2015.0.6140 / Virus Database: 4435/10788 - Release Date: >>>> 10/09/15 > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
MS
Mark Spencer
Sun, Oct 11, 2015 8:22 PM

I'm fortunate that several of pieces of my time nuts gear (including two of my ocxo's) feature backup 24 volt dc power inputs.  They were the only things in my house that stayed running during a recent 2 day power outage while I was away.

I have two large 12 volt gel cells in series that I re charge from time to time with a power supply via a blocking diode.

I agree about the importance of the fusing.  I've also found it's easy to buy fuses rated to work on 12 and 24 volt dc systems, fuses for 48 volt and higher dc systems are harder to find.

I also bolt the fuses directly to the battery terminals.

Sent from my iPhone

On Oct 10, 2015, at 9:31 AM, Alex Pummer alex@pcscons.com wrote:

for a very similar application I am using a solar panel to charge the battery, but I have a vented NiFe battery, which is not sensitive of over charging or deep discharging, and has almost unlimited life time -- I have seen some in forklifts which were 60 years old and working...
73
KJ6UHN
Alex

On 10/10/2015 7:14 AM, Poul-Henning Kamp wrote:

In message 1444483218108.6a07c91c@Nodemailer, "Chris Waldrup" writes:

Has anyone had bad experience noise wise with the APC brand units
like are available on Amazon and at Staples? I'd like to get one
that doesn't generate lots of RFI. Thank you.

Then don't.

Instead get 12 or 24 Volt sealed lead-acid batteries and a good
float-charger, and run your stuff from that.

You avoid a lot of conversion losses, and you get to decide what
quality batteries you want (As opposed to "the cheapest we can get
away with") and you get to decide how long hold-up time you want.

The important tricks are:

  1. ATO Fuse RIGHT NEXT TO THE BATTERY.  Not a meter away, but
    quite literally bolted right onto the terminal.

  2. Don't buy a shit charger, it will cost you battery life.

  3. Suitably sized fuse/polyfuses on all loads.

  4. Either put 0.010 Ohm current shunts in all over the place
    or buy a 1mA resolution clamp meter and prepare the wiring
    for measurement.

And that's it really...

I run all the always-on stuff in my lab from two 12V/105Ah telco-grade
sealed lead-acid batteries, and I'll never look back.

Presenty the load is 6.7A @ 24V, and that powers my ADSL lines,
firewalls (soekris), home server (ITX with mini-box.com PSU),
emergency lights (LED strips), GPS, GPSDO, HP5065 etc. etc.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

I'm fortunate that several of pieces of my time nuts gear (including two of my ocxo's) feature backup 24 volt dc power inputs. They were the only things in my house that stayed running during a recent 2 day power outage while I was away. I have two large 12 volt gel cells in series that I re charge from time to time with a power supply via a blocking diode. I agree about the importance of the fusing. I've also found it's easy to buy fuses rated to work on 12 and 24 volt dc systems, fuses for 48 volt and higher dc systems are harder to find. I also bolt the fuses directly to the battery terminals. Sent from my iPhone > On Oct 10, 2015, at 9:31 AM, Alex Pummer <alex@pcscons.com> wrote: > > for a very similar application I am using a solar panel to charge the battery, but I have a vented NiFe battery, which is not sensitive of over charging or deep discharging, and has almost unlimited life time -- I have seen some in forklifts which were 60 years old and working... > 73 > KJ6UHN > Alex > > > >> On 10/10/2015 7:14 AM, Poul-Henning Kamp wrote: >> -------- >> In message <1444483218108.6a07c91c@Nodemailer>, "Chris Waldrup" writes: >> >> >>> Has anyone had bad experience noise wise with the APC brand units >>> like are available on Amazon and at Staples? I'd like to get one >>> that doesn't generate lots of RFI. Thank you. >> Then don't. >> >> Instead get 12 or 24 Volt sealed lead-acid batteries and a good >> float-charger, and run your stuff from that. >> >> You avoid a lot of conversion losses, and you get to decide what >> quality batteries you want (As opposed to "the cheapest we can get >> away with") and you get to decide how long hold-up time you want. >> >> The important tricks are: >> >> 1. ATO Fuse *RIGHT NEXT TO THE BATTERY*. Not a meter away, but >> quite literally bolted right onto the terminal. >> >> 2. Don't buy a shit charger, it will cost you battery life. >> >> 3. Suitably sized fuse/polyfuses on all loads. >> >> 4. Either put 0.010 Ohm current shunts in all over the place >> or buy a 1mA resolution clamp meter and prepare the wiring >> for measurement. >> >> And that's it really... >> >> I run all the always-on stuff in my lab from two 12V/105Ah telco-grade >> sealed lead-acid batteries, and I'll never look back. >> >> Presenty the load is 6.7A @ 24V, and that powers my ADSL lines, >> firewalls (soekris), home server (ITX with mini-box.com PSU), >> emergency lights (LED strips), GPS, GPSDO, HP5065 etc. etc. > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
JH
Jim Harman
Sun, Oct 11, 2015 8:54 PM

On Sat, Oct 10, 2015 at 9:20 AM, Chris Waldrup kd4pbj@gmail.com wrote:

Has anyone had bad experience noise wise with the APC brand units like are
available on Amazon and at Staples? I'd like to get one that doesn't
generate lots of RFI.

I have an inexpensive CyberPower 825 AVR UPS, The UPS does the job of
keeping my computer and time-nuts gear running, but it causes an annoying
amount of RFI in the AM broadcast band. The noise is radiated from the
circuit that feeds the UPS. I found that plugging the UPS into a Belkin
outlet strip, which presumably includes some line filtering,reduced the
interference significantly.

--

--Jim Harman

On Sat, Oct 10, 2015 at 9:20 AM, Chris Waldrup <kd4pbj@gmail.com> wrote: > Has anyone had bad experience noise wise with the APC brand units like are > available on Amazon and at Staples? I'd like to get one that doesn't > generate lots of RFI. I have an inexpensive CyberPower 825 AVR UPS, The UPS does the job of keeping my computer and time-nuts gear running, but it causes an annoying amount of RFI in the AM broadcast band. The noise is radiated from the circuit that feeds the UPS. I found that plugging the UPS into a Belkin outlet strip, which presumably includes some line filtering,reduced the interference significantly. -- --Jim Harman
MS
Mark Spencer
Sun, Oct 11, 2015 8:58 PM

Yes this is a complex topic.  At one point in my career when I was responsible for the up time of several data centres for a high tech firm I had an Electrical Engineer on my team to (amongst other roles) work thru the various issues pertaining to UPS systems.  I recall there were significant differences between the various UPS designs.

Getting out of high tech and into an industry where data centres were out sourced was a nice change for me (:

To relate this to time nuts, those of us looking at making significant investments in this type of equipment would do well to seek out the advice of those who are knowledgable.

Sent from my iPhone

On Oct 10, 2015, at 7:51 AM, Bob Camp kb8tq@n1k.org wrote:

Hi

All of the UPS vendors these days make a wide range of products. They range from
low cost to mighty expensive. They also range a bit in terms of performance. Finding out
exactly what this or that model does do can be a major pain. The marketing guys apparently
don’t want you to figure out that the low cost gizmo does not have all the performance
of the one that costs 5 times as much.

First thing to avoid - the pure square wave output versions. These may or may not
generate RFI in this or that UHF band. They will take out big chunks of HF and mess up 10 MHz
distribution. I suspect that the filters on some are better than the filters on others. The bigger issue
is that they do not play nice with modern power factor corrected power supplies. These supplies
seem to expect a sine wave and a (possibly ringing) square wave may get them confused.

Next thing to avoid - The stepped square wave / modified square wave versions. Theses aren’t
quite as bad as the centuries old square wave units. It’s more likely you will find these than a
pure square. They still have the same issues on RFI. They may or may not antagonize a PFC
supply to the same extent.

The target is a “pure sine wave” output. That keeps a PFC supply happy. As with any verbal spec,
“pure” likely has a few qualifiers on it. It’s not guaranteed to take out the RFI. It at least will reduce
the spikes on your 1 pps lines. If you look at the output on a ’scope the waveform at least looks like
a sine wave.

All of these gizmos run a switcher in the “few hundred KHz” range to generate the output. They run
a similar switcher to charge the battery. None of them are compatible with an indoor antenna in the same
room trying to listen to MF. None of the ones I have tried are nasty enough to bother GPS, either indoor or
outdoor. Put another way, I’ve had more trouble from LED lights than from sine wave UPS’s.

Cyber Power (via Amazon) seems to make some pretty good stuff at a price point a bit below APC. As
with everybody else, it’s a pain to figure out what’s what. Are you after a “big” rack mount unit (as in $500
and up) or something smaller?

Bob

On Oct 10, 2015, at 9:20 AM, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter.
Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you.

Chris
KD4PBJ


Sent from Mailbox


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Yes this is a complex topic. At one point in my career when I was responsible for the up time of several data centres for a high tech firm I had an Electrical Engineer on my team to (amongst other roles) work thru the various issues pertaining to UPS systems. I recall there were significant differences between the various UPS designs. Getting out of high tech and into an industry where data centres were out sourced was a nice change for me (: To relate this to time nuts, those of us looking at making significant investments in this type of equipment would do well to seek out the advice of those who are knowledgable. Sent from my iPhone > On Oct 10, 2015, at 7:51 AM, Bob Camp <kb8tq@n1k.org> wrote: > > Hi > > All of the UPS vendors these days make a wide range of products. They range from > low cost to mighty expensive. They also range a bit in terms of performance. Finding out > exactly what this or that model *does* do can be a major pain. The marketing guys apparently > don’t want you to figure out that the low cost gizmo does not have all the performance > of the one that costs 5 times as much. > > First thing to avoid - the pure square wave output versions. These may or may not > generate RFI in this or that UHF band. They will take out big chunks of HF and mess up 10 MHz > distribution. I suspect that the filters on some are better than the filters on others. The bigger issue > is that they do not play nice with modern power factor corrected power supplies. These supplies > seem to expect a sine wave and a (possibly ringing) square wave may get them confused. > > Next thing to avoid - The stepped square wave / modified square wave versions. Theses aren’t > quite as bad as the centuries old square wave units. It’s more likely you will find these than a > pure square. They still have the same issues on RFI. They may or may not antagonize a PFC > supply to the same extent. > > The target is a “pure sine wave” output. That keeps a PFC supply happy. As with any verbal spec, > “pure” likely has a few qualifiers on it. It’s not guaranteed to take out the RFI. It at least will reduce > the spikes on your 1 pps lines. If you look at the output on a ’scope the waveform at least *looks* like > a sine wave. > > All of these gizmos run a switcher in the “few hundred KHz” range to generate the output. They run > a similar switcher to charge the battery. None of them are compatible with an indoor antenna in the same > room trying to listen to MF. None of the ones I have tried are nasty enough to bother GPS, either indoor or > outdoor. Put another way, I’ve had more trouble from LED lights than from sine wave UPS’s. > > Cyber Power (via Amazon) seems to make some pretty good stuff at a price point a bit below APC. As > with everybody else, it’s a pain to figure out what’s what. Are you after a “big” rack mount unit (as in $500 > and up) or something smaller? > > Bob > > >> On Oct 10, 2015, at 9:20 AM, Chris Waldrup <kd4pbj@gmail.com> wrote: >> >> Hi, >> >> >> I have decided I'd like to get a UPS to put on the rack containing my Thunderbolt, the laptop that runs Lady Heather, and frequency counter. >> Has anyone had bad experience noise wise with the APC brand units like are available on Amazon and at Staples? I'd like to get one that doesn't generate lots of RFI. Thank you. >> >> >> Chris >> KD4PBJ >> >> — >> Sent from Mailbox >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
BC
Bob Camp
Sun, Oct 11, 2015 11:55 PM

Hi

In the US, you dig those systems up either via R/V outfits or from the guys who set up big boats
(think water borne RVs rather than super tankers). The other source are the off grid solar guys.
A lot depends on just how fancy a system you are after. With reasonable effort you can pick up systems
up into the several 100 KW range.

Bob

On Oct 11, 2015, at 4:11 PM, Mark Spencer mark@alignedsolutions.com wrote:

I've also seen inverter systems that are designed for stand by power use in service at commercial sites in third world countries.  Within reason they basically let you run what ever reasonable arrangement of rechargeable lead acid based batteries you want that will supply the required voltage and current.  They handle the conversion of dc to ac and the switch over from commercial to inverter power.  They usually also feature a basic battery charger with settings to charge various types of batteries (ie, gel or conventional lead acid.)

Typically I've seen them used with a number of automotive style batteries.

The users would need to sort out the necessary cables, fuses, batteries, deal with safety considerations etc.

I've never seen these devices in Canada or the U.S.  Sort of a value engineered UPS system for price conscious markets.  Might be a nice starting point for those who want to role their own system and can deal with the safety aspects of this.  I'm not sure what the transfer time from utility to inverter power would be.

In the U.S. and Canada the typical practice seems to be to use packaged UPS systems that include their own batteries.

Sent from my iPhone

On Oct 11, 2015, at 10:36 AM, Bob Benward rbenward@verizon.net wrote:

Dave,
You could use a 120V relay and switch the high capacity battery from its own
charger to the battery pack in the UPS.  When power comes back, the relay
automatically switches the battery out and back to its own charger.

Bob

-----Original Message-----
From: time-nuts [mailto:time-nuts-bounces@febo.com] On Behalf Of Dr.
David Kirkby (Kirkby Microwave Ltd)
Sent: Saturday, October 10, 2015 6:07 PM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] UPS for my time rack

On 10 October 2015 at 14:20, Chris Waldrup kd4pbj@gmail.com wrote:

Hi,

I have decided I'd like to get a UPS to put on the rack containing my
Thunderbolt, the laptop that runs Lady Heather, and frequency counter.

There's one issue with them that I don't see anyone mention.

I was thinking of doing the same a while back, and intended getting a

UPS

and adding a large external battery pack, so if the mains failed late at

night, I

could run the GPS receiver and a few other things overnight, and

consider

starting the generator in the morning.  I contacted a dealer on eBay,

who

specilaises in UPSs. He told me that the smaller units with built in

batteries

will die if you put large external batteries on them.
Essentially the charging circuits are not designed to run as long as

needed to

charge big batteries. Even on ones designed for external batteries,

there's a

recommended limit on the size of them. So if you think you might want to
increase runtime by adding some batteries, buy one designed for that

service.

I've had two here which were HP/Compaq 5 kW units. These were different
to the normal, in that the batteries added up to over 300 V, so could

produce

240 VAC with no need to step it up. Both these blew up on me, for

reasons I

never worked out. The load was never anywhere near 5 kW.

Lots of people mention sine wave. Of course, if you keen enough, you

could

make a class A amplifier and sine wave oscillator. The problem is that

the

pure sine wave inverters tend to be very inefficient.

As with most things, there are a lot of things to balance - runtime,

cost,

quality of output, audio noise, RFI  etc etc.

Dave


time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.6140 / Virus Database: 4435/10788 - Release Date:
10/09/15


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi In the US, you dig those systems up either via R/V outfits or from the guys who set up big boats (think water borne RVs rather than super tankers). The other source are the off grid solar guys. A lot depends on just how fancy a system you are after. With reasonable effort you can pick up systems up into the several 100 KW range. Bob > On Oct 11, 2015, at 4:11 PM, Mark Spencer <mark@alignedsolutions.com> wrote: > > I've also seen inverter systems that are designed for stand by power use in service at commercial sites in third world countries. Within reason they basically let you run what ever reasonable arrangement of rechargeable lead acid based batteries you want that will supply the required voltage and current. They handle the conversion of dc to ac and the switch over from commercial to inverter power. They usually also feature a basic battery charger with settings to charge various types of batteries (ie, gel or conventional lead acid.) > > Typically I've seen them used with a number of automotive style batteries. > > The users would need to sort out the necessary cables, fuses, batteries, deal with safety considerations etc. > > I've never seen these devices in Canada or the U.S. Sort of a value engineered UPS system for price conscious markets. Might be a nice starting point for those who want to role their own system and can deal with the safety aspects of this. I'm not sure what the transfer time from utility to inverter power would be. > > In the U.S. and Canada the typical practice seems to be to use packaged UPS systems that include their own batteries. > > > Sent from my iPhone > >> On Oct 11, 2015, at 10:36 AM, Bob Benward <rbenward@verizon.net> wrote: >> >> Dave, >> You could use a 120V relay and switch the high capacity battery from its own >> charger to the battery pack in the UPS. When power comes back, the relay >> automatically switches the battery out and back to its own charger. >> >> Bob >> >>>>> -----Original Message----- >>>>> From: time-nuts [mailto:time-nuts-bounces@febo.com] On Behalf Of Dr. >>>>> David Kirkby (Kirkby Microwave Ltd) >>>>> Sent: Saturday, October 10, 2015 6:07 PM >>>>> To: Discussion of precise time and frequency measurement >>>>> Subject: Re: [time-nuts] UPS for my time rack >>>>> >>>>>> On 10 October 2015 at 14:20, Chris Waldrup <kd4pbj@gmail.com> wrote: >>>>>> >>>>>> Hi, >>>>>> >>>>>> >>>>>> I have decided I'd like to get a UPS to put on the rack containing my >>>>>> Thunderbolt, the laptop that runs Lady Heather, and frequency counter. >>>>> >>>>> There's one issue with them that I don't see anyone mention. >>>>> >>>>> I was thinking of doing the same a while back, and intended getting a >> UPS >>>>> and adding a large external battery pack, so if the mains failed late at >> night, I >>>>> could run the GPS receiver and a few other things overnight, and >> consider >>>>> starting the generator in the morning. I contacted a dealer on eBay, >> who >>>>> specilaises in UPSs. He told me that the smaller units with built in >> batteries >>>>> will die if you put large external batteries on them. >>>>> Essentially the charging circuits are not designed to run as long as >> needed to >>>>> charge big batteries. Even on ones designed for external batteries, >> there's a >>>>> recommended limit on the size of them. So if you think you might want to >>>>> increase runtime by adding some batteries, buy one designed for that >> service. >>>>> >>>>> I've had two here which were HP/Compaq 5 kW units. These were different >>>>> to the normal, in that the batteries added up to over 300 V, so could >> produce >>>>> 240 VAC with no need to step it up. Both these blew up on me, for >> reasons I >>>>> never worked out. The load was never anywhere near 5 kW. >>>>> >>>>> Lots of people mention sine wave. Of course, if you keen enough, you >> could >>>>> make a class A amplifier and sine wave oscillator. The problem is that >> the >>>>> pure sine wave inverters tend to be very inefficient. >>>>> >>>>> As with most things, there are a lot of things to balance - runtime, >> cost, >>>>> quality of output, audio noise, RFI etc etc. >>>>> >>>>> Dave >>>>> _______________________________________________ >>>>> time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to >>>>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>>>> and follow the instructions there. >>>>> ----- >>>>> No virus found in this message. >>>>> Checked by AVG - www.avg.com >>>>> Version: 2015.0.6140 / Virus Database: 4435/10788 - Release Date: >>>>> 10/09/15 >> >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. >> > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
BH
Bill Hawkins
Mon, Oct 12, 2015 6:28 AM

My apologies in advance for further putting tension on this OT thread,
but one of the great stories from the early days of Usenet concerned a
really large UPS system for a data center. In the late 80s the Digital
Equipment Corp VAX computer was among the most powerful you could buy.
If you can accept that amount of time travel, follow this link:

http://www.hactrn.net/sra/vaxen.html

or Google "vaxen immortal power"

The reference to October 19, 1987, is to the first computer failure to
have a major effect on the stock market.

Enjoy, as they say

Bill Hawkins

My apologies in advance for further putting tension on this OT thread, but one of the great stories from the early days of Usenet concerned a really large UPS system for a data center. In the late 80s the Digital Equipment Corp VAX computer was among the most powerful you could buy. If you can accept that amount of time travel, follow this link: http://www.hactrn.net/sra/vaxen.html or Google "vaxen immortal power" The reference to October 19, 1987, is to the first computer failure to have a major effect on the stock market. Enjoy, as they say Bill Hawkins
BB
Bill Byrom
Tue, Oct 13, 2015 2:05 AM

HA! That was good. I started working at Tektronix in September 1987 and
we used VAX computers in our major field offices for order processing in
the late 80's and early 90s. They batched their daily results to our
headquarters in Oregon every night on "high speed" modems on special
phone lines. We had daily and weekly backups at each office onto open
reel tape.

The UPS horror story I can relate was at a major airline underground
computer center in the 90's. I was waiting to train a group on a high
power curve tracer they had purchased to test SCR's every time one of
their UPS inverters blew up (which must have been moderately often). I
was waiting in the supervisor's office, which had two telephones. One of
the was fire engine red, which I thought was reserved for the Hot Line
with Russia in Washington. The supervisor told me that if the red phone
rang it would be a call directly from the well-known CEO of the airline.
It seems that sometime before a worker was using a large wrench (which
was not conformally coated) directly above the critical location where
the switch between the UPS output nd city power was located. When the
wrench fell it shorted the single point of failure in their system,
stopping their reservation and flight system operation systems. So the
maintenance department suddenly received a red hotline phone for the CEO
to call when the UPS failed.

Anything can (and will) fail, and as your story about the VAX improper
manual reboot shows good intentions can turn into epic fails. When I
owned a small business in the mid-80's I was contacted by a local
company in central Texas with a small VAX and CDC disk drive who had a
major failure at his data entry company. He knew he wasn't perfroming
backups so thought it was a good time to perform preventative
maintenance on the physically large CDC removable disk pack drive (with
a huge magnet and large voice coil actuator). The company owner decided
to clean the "sock" disk drive air filter, so he removed it and vacuumed
it off.

He then made a command decision that he should use the clean side of the
filter now (since one side had been filthy) and inverted the sock filter
before reinstalling it. Gasp!! Shortly after the drive spun up a large
dust particle was sucked off the dirty side of the filter (now in the
previously clean drive chamber) and he heard a disk head bouncing around
the inside of the drive. It was (of course) the servo head. Remember
that they had no backups.

The drive was transported to CDC headquarters and they declared it a
lost cause. The small company owner asked me (and probably others) if I
would help him strap a good drive to the bad one and fabricate an arm
between the good and bad drive head acuators so the good drive servo
track would move the bad drive heads (with other required rewiring to
get the drives to work "together"). I told him NO and walked out without
wasting my time explaining how servo tracks really worked and the
mechanical and electrical engineering fallacies in this crazy scheme.
No, I would not take a penny of his money to try any portion any of that
scheme! His company soon went bankrupt, I believe.

--
Bill Byrom N5BB

On Mon, Oct 12, 2015, at 01:28 AM, Bill Hawkins wrote:

My apologies in advance for further putting tension on this OT thread,
but one of the great stories from the early days of Usenet concerned a
really large UPS system for a data center. In the late 80s the Digital
Equipment Corp VAX computer was among the most powerful you could buy.
If you can accept that amount of time travel, follow this link:

http://www.hactrn.net/sra/vaxen.html

or Google "vaxen immortal power"

The reference to October 19, 1987, is to the first computer failure to
have a major effect on the stock market.

Enjoy, as they say

Bill Hawkins


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

HA! That was good. I started working at Tektronix in September 1987 and we used VAX computers in our major field offices for order processing in the late 80's and early 90s. They batched their daily results to our headquarters in Oregon every night on "high speed" modems on special phone lines. We had daily and weekly backups at each office onto open reel tape. The UPS horror story I can relate was at a major airline underground computer center in the 90's. I was waiting to train a group on a high power curve tracer they had purchased to test SCR's every time one of their UPS inverters blew up (which must have been moderately often). I was waiting in the supervisor's office, which had two telephones. One of the was fire engine red, which I thought was reserved for the Hot Line with Russia in Washington. The supervisor told me that if the red phone rang it would be a call directly from the well-known CEO of the airline. It seems that sometime before a worker was using a large wrench (which was not conformally coated) directly above the critical location where the switch between the UPS output nd city power was located. When the wrench fell it shorted the single point of failure in their system, stopping their reservation and flight system operation systems. So the maintenance department suddenly received a red hotline phone for the CEO to call when the UPS failed. Anything can (and will) fail, and as your story about the VAX improper manual reboot shows good intentions can turn into epic fails. When I owned a small business in the mid-80's I was contacted by a local company in central Texas with a small VAX and CDC disk drive who had a major failure at his data entry company. He knew he wasn't perfroming backups so thought it was a good time to perform preventative maintenance on the physically large CDC removable disk pack drive (with a huge magnet and large voice coil actuator). The company owner decided to clean the "sock" disk drive air filter, so he removed it and vacuumed it off. He then made a command decision that he should use the clean side of the filter now (since one side had been filthy) and inverted the sock filter before reinstalling it. Gasp!! Shortly after the drive spun up a large dust particle was sucked off the dirty side of the filter (now in the previously clean drive chamber) and he heard a disk head bouncing around the inside of the drive. It was (of course) the servo head. Remember that they had no backups. The drive was transported to CDC headquarters and they declared it a lost cause. The small company owner asked me (and probably others) if I would help him strap a good drive to the bad one and fabricate an arm between the good and bad drive head acuators so the good drive servo track would move the bad drive heads (with other required rewiring to get the drives to work "together"). I told him NO and walked out without wasting my time explaining how servo tracks really worked and the mechanical and electrical engineering fallacies in this crazy scheme. No, I would not take a penny of his money to try any portion any of that scheme! His company soon went bankrupt, I believe. -- Bill Byrom N5BB On Mon, Oct 12, 2015, at 01:28 AM, Bill Hawkins wrote: > My apologies in advance for further putting tension on this OT thread, > but one of the great stories from the early days of Usenet concerned a > really large UPS system for a data center. In the late 80s the Digital > Equipment Corp VAX computer was among the most powerful you could buy. > If you can accept that amount of time travel, follow this link: > > http://www.hactrn.net/sra/vaxen.html > > or Google "vaxen immortal power" > > The reference to October 19, 1987, is to the first computer failure to > have a major effect on the stock market. > > Enjoy, as they say > > Bill Hawkins > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
PK
Poul-Henning Kamp
Tue, Oct 13, 2015 6:44 AM

Anything can (and will) fail, [...]

The interesting thing is that several sources in that business have
reported to me that about 30-40% of all power related downtime is
caused by Battery, generator and UPS failure, in that order.

Many sites simply have lower uptime after they install UPS systems.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

-------- In message <1444701906.379459.408467601.5676DFA5@webmail.messagingengine.com>, Bill Byrom writes: >Anything can (and will) fail, [...] The interesting thing is that several sources in that business have reported to me that about 30-40% of all power related downtime is caused by Battery, generator and UPS failure, in that order. Many sites simply have lower uptime after they install UPS systems. -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.
TV
Tom Van Baak
Tue, Oct 13, 2015 6:07 PM

I found this UPS article fascinating, because it echoed what I eventually found in my own lab:

http://www.theplatform.net/2015/03/13/how-this-battery-cut-microsoft-datacenter-costs-by-a-quarter/

I used to rely on one massive UPS (along with natural gas generator) for my entire lab. Eventually I found it more reliable and convenient to have localized power backup. By local I mean backup for a single shelf, or even a single instrument.

Consider that many Rb/Cs standards and even some Qz standards have internal batteries. Even if one chooses not to use their internal batteries, most of these instruments still feature dual power inputs. In addition to power redundancy it also makes it easy to move equipment or cables around without power loss. Most importantly, local backup like this avoids the possibility of single-point lab-wide power failures.

Recently, as some of my gear works from 5 VDC, those ~2600 mAh mobile phone USB backup power bricks make an excellent mini-UPS. The ideal models are those without LEDs or on/off buttons so they discharge and charge/float seamlessly without manual intervention, even if fully drained.

Multiple units can be placed in series for additional, if slightly inefficient, capacity. A good self-test is:

http://leapsecond.com/images/perpetual-USB-power.jpg

/tvb

----- Original Message -----
From: "Poul-Henning Kamp" phk@phk.freebsd.dk
To: "Discussion of precise time and frequency measurement" time-nuts@febo.com; "Bill Byrom" time@radio.sent.com
Sent: Monday, October 12, 2015 11:44 PM
Subject: Re: [time-nuts] UPS for my time rack

Anything can (and will) fail, [...]

The interesting thing is that several sources in that business have
reported to me that about 30-40% of all power related downtime is
caused by Battery, generator and UPS failure, in that order.

Many sites simply have lower uptime after they install UPS systems.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

I found this UPS article fascinating, because it echoed what I eventually found in my own lab: http://www.theplatform.net/2015/03/13/how-this-battery-cut-microsoft-datacenter-costs-by-a-quarter/ I used to rely on one massive UPS (along with natural gas generator) for my entire lab. Eventually I found it more reliable and convenient to have localized power backup. By local I mean backup for a single shelf, or even a single instrument. Consider that many Rb/Cs standards and even some Qz standards have internal batteries. Even if one chooses not to use their internal batteries, most of these instruments still feature dual power inputs. In addition to power redundancy it also makes it easy to move equipment or cables around without power loss. Most importantly, local backup like this avoids the possibility of single-point lab-wide power failures. Recently, as some of my gear works from 5 VDC, those ~2600 mAh mobile phone USB backup power bricks make an excellent mini-UPS. The ideal models are those without LEDs or on/off buttons so they discharge and charge/float seamlessly without manual intervention, even if fully drained. Multiple units can be placed in series for additional, if slightly inefficient, capacity. A good self-test is: http://leapsecond.com/images/perpetual-USB-power.jpg /tvb ----- Original Message ----- From: "Poul-Henning Kamp" <phk@phk.freebsd.dk> To: "Discussion of precise time and frequency measurement" <time-nuts@febo.com>; "Bill Byrom" <time@radio.sent.com> Sent: Monday, October 12, 2015 11:44 PM Subject: Re: [time-nuts] UPS for my time rack > -------- > In message <1444701906.379459.408467601.5676DFA5@webmail.messagingengine.com>, > Bill Byrom writes: > >>Anything can (and will) fail, [...] > > The interesting thing is that several sources in that business have > reported to me that about 30-40% of all power related downtime is > caused by Battery, generator and UPS failure, in that order. > > Many sites simply have lower uptime after they install UPS systems. > > -- > Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 > phk@FreeBSD.ORG | TCP/IP since RFC 956 > FreeBSD committer | BSD since 4.3-tahoe > Never attribute to malice what can adequately be explained by incompetence.
PK
Poul-Henning Kamp
Tue, Oct 13, 2015 6:54 PM

In message 4FD0F30EBAEF49609DF207E3EE61C15B@pc52, "Tom Van Baak" writes:

I used to rely on one massive UPS (along with natural gas generator)
for my entire lab. Eventually I found it more reliable and convenient
to have localized power backup. By local I mean backup for a single
shelf, or even a single instrument.

The big gain is avoiding the DC->AC conversions.

AC->DC conversions are covered under EnergyStar and similar programmes,
so they're generally 90% efficient or better.

But DC->AC conversions, for instance in inverters and UPS's are not
covered, the argument going that they are only run very seldomly,
and therefore capital cost would be wasted.

In the professional segment, UPS's which require a forklift,
efficiencies are good, in some cases very good, because power costs
money at that scale.

But anyting you can fit into a rack will typically have horrible
losses, the smaller the UPS the worse.  I've personally measured
sub 50% efficiency in one case.

The argument against running stuff on 12 or 24V DC is the short
circuit currents, and the absense of an affordable standarized
connector.

For the short circuit currents the only cure is fuses and caution,
and for connectors there seems to be no hope of a standard - ever.

China forced USB through as the standard for mobile phones, but
despite several valiant attempts nobody has ever managed to get
anything above 5V/5W standardized.

Here's the website of the IEEE WG which came out with a standard
(IEEE 1823:2015) this May:

http://grouper.ieee.org/groups/msc/upamd/

It will cost you $160 to see the full standard, which is a very
good and strong reason why adoption will be slow, and nobody
I've talked to expects it to go anywhere ever.

At the same time USB has come up with 100W power concept
which is not compatible, since IEEE uses CANbus and different
connectors.

I've not heard any rumours that China man nail this one.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

-------- In message <4FD0F30EBAEF49609DF207E3EE61C15B@pc52>, "Tom Van Baak" writes: >I used to rely on one massive UPS (along with natural gas generator) >for my entire lab. Eventually I found it more reliable and convenient >to have localized power backup. By local I mean backup for a single >shelf, or even a single instrument. The big gain is avoiding the DC->AC conversions. AC->DC conversions are covered under EnergyStar and similar programmes, so they're generally 90% efficient or better. But DC->AC conversions, for instance in inverters and UPS's are not covered, the argument going that they are only run very seldomly, and therefore capital cost would be wasted. In the professional segment, UPS's which require a forklift, efficiencies are good, in some cases very good, because power costs money at that scale. But anyting you can fit into a rack will typically have horrible losses, the smaller the UPS the worse. I've personally measured sub 50% efficiency in one case. The argument against running stuff on 12 or 24V DC is the short circuit currents, and the absense of an affordable standarized connector. For the short circuit currents the only cure is fuses and caution, and for connectors there seems to be no hope of a standard - ever. China forced USB through as the standard for mobile phones, but despite several valiant attempts nobody has ever managed to get anything above 5V/5W standardized. Here's the website of the IEEE WG which came out with a standard (IEEE 1823:2015) this May: http://grouper.ieee.org/groups/msc/upamd/ It will cost you $160 to see the full standard, which is a very good and strong reason why adoption will be slow, and nobody I've talked to expects it to go anywhere ever. At the same time USB has come up with 100W power concept which is not compatible, since IEEE uses CANbus and different connectors. I've not heard any rumours that China man nail this one. -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.