In a message dated 1/9/2008 12:03:02 A.M. Eastern Standard Time,
whitestone1corp@aol.com writes:
Hi all..
?? need help with an old Onan 7.5-MDJE-3CR, it wont shut down with the off
switches, niether the remote panel or the onboard, i have to manually?push the
lever on the injection?pump down to shut the unit off, what could it be
On my Westerbeke The fuel solenoid is pulled in during start and stays there
until you push the stop switch which disrupts the ground and releases the
solenoid. I believe that Onan fuel solenoid is only activated to turn the fuel
off.. The off switches are in series so both switches have to be good for the
circuit to work. Probably the easiest thing to do would be have a helper
check by activating the stop switch while you take readings at the solenoid. That
should help you determine if the solenoid is bad, a bad switch, or wiring in
between.
**************Start the year off right. Easy ways to stay in shape.
http://body.aol.com/fitness/winter-exercise?NCID=aolcmp00300000002489
From: JSpence47@aol.com
I believe that Onan fuel solenoid is only activated to turn the fuel
off.. The off switches are in series so both switches have to be good for
the
circuit to work. Probably the easiest thing to do would be have a helper
check by activating the stop switch while you take readings at the
solenoid.
Actually, if the solenoid is only activated to kill the engine, then the
switches would have to be normaly off, momentary contact switches, and they
would not be in series. They would have to be in parallel. If neither switch
is working, it's probably not a switch, unless by some chance they both went
bad at the same time. More than likely a bad wire, loose contact at the end
of a wire, or bad solenoid.
Brent Hodges
Friendship
43 Albin
Seabrook, Tx
Negative.
On the Onan MDJE the fuel solenoid is energized to provide fuel flow. When
power is interrupted anywhere on the safety circuit, power is cut to the
solenoid shutting off the fuel. I would check the wiring going from the main
panel to the generator. Broken wire, loose connection, something is not
cutting power to the fuel solenoid.
Walt Konieczko
Annie Sez Too
34 Maine Trader (with Onan MDJE)
Lanoka Harbor, NJ
Hi all..
?? need help with an old Onan 7.5-MDJE-3CR, it wont shut down with the
off
switches, niether the remote panel or the onboard, i have to
manually?push the
lever on the injection?pump down to shut the unit off, what could it be
On my Westerbeke The fuel solenoid is pulled in during start and stays
there
until you push the stop switch which disrupts the ground and releases the
solenoid. I believe that Onan fuel solenoid is only activated to turn the
fuel
off.. The off switches are in series so both switches have to be good for
the
circuit to work. Probably the easiest thing to do would be have a helper
check by activating the stop switch while you take readings at the
solenoid. That
should help you determine if the solenoid is bad, a bad switch, or wiring
in
between.