60 Hz measurement party

TV
Tom Van Baak
Sat, Jun 25, 2011 7:34 PM

We are more a group of experimenters than lamenters, so
here's an open invitation to all of you in the US to join me
on a 60 Hz measurement party, starting as soon as you
can and lasting as many weeks or months that it takes to
get interesting plots.

There's no agenda; we measure because we can. Anything
about precise time is fun. There hasn't been a leap second
to watch for a while so this is the next best thing.

The last time I carefully measured 60 Hz was in 2004. See:
http://www.leapsecond.com/pages/mains/

To overcome some questions about that data set, last year I
collected 60 Hz data using a GPSDO PIC that time-stamped
each zero crossing (yes, it's excessive but since when has
that stopped me). I'll restart that now and let it run all summer.

Anyway, you're welcome to use any 60 Hz monitoring method
that you can think of, whether seriously technical or just plain
humorous; clever or Rube Goldberg. Actually, the greater the
variety of methods used the more fun the group project will be.

It could be as simple as noting AC wall clock time once a day
and making a summer plot on the back of an envelope.
Or as weird as integrating the hum of a sound card on a PC
running NTP making MRTG plots. Let your imagination flow.

Please consider contributing to the effort. It seems the last
time anything interesting happened with mains frequency was
when Los Angeles changed from 50 Hz to 60 Hz in 1936.

Thanks,
/tvb
http://www.LeapSecond.com/time-nuts.htm

We are more a group of experimenters than lamenters, so here's an open invitation to all of you in the US to join me on a 60 Hz measurement party, starting as soon as you can and lasting as many weeks or months that it takes to get interesting plots. There's no agenda; we measure because we can. Anything about precise time is fun. There hasn't been a leap second to watch for a while so this is the next best thing. The last time I carefully measured 60 Hz was in 2004. See: http://www.leapsecond.com/pages/mains/ To overcome some questions about that data set, last year I collected 60 Hz data using a GPSDO PIC that time-stamped each zero crossing (yes, it's excessive but since when has that stopped me). I'll restart that now and let it run all summer. Anyway, you're welcome to use any 60 Hz monitoring method that you can think of, whether seriously technical or just plain humorous; clever or Rube Goldberg. Actually, the greater the variety of methods used the more fun the group project will be. It could be as simple as noting AC wall clock time once a day and making a summer plot on the back of an envelope. Or as weird as integrating the hum of a sound card on a PC running NTP making MRTG plots. Let your imagination flow. Please consider contributing to the effort. It seems the last time anything interesting happened with mains frequency was when Los Angeles changed from 50 Hz to 60 Hz in 1936. Thanks, /tvb http://www.LeapSecond.com/time-nuts.htm
MD
Magnus Danielson
Sat, Jun 25, 2011 8:33 PM

On 06/25/2011 09:34 PM, Tom Van Baak wrote:

We are more a group of experimenters than lamenters, so
here's an open invitation to all of you in the US to join me
on a 60 Hz measurement party, starting as soon as you
can and lasting as many weeks or months that it takes to
get interesting plots.

There's no agenda; we measure because we can. Anything
about precise time is fun. There hasn't been a leap second
to watch for a while so this is the next best thing.

The last time I carefully measured 60 Hz was in 2004. See:
http://www.leapsecond.com/pages/mains/

To overcome some questions about that data set, last year I
collected 60 Hz data using a GPSDO PIC that time-stamped
each zero crossing (yes, it's excessive but since when has
that stopped me). I'll restart that now and let it run all summer.

Anyway, you're welcome to use any 60 Hz monitoring method
that you can think of, whether seriously technical or just plain
humorous; clever or Rube Goldberg. Actually, the greater the
variety of methods used the more fun the group project will be.

It could be as simple as noting AC wall clock time once a day
and making a summer plot on the back of an envelope.
Or as weird as integrating the hum of a sound card on a PC
running NTP making MRTG plots. Let your imagination flow.

Please consider contributing to the effort. It seems the last
time anything interesting happened with mains frequency was
when Los Angeles changed from 50 Hz to 60 Hz in 1936.

Great idea Tom!

I'm safely on my 50 Hz grid over here, so I let you guys play around in
your end.

Maybe we should do something on our grid, we are a few time-nuts on the
nordic grid.

Cheers,
Magnus

On 06/25/2011 09:34 PM, Tom Van Baak wrote: > We are more a group of experimenters than lamenters, so > here's an open invitation to all of you in the US to join me > on a 60 Hz measurement party, starting as soon as you > can and lasting as many weeks or months that it takes to > get interesting plots. > > There's no agenda; we measure because we can. Anything > about precise time is fun. There hasn't been a leap second > to watch for a while so this is the next best thing. > > The last time I carefully measured 60 Hz was in 2004. See: > http://www.leapsecond.com/pages/mains/ > > To overcome some questions about that data set, last year I > collected 60 Hz data using a GPSDO PIC that time-stamped > each zero crossing (yes, it's excessive but since when has > that stopped me). I'll restart that now and let it run all summer. > > Anyway, you're welcome to use any 60 Hz monitoring method > that you can think of, whether seriously technical or just plain > humorous; clever or Rube Goldberg. Actually, the greater the > variety of methods used the more fun the group project will be. > > It could be as simple as noting AC wall clock time once a day > and making a summer plot on the back of an envelope. > Or as weird as integrating the hum of a sound card on a PC > running NTP making MRTG plots. Let your imagination flow. > > Please consider contributing to the effort. It seems the last > time anything interesting happened with mains frequency was > when Los Angeles changed from 50 Hz to 60 Hz in 1936. Great idea Tom! I'm safely on my 50 Hz grid over here, so I let you guys play around in your end. Maybe we should do something on our grid, we are a few time-nuts on the nordic grid. Cheers, Magnus
TV
Tom Van Baak
Sat, Jun 25, 2011 11:07 PM

Great idea Tom!

I'm safely on my 50 Hz grid over here, so I let you guys play around in
your end.

Maybe we should do something on our grid, we are a few time-nuts on the
nordic grid.

Cheers,
Magnus

Magnus,

Yes, after the current 60 Hz excitement here in the US winds down
my longer-term idea is for many of us to continuously monitor our
local power frequency with some sort of web-uploading TAPR kit
and then have an informal international TDEV competition. There
are now time-nuts in dozens of countries so this is both possible
and interesting.

You're welcome to collect data on your 50 Hz; it could serve as a
benchmark for us time drifters here in the west.

Extrapolating further, I wonder if anyone has done common view
time transfer based on synchronized power grids? Although not
as precise as LF or TV or GPS methods it would make a nice
demo of the concept.

/tvb

> Great idea Tom! > > I'm safely on my 50 Hz grid over here, so I let you guys play around in > your end. > > Maybe we should do something on our grid, we are a few time-nuts on the > nordic grid. > > Cheers, > Magnus Magnus, Yes, after the current 60 Hz excitement here in the US winds down my longer-term idea is for many of us to continuously monitor our local power frequency with some sort of web-uploading TAPR kit and then have an informal international TDEV competition. There are now time-nuts in dozens of countries so this is both possible and interesting. You're welcome to collect data on your 50 Hz; it could serve as a benchmark for us time drifters here in the west. Extrapolating further, I wonder if anyone has done common view time transfer based on synchronized power grids? Although not as precise as LF or TV or GPS methods it would make a nice demo of the concept. /tvb
MD
Magnus Danielson
Sat, Jun 25, 2011 11:30 PM

Hi Tom,

On 06/26/2011 01:07 AM, Tom Van Baak wrote:

Magnus,

Yes, after the current 60 Hz excitement here in the US winds down
my longer-term idea is for many of us to continuously monitor our
local power frequency with some sort of web-uploading TAPR kit
and then have an informal international TDEV competition. There
are now time-nuts in dozens of countries so this is both possible
and interesting.

You're welcome to collect data on your 50 Hz; it could serve as a
benchmark for us time drifters here in the west.

Extrapolating further, I wonder if anyone has done common view
time transfer based on synchronized power grids? Although not
as precise as LF or TV or GPS methods it would make a nice
demo of the concept.

Infact, Poul-Henning and I had the idea to test this on our grid to see
what kind of performance we would get out of it. He sent me a
transformer prepped for the work, but it seems both of us got caught up
doing other stuff to follow through, but this is a good trigger.

We should recall that IEEE 1588 was originally created to meet the power
industries need for synchronisation. There are players in the PTP world
that became big thanks to the power industry.

Anyway, a suitable measurement set-up would include a GPS, a transformer
for measurement signal, and a simple TIC of choice, such as a PICTIC.
Hook the start pulse to the PPS and the stop pulse to the power grid.
Cycle slips will be easy to see in data (20 ms or 16.67 ms steps) so
compensation and counting is quite easy to do in post-processing.

It could be interesting just to monitor the phase of the L1, L2 and L3
phases of the house. :)

Cheers,
Magnus

Hi Tom, On 06/26/2011 01:07 AM, Tom Van Baak wrote: > Magnus, > > Yes, after the current 60 Hz excitement here in the US winds down > my longer-term idea is for many of us to continuously monitor our > local power frequency with some sort of web-uploading TAPR kit > and then have an informal international TDEV competition. There > are now time-nuts in dozens of countries so this is both possible > and interesting. > > You're welcome to collect data on your 50 Hz; it could serve as a > benchmark for us time drifters here in the west. > > Extrapolating further, I wonder if anyone has done common view > time transfer based on synchronized power grids? Although not > as precise as LF or TV or GPS methods it would make a nice > demo of the concept. Infact, Poul-Henning and I had the idea to test this on our grid to see what kind of performance we would get out of it. He sent me a transformer prepped for the work, but it seems both of us got caught up doing other stuff to follow through, but this is a good trigger. We should recall that IEEE 1588 was originally created to meet the power industries need for synchronisation. There are players in the PTP world that became big thanks to the power industry. Anyway, a suitable measurement set-up would include a GPS, a transformer for measurement signal, and a simple TIC of choice, such as a PICTIC. Hook the start pulse to the PPS and the stop pulse to the power grid. Cycle slips will be easy to see in data (20 ms or 16.67 ms steps) so compensation and counting is quite easy to do in post-processing. It could be interesting just to monitor the phase of the L1, L2 and L3 phases of the house. :) Cheers, Magnus
JL
Jim Lux
Sat, Jun 25, 2011 11:31 PM

Extrapolating further, I wonder if anyone has done common view
time transfer based on synchronized power grids? Although not
as precise as LF or TV or GPS methods it would make a nice
demo of the concept.

/tvb

Interesting idea.. but here's a potential wrench in the works.. the
phase in the "consuming area" is always lagging the phase in the
"sending area"... as the amount of power sent varies, the phase
difference varies.

So, for instance, you're up in the Pacific NW.. generally a "sender" of
power via the Pacific Intertie down to us in the LA area.

What might be interesting is for both of us to measure phase against
some common reference (e.g. GPS) and then do a delta.

Then compare that delta (perhaps integrated over a day?) against the
published power that's been transmitted over the links (CAISO has this
on their website, I think)

There's also a fair amount of phase shift possible between transmission,
through distribution to your house.  Maybe some sort of E/H field pickup
under a HV power line (if that didn't trigger the DHS dragging you away).

The field should be easily detectable. For an exercise when I was
substitute teaching a coworker's EM statics class at Cal State
Northridge, I had them work out whether a) a compass needle would
deflect under the DC link (carrying 3000A), and b)whether you could
measure the current that way.  The general answer is yes and yes,
although it's a lot easier if one of the links is down and they're
running with the ocean return path.

> Extrapolating further, I wonder if anyone has done common view > time transfer based on synchronized power grids? Although not > as precise as LF or TV or GPS methods it would make a nice > demo of the concept. > > /tvb Interesting idea.. but here's a potential wrench in the works.. the phase in the "consuming area" is always lagging the phase in the "sending area"... as the amount of power sent varies, the phase difference varies. So, for instance, you're up in the Pacific NW.. generally a "sender" of power via the Pacific Intertie down to us in the LA area. What might be interesting is for both of us to measure phase against some common reference (e.g. GPS) and then do a delta. Then compare that delta (perhaps integrated over a day?) against the published power that's been transmitted over the links (CAISO has this on their website, I think) There's also a fair amount of phase shift possible between transmission, through distribution to your house. Maybe some sort of E/H field pickup under a HV power line (if that didn't trigger the DHS dragging you away). The field should be easily detectable. For an exercise when I was substitute teaching a coworker's EM statics class at Cal State Northridge, I had them work out whether a) a compass needle would deflect under the DC link (carrying 3000A), and b)whether you could measure the current that way. The general answer is yes and yes, although it's a lot easier if one of the links is down and they're running with the ocean return path.
KP
Kasper Pedersen
Sat, Jun 25, 2011 11:53 PM

On 06/26/2011 01:07 AM, Tom Van Baak wrote:

Extrapolating further, I wonder if anyone has done common view
time transfer based on synchronized power grids? Although not
as precise as LF or TV or GPS methods it would make a nice
demo of the concept.

/tvb

http://n1.taur.dk/plcv/

(with pretty plots. Posted to 'nuts 1.5 years ago)

The two sites were on different 60kV radials, but within the same city.

I wonder what fun things one might deduce by watching the difference in
phase across the continent?

/Kasper Pedersen

The files on the site are pretty old. I still have this in operation to
a time server where I can get the space, power, and bandwidth, but not
the antenna space.

On 06/26/2011 01:07 AM, Tom Van Baak wrote: > Extrapolating further, I wonder if anyone has done common view > time transfer based on synchronized power grids? Although not > as precise as LF or TV or GPS methods it would make a nice > demo of the concept. > > /tvb http://n1.taur.dk/plcv/ (with pretty plots. Posted to 'nuts 1.5 years ago) The two sites were on different 60kV radials, but within the same city. I wonder what fun things one might deduce by watching the difference in phase across the continent? /Kasper Pedersen The files on the site are pretty old. I still have this in operation to a time server where I can get the space, power, and bandwidth, but not the antenna space.
L
lists@lazygranch.com
Sun, Jun 26, 2011 12:18 AM

RDS is a frequency standard?
-----Original Message-----
From: Kasper Pedersen time-nuts@kasperkp.dk
Sender: time-nuts-bounces@febo.com
Date: Sun, 26 Jun 2011 01:53:02
To: time-nuts@febo.com
Reply-To: Discussion of precise time and frequency measurement
time-nuts@febo.com
Subject: Re: [time-nuts] 60 Hz measurement party

On 06/26/2011 01:07 AM, Tom Van Baak wrote:

Extrapolating further, I wonder if anyone has done common view
time transfer based on synchronized power grids? Although not
as precise as LF or TV or GPS methods it would make a nice
demo of the concept.

/tvb

http://n1.taur.dk/plcv/

(with pretty plots. Posted to 'nuts 1.5 years ago)

The two sites were on different 60kV radials, but within the same city.

I wonder what fun things one might deduce by watching the difference in
phase across the continent?

/Kasper Pedersen

The files on the site are pretty old. I still have this in operation to
a time server where I can get the space, power, and bandwidth, but not
the antenna space.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

RDS is a frequency standard? -----Original Message----- From: Kasper Pedersen <time-nuts@kasperkp.dk> Sender: time-nuts-bounces@febo.com Date: Sun, 26 Jun 2011 01:53:02 To: <time-nuts@febo.com> Reply-To: Discussion of precise time and frequency measurement <time-nuts@febo.com> Subject: Re: [time-nuts] 60 Hz measurement party On 06/26/2011 01:07 AM, Tom Van Baak wrote: > Extrapolating further, I wonder if anyone has done common view > time transfer based on synchronized power grids? Although not > as precise as LF or TV or GPS methods it would make a nice > demo of the concept. > > /tvb http://n1.taur.dk/plcv/ (with pretty plots. Posted to 'nuts 1.5 years ago) The two sites were on different 60kV radials, but within the same city. I wonder what fun things one might deduce by watching the difference in phase across the continent? /Kasper Pedersen The files on the site are pretty old. I still have this in operation to a time server where I can get the space, power, and bandwidth, but not the antenna space. _______________________________________________ time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts and follow the instructions there.
MD
Magnus Danielson
Sun, Jun 26, 2011 12:47 AM

On 06/26/2011 02:18 AM, lists@lazygranch.com wrote:

RDS is a frequency standard?

RDS can give time of day, notice how it says "FM radio RDS+pilot CV" so
the 19 kHz pilot tone is used in conjunction with RDS.

The danger in that is that RDS time of day setting may be bogus, since
some broadcasters does not guarantee to steer it even if it happens to
be correct most of the times. The traceability of the pilot tone may
also be bogus. For common view it would kind of work.

Cheers,
Magnus

On 06/26/2011 02:18 AM, lists@lazygranch.com wrote: > RDS is a frequency standard? RDS can give time of day, notice how it says "FM radio RDS+pilot CV" so the 19 kHz pilot tone is used in conjunction with RDS. The danger in that is that RDS time of day setting may be bogus, since some broadcasters does not guarantee to steer it even if it happens to be correct most of the times. The traceability of the pilot tone may also be bogus. For common view it would kind of work. Cheers, Magnus
PK
Poul-Henning Kamp
Sun, Jun 26, 2011 5:38 PM

In message 4E066FAC.5090709@rubidium.dyndns.org, Magnus Danielson writes:

Infact, Poul-Henning and I had the idea to test this on our grid to see
what kind of performance we would get out of it. He sent me a
transformer prepped for the work, but it seems both of us got caught up
doing other stuff to follow through, but this is a good trigger.

Yeah, life, don't talk to me about life... :-)

Actually what I wanted to measure back then was the phase-stiffness
of the grid between us.

This may be relevant to Tom's experiment as well, and in particular
to those of you living in California, so let me explain what it is:

Imagine two time-nuts, N1 and N2, two generators G1 and G2 and
various chains of transformators T1a... and T2a... in the same
powergrid but some n*100km apart.

G1 --- T1a -+- T1b ------------------------T2b -+- T2a --- G2
|                                  |
T1c                                T2c
|                                  |
N1                                  N2

If all the power is generated by G1, the absolute GPS relative
phase seen at N1, depends on G1, T1a and T1c, which N2 sees
the combined effects og G1, T1a, T1b, T2b, T2c.  When G2 produces
all the power, the picture reverses and when G1 and G2 each produce
half the phase difference btween N1 and N2 should be constant.

(But not zero, because they may not be on the same of the three
phases and because grid transformers shifts phases around to match
things up.  Long story, not for today.)

Which way you push power through T1b and T2b affects what they do
to the phase of the grid on either side so the phase difference
seen between N1 and N2 depends on how power flows in the grid.

The reason everybody in the same grid sees the same frequency, is
that when you have a big heavy generator, frequency is a usable
proxy measurements for energy.

If you add an electrical load, the generator have to produce more
electricity which takes more mechanical work causing the
turbine to slow down.  And vice versa.

Typically, a frequency deviation of as little as 0.02 % will cause
regulation of turbine steam.

Load changes also cause the voltage to change, but this is much
less pronounced and much harder to measure/regulate with, primarily
because of the very noisy measurements.

So the power-grid basically doesn't use voltage for regulation.
Various mechanisms keep the voltage inside a +/- 10% tolerance
at various points and that's that.

With me so far ?

All this breaks down once we start adding power-producers which
are not based on huge rotating lumps of copper-ensnarled iron.

Solar cells, wind generators, HVDC transmission, electrical cars
feeding battery power and all these other fancy modern things, feed
power into the grid with a computer controlled switch mode gadget
which just tracks whatever phase and frequency your grid has right
now.

When the frequency changes on one of these switchmodes, they just
follow the grid, they do not try to join in on the "voting" on
the frequency by trying to pull the grid ahead or behind depending
on their power-state.

As the grid moves from big rotating lumps of iron to switch mode
attachment, a larger and larger fraction of the generation capacity
free-wheels in the frequency 'voting'.

At some point, the system will no longer be stable, and something
has to happen.

My particular corner of the world is ground-zero for this, because
we generate 1/5th of our electricity with windmills and have
relatively little rotating machinery running in good winds.

So far, we are not approaching instability, at least not so that
anybody will admit it.

But the way to tell if instability is approaching, is to monitor
the phase difference between N1 and N2 as explained above, the
larger variations and the more resonance frequencies manifest
themselves therein, the more you should get involved in local
power-politics.

The future of grid regulation is to move to a "absolute frequency"
model, where the frequency is UTC-locked through-out the grid, and
regulation happens only on voltage.

There is a lot of fancy technology involved in this, and som scary
propositions about what we can and can not do with "holistic grid
regulation" and other such buzzwords.

Really long term, Edison will win and long-haul electricity will
all happen on HVDC lines.  When we get buck/boost converters working
directly on HVDC, everything will be much simpler and stabler, so
people are seriously dragging their feet.

My idea for measuring this, was to measure the time from the
utc second from a GPS receiver to the first zero-crossing of
the grid, and try plot Magnus and my measurements together.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

In message <4E066FAC.5090709@rubidium.dyndns.org>, Magnus Danielson writes: >Infact, Poul-Henning and I had the idea to test this on our grid to see >what kind of performance we would get out of it. He sent me a >transformer prepped for the work, but it seems both of us got caught up >doing other stuff to follow through, but this is a good trigger. Yeah, life, don't talk to me about life... :-) Actually what I wanted to measure back then was the phase-stiffness of the grid between us. This may be relevant to Tom's experiment as well, and in particular to those of you living in California, so let me explain what it is: Imagine two time-nuts, N1 and N2, two generators G1 and G2 and various chains of transformators T1a... and T2a... in the same powergrid but some n*100km apart. G1 --- T1a -+- T1b ------------------------T2b -+- T2a --- G2 | | T1c T2c | | N1 N2 If all the power is generated by G1, the absolute GPS relative phase seen at N1, depends on G1, T1a and T1c, which N2 sees the combined effects og G1, T1a, T1b, T2b, T2c. When G2 produces all the power, the picture reverses and when G1 and G2 each produce half the phase difference btween N1 and N2 should be constant. (But not zero, because they may not be on the same of the three phases and because grid transformers shifts phases around to match things up. Long story, not for today.) Which way you push power through T1b and T2b affects what they do to the phase of the grid on either side so the phase difference seen between N1 and N2 depends on how power flows in the grid. The reason everybody in the same grid sees the same frequency, is that when you have a big heavy generator, frequency is a usable proxy measurements for energy. If you add an electrical load, the generator have to produce more electricity which takes more mechanical work causing the turbine to slow down. And vice versa. Typically, a frequency deviation of as little as 0.02 % will cause regulation of turbine steam. Load changes also cause the voltage to change, but this is much less pronounced and much harder to measure/regulate with, primarily because of the very noisy measurements. So the power-grid basically doesn't use voltage for regulation. Various mechanisms keep the voltage inside a +/- 10% tolerance at various points and that's that. With me so far ? All this breaks down once we start adding power-producers which are not based on huge rotating lumps of copper-ensnarled iron. Solar cells, wind generators, HVDC transmission, electrical cars feeding battery power and all these other fancy modern things, feed power into the grid with a computer controlled switch mode gadget which just tracks whatever phase and frequency your grid has right now. When the frequency changes on one of these switchmodes, they just follow the grid, they do not try to join in on the "voting" on the frequency by trying to pull the grid ahead or behind depending on their power-state. As the grid moves from big rotating lumps of iron to switch mode attachment, a larger and larger fraction of the generation capacity free-wheels in the frequency 'voting'. At some point, the system will no longer be stable, and something has to happen. My particular corner of the world is ground-zero for this, because we generate 1/5th of our electricity with windmills and have relatively little rotating machinery running in good winds. So far, we are not approaching instability, at least not so that anybody will admit it. But the way to tell if instability is approaching, is to monitor the phase difference between N1 and N2 as explained above, the larger variations and the more resonance frequencies manifest themselves therein, the more you should get involved in local power-politics. The future of grid regulation is to move to a "absolute frequency" model, where the frequency is UTC-locked through-out the grid, and regulation happens only on voltage. There is a lot of fancy technology involved in this, and som scary propositions about what we can and can not do with "holistic grid regulation" and other such buzzwords. Really long term, Edison will win and long-haul electricity will all happen on HVDC lines. When we get buck/boost converters working directly on HVDC, everything will be much simpler and stabler, so people are seriously dragging their feet. My idea for measuring this, was to measure the time from the utc second from a GPS receiver to the first zero-crossing of the grid, and try plot Magnus and my measurements together. -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.
WM
Will Matney
Sun, Jun 26, 2011 6:10 PM

I quite like your generator description of "huge rotating lumps of
copper-ensnarled iron". It brings me back to around 20 years ago, when I
was a plant electrician at an older railcar manufacturer. They had huge
open-frame synchronous motors, from around the 1930's, that ran their air
compressors, and why they used this type of motor is anybodies guess. If I
remember right, they were rated at around 200 HP, or so, and were about 8
feet in diameter. The rotor shaft was mounted on huge babbit bearings upon
concrete pillars, and about 1/3 of the motor sat in a pit in the concrete
floor. I used to have to repair the brushes on the slip rings constantly,
until I talked the boss into adding a shunt across the n.o. contacts on the
250 Vdc contactors to quench any arcing. The motors stator itself ran on
4160 Vac. Would the other compressors have to run in sync somehow, as all
of them had these motors, just some a little smaller than the others? They
drove large single cylinder compressors that fed something like a 6 inch
air line (pipe). However, they all did not run at once, and they only did
when there was a larger demand for air. Timing is the only thing I can lay
this to, and was wondering about it.

Best,

Will

*********** REPLY SEPARATOR  ***********

On 6/26/2011 at 5:38 PM Poul-Henning Kamp wrote:

In message 4E066FAC.5090709@rubidium.dyndns.org, Magnus Danielson

writes:

Infact, Poul-Henning and I had the idea to test this on our grid to see
what kind of performance we would get out of it. He sent me a
transformer prepped for the work, but it seems both of us got caught up
doing other stuff to follow through, but this is a good trigger.

Yeah, life, don't talk to me about life... :-)

Actually what I wanted to measure back then was the phase-stiffness
of the grid between us.

This may be relevant to Tom's experiment as well, and in particular
to those of you living in California, so let me explain what it is:

Imagine two time-nuts, N1 and N2, two generators G1 and G2 and
various chains of transformators T1a... and T2a... in the same
powergrid but some n*100km apart.

G1 --- T1a -+- T1b ------------------------T2b -+- T2a --- G2
|                                  |
T1c                                T2c
|                                  |
N1                                  N2

If all the power is generated by G1, the absolute GPS relative
phase seen at N1, depends on G1, T1a and T1c, which N2 sees
the combined effects og G1, T1a, T1b, T2b, T2c.  When G2 produces
all the power, the picture reverses and when G1 and G2 each produce
half the phase difference btween N1 and N2 should be constant.

(But not zero, because they may not be on the same of the three
phases and because grid transformers shifts phases around to match
things up.  Long story, not for today.)

Which way you push power through T1b and T2b affects what they do
to the phase of the grid on either side so the phase difference
seen between N1 and N2 depends on how power flows in the grid.

The reason everybody in the same grid sees the same frequency, is
that when you have a big heavy generator, frequency is a usable
proxy measurements for energy.

If you add an electrical load, the generator have to produce more
electricity which takes more mechanical work causing the
turbine to slow down.  And vice versa.

Typically, a frequency deviation of as little as 0.02 % will cause
regulation of turbine steam.

Load changes also cause the voltage to change, but this is much
less pronounced and much harder to measure/regulate with, primarily
because of the very noisy measurements.

So the power-grid basically doesn't use voltage for regulation.
Various mechanisms keep the voltage inside a +/- 10% tolerance
at various points and that's that.

With me so far ?

All this breaks down once we start adding power-producers which
are not based on huge rotating lumps of copper-ensnarled iron.

Solar cells, wind generators, HVDC transmission, electrical cars
feeding battery power and all these other fancy modern things, feed
power into the grid with a computer controlled switch mode gadget
which just tracks whatever phase and frequency your grid has right
now.

When the frequency changes on one of these switchmodes, they just
follow the grid, they do not try to join in on the "voting" on
the frequency by trying to pull the grid ahead or behind depending
on their power-state.

As the grid moves from big rotating lumps of iron to switch mode
attachment, a larger and larger fraction of the generation capacity
free-wheels in the frequency 'voting'.

At some point, the system will no longer be stable, and something
has to happen.

My particular corner of the world is ground-zero for this, because
we generate 1/5th of our electricity with windmills and have
relatively little rotating machinery running in good winds.

So far, we are not approaching instability, at least not so that
anybody will admit it.

But the way to tell if instability is approaching, is to monitor
the phase difference between N1 and N2 as explained above, the
larger variations and the more resonance frequencies manifest
themselves therein, the more you should get involved in local
power-politics.

The future of grid regulation is to move to a "absolute frequency"
model, where the frequency is UTC-locked through-out the grid, and
regulation happens only on voltage.

There is a lot of fancy technology involved in this, and som scary
propositions about what we can and can not do with "holistic grid
regulation" and other such buzzwords.

Really long term, Edison will win and long-haul electricity will
all happen on HVDC lines.  When we get buck/boost converters working
directly on HVDC, everything will be much simpler and stabler, so
people are seriously dragging their feet.

My idea for measuring this, was to measure the time from the
utc second from a GPS receiver to the first zero-crossing of
the grid, and try plot Magnus and my measurements together.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by

incompetence.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.

__________ Information from ESET Smart Security, version of virus

signature database 5851 (20110206) __________

The message was checked by ESET Smart Security.

http://www.eset.com

I quite like your generator description of "huge rotating lumps of copper-ensnarled iron". It brings me back to around 20 years ago, when I was a plant electrician at an older railcar manufacturer. They had huge open-frame synchronous motors, from around the 1930's, that ran their air compressors, and why they used this type of motor is anybodies guess. If I remember right, they were rated at around 200 HP, or so, and were about 8 feet in diameter. The rotor shaft was mounted on huge babbit bearings upon concrete pillars, and about 1/3 of the motor sat in a pit in the concrete floor. I used to have to repair the brushes on the slip rings constantly, until I talked the boss into adding a shunt across the n.o. contacts on the 250 Vdc contactors to quench any arcing. The motors stator itself ran on 4160 Vac. Would the other compressors have to run in sync somehow, as all of them had these motors, just some a little smaller than the others? They drove large single cylinder compressors that fed something like a 6 inch air line (pipe). However, they all did not run at once, and they only did when there was a larger demand for air. Timing is the only thing I can lay this to, and was wondering about it. Best, Will *********** REPLY SEPARATOR *********** On 6/26/2011 at 5:38 PM Poul-Henning Kamp wrote: >In message <4E066FAC.5090709@rubidium.dyndns.org>, Magnus Danielson writes: > >>Infact, Poul-Henning and I had the idea to test this on our grid to see >>what kind of performance we would get out of it. He sent me a >>transformer prepped for the work, but it seems both of us got caught up >>doing other stuff to follow through, but this is a good trigger. > >Yeah, life, don't talk to me about life... :-) > >Actually what I wanted to measure back then was the phase-stiffness >of the grid between us. > >This may be relevant to Tom's experiment as well, and in particular >to those of you living in California, so let me explain what it is: > >Imagine two time-nuts, N1 and N2, two generators G1 and G2 and >various chains of transformators T1a... and T2a... in the same >powergrid but some n*100km apart. > > >G1 --- T1a -+- T1b ------------------------T2b -+- T2a --- G2 > | | > T1c T2c > | | > N1 N2 > >If all the power is generated by G1, the absolute GPS relative >phase seen at N1, depends on G1, T1a and T1c, which N2 sees >the combined effects og G1, T1a, T1b, T2b, T2c. When G2 produces >all the power, the picture reverses and when G1 and G2 each produce >half the phase difference btween N1 and N2 should be constant. > >(But not zero, because they may not be on the same of the three >phases and because grid transformers shifts phases around to match >things up. Long story, not for today.) > >Which way you push power through T1b and T2b affects what they do >to the phase of the grid on either side so the phase difference >seen between N1 and N2 depends on how power flows in the grid. > >The reason everybody in the same grid sees the same frequency, is >that when you have a big heavy generator, frequency is a usable >proxy measurements for energy. > >If you add an electrical load, the generator have to produce more >electricity which takes more mechanical work causing the >turbine to slow down. And vice versa. > >Typically, a frequency deviation of as little as 0.02 % will cause >regulation of turbine steam. > >Load changes also cause the voltage to change, but this is much >less pronounced and much harder to measure/regulate with, primarily >because of the very noisy measurements. > >So the power-grid basically doesn't use voltage for regulation. >Various mechanisms keep the voltage inside a +/- 10% tolerance >at various points and that's that. > >With me so far ? > >All this breaks down once we start adding power-producers which >are not based on huge rotating lumps of copper-ensnarled iron. > >Solar cells, wind generators, HVDC transmission, electrical cars >feeding battery power and all these other fancy modern things, feed >power into the grid with a computer controlled switch mode gadget >which just tracks whatever phase and frequency your grid has right >now. > >When the frequency changes on one of these switchmodes, they just >follow the grid, they do not try to join in on the "voting" on >the frequency by trying to pull the grid ahead or behind depending >on their power-state. > >As the grid moves from big rotating lumps of iron to switch mode >attachment, a larger and larger fraction of the generation capacity >free-wheels in the frequency 'voting'. > >At some point, the system will no longer be stable, and something >has to happen. > >My particular corner of the world is ground-zero for this, because >we generate 1/5th of our electricity with windmills and have >relatively little rotating machinery running in good winds. > >So far, we are not approaching instability, at least not so that >anybody will admit it. > >But the way to tell if instability is approaching, is to monitor >the phase difference between N1 and N2 as explained above, the >larger variations and the more resonance frequencies manifest >themselves therein, the more you should get involved in local >power-politics. > > >The future of grid regulation is to move to a "absolute frequency" >model, where the frequency is UTC-locked through-out the grid, and >regulation happens only on voltage. > >There is a lot of fancy technology involved in this, and som scary >propositions about what we can and can not do with "holistic grid >regulation" and other such buzzwords. > >Really long term, Edison will win and long-haul electricity will >all happen on HVDC lines. When we get buck/boost converters working >directly on HVDC, everything will be much simpler and stabler, so >people are seriously dragging their feet. > >My idea for measuring this, was to measure the time from the >utc second from a GPS receiver to the first zero-crossing of >the grid, and try plot Magnus and my measurements together. > >-- >Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 >phk@FreeBSD.ORG | TCP/IP since RFC 956 >FreeBSD committer | BSD since 4.3-tahoe >Never attribute to malice what can adequately be explained by incompetence. > >_______________________________________________ >time-nuts mailing list -- time-nuts@febo.com >To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >and follow the instructions there. > >__________ Information from ESET Smart Security, version of virus signature database 5851 (20110206) __________ > >The message was checked by ESET Smart Security. > >http://www.eset.com
JL
Jim Lux
Sun, Jun 26, 2011 11:24 PM

On 6/26/11 10:38 AM, Poul-Henning Kamp wrote:

My idea for measuring this, was to measure the time from the
utc second from a GPS receiver to the first zero-crossing of
the grid, and try plot Magnus and my measurements together.

So, to make this easy on folks..

Seems the easiest PC hardware thing would be to use a sound card input..
left input is the 1pps, right input is 50/60Hz derived from some local
source (a wire hanging out is probably enough, but noisy.. a transformer
or capacitor coupling from power line would be better)..

We could have a little application that runs and grabs, say, 10 seconds
worth of sound card data, figures out the phase, and logs it (or does a
cURL to send it to a website as a HTTP POST).

Even better would be a little dedicated widget that does it.  I wonder
if one of those sub-$100 retail plug in servers (like the POGO plug)
could do it.

I think if we could make the "end user price" <$100, and it's truly plug
and play (i.e. not a "get this from place A, and find part B surplus,
and make a cable, etc.), we could probably get a bunch of people to just
try it.  I sure would, and I know a bunch of people at work for which
this is in the "yeah, I'd do it as a toy" kind of category, as long as
it's less than, say, a couple hours to fool with it.

On 6/26/11 10:38 AM, Poul-Henning Kamp wrote: > My idea for measuring this, was to measure the time from the > utc second from a GPS receiver to the first zero-crossing of > the grid, and try plot Magnus and my measurements together. > So, to make this easy on folks.. Seems the easiest PC hardware thing would be to use a sound card input.. left input is the 1pps, right input is 50/60Hz derived from some local source (a wire hanging out is probably enough, but noisy.. a transformer or capacitor coupling from power line would be better).. We could have a little application that runs and grabs, say, 10 seconds worth of sound card data, figures out the phase, and logs it (or does a cURL to send it to a website as a HTTP POST). Even better would be a little dedicated widget that does it. I wonder if one of those sub-$100 retail plug in servers (like the POGO plug) could do it. I think if we could make the "end user price" <$100, and it's truly plug and play (i.e. not a "get this from place A, and find part B surplus, and make a cable, etc.), we could probably get a bunch of people to just try it. I sure would, and I know a bunch of people at work for which this is in the "yeah, I'd do it as a toy" kind of category, as long as it's less than, say, a couple hours to fool with it.
TA
Thomas A Frank
Mon, Jun 27, 2011 1:29 AM

On Jun 25, 2011, at 7:31 PM, Jim Lux wrote:

although it's a lot easier if one of the links is down and they're running with the ocean return path.

Ocean return path?  Please say more.

I picture a gigantic carbon electrode stuck in the ocean by a power station - rather like the core of a really large "D" cell.

That sounds like a recipe for excitement - DC current into seawater should generate hydrogen on one and and oxygen on the other electrode.  At 3000 amps, rather a lot of it.

As for monitoring 60 Hz, I was doing some on line research, and found some interesting power line frequency meters at:

http://www.laurels.com/frequency.htm

Surprisingly affordable (less than $300).

Tom Frank

On Jun 25, 2011, at 7:31 PM, Jim Lux wrote: > although it's a lot easier if one of the links is down and they're running with the ocean return path. Ocean return path? Please say more. I picture a gigantic carbon electrode stuck in the ocean by a power station - rather like the core of a really large "D" cell. That sounds like a recipe for excitement - DC current into seawater should generate hydrogen on one and and oxygen on the other electrode. At 3000 amps, rather a lot of it. As for monitoring 60 Hz, I was doing some on line research, and found some interesting power line frequency meters at: http://www.laurels.com/frequency.htm Surprisingly affordable (less than $300). Tom Frank
TV
Tom Van Baak
Mon, Jun 27, 2011 3:02 AM

As for monitoring 60 Hz, I was doing some on line research, and found some interesting power line frequency meters at:

http://www.laurels.com/frequency.htm

Surprisingly affordable (less than $300).

Tom Frank

For this experiment you want an [accumulated] phase error meter,
not a line frequency meter. Remember, NERC is not dramatically
changing the 60 Hz frequency; the proposal is simply to eliminate
the steering that used to keep the cycles roughly aligned with UTC.

So a 3 or 4 or 5 digit sampling frequency counter will not reveal
the change. But over hours or days a mains connected kitchen
clock compared with your cell phone, will. In general, to see the
effect, you want something that faithfully tracks the phase and
compares it to a reference that's at least 1 ppm accurate.

Another approach, the one I use, is to continuously compare
60 Hz phase against UTC using a TIC, handling rollovers, etc.

/tvb

> As for monitoring 60 Hz, I was doing some on line research, and found some interesting power line frequency meters at: > > http://www.laurels.com/frequency.htm > > Surprisingly affordable (less than $300). > > Tom Frank For this experiment you want an [accumulated] phase error meter, not a line frequency meter. Remember, NERC is not dramatically changing the 60 Hz frequency; the proposal is simply to eliminate the steering that used to keep the cycles roughly aligned with UTC. So a 3 or 4 or 5 digit sampling frequency counter will not reveal the change. But over hours or days a mains connected kitchen clock compared with your cell phone, will. In general, to see the effect, you want something that faithfully tracks the phase and compares it to a reference that's at least 1 ppm accurate. Another approach, the one I use, is to continuously compare 60 Hz phase against UTC using a TIC, handling rollovers, etc. /tvb
BH
Bill Hawkins
Mon, Jun 27, 2011 3:12 AM

Will, and the rest of you fascinated by power distribution,

A big synchronous motor allows its power factor to be changed by
changing the field current for a given load. The motor can be
adjusted to look like a resistive load instead of inductive, or
even capacitive to correct plant power factor. Look it up.

Industrial power consumers are charged extra for power factors
less than unity because the distribution system must carry more
current for the same watts as the power factor departs from
unity.

Induction motors have inductive power factors because there must
be slip between the rotating field and the speed of the rotor.
Synchronous motors don't have slip, just phase angle. Zero angle
looks like a resistive load, yes?

The compressors don't have to run in sync.

Best,
Bill Hawkins
(who heaves a nostalgic sigh just thinking about those fine old
engines of progress)

-----Original Message-----
From: Will Matney
Sent: Sunday, June 26, 2011 1:11 PM
To: time-nuts@febo.com
Subject: Re: [time-nuts] 60 Hz measurement party

I quite like your generator description of "huge rotating lumps of
copper-ensnarled iron". It brings me back to around 20 years ago, when I
was a plant electrician at an older railcar manufacturer. They had huge
open-frame synchronous motors, from around the 1930's, that ran their air
compressors, and why they used this type of motor is anybodies guess. If I
remember right, they were rated at around 200 HP, or so, and were about 8
feet in diameter. The rotor shaft was mounted on huge babbit bearings upon
concrete pillars, and about 1/3 of the motor sat in a pit in the concrete
floor. I used to have to repair the brushes on the slip rings constantly,
until I talked the boss into adding a shunt across the n.o. contacts on the
250 Vdc contactors to quench any arcing. The motors stator itself ran on
4160 Vac. Would the other compressors have to run in sync somehow, as all
of them had these motors, just some a little smaller than the others? They
drove large single cylinder compressors that fed something like a 6 inch
air line (pipe). However, they all did not run at once, and they only did
when there was a larger demand for air. Timing is the only thing I can lay
this to, and was wondering about it.

Best,

Will

Will, and the rest of you fascinated by power distribution, A big synchronous motor allows its power factor to be changed by changing the field current for a given load. The motor can be adjusted to look like a resistive load instead of inductive, or even capacitive to correct plant power factor. Look it up. Industrial power consumers are charged extra for power factors less than unity because the distribution system must carry more current for the same watts as the power factor departs from unity. Induction motors have inductive power factors because there must be slip between the rotating field and the speed of the rotor. Synchronous motors don't have slip, just phase angle. Zero angle looks like a resistive load, yes? The compressors don't have to run in sync. Best, Bill Hawkins (who heaves a nostalgic sigh just thinking about those fine old engines of progress) -----Original Message----- From: Will Matney Sent: Sunday, June 26, 2011 1:11 PM To: time-nuts@febo.com Subject: Re: [time-nuts] 60 Hz measurement party I quite like your generator description of "huge rotating lumps of copper-ensnarled iron". It brings me back to around 20 years ago, when I was a plant electrician at an older railcar manufacturer. They had huge open-frame synchronous motors, from around the 1930's, that ran their air compressors, and why they used this type of motor is anybodies guess. If I remember right, they were rated at around 200 HP, or so, and were about 8 feet in diameter. The rotor shaft was mounted on huge babbit bearings upon concrete pillars, and about 1/3 of the motor sat in a pit in the concrete floor. I used to have to repair the brushes on the slip rings constantly, until I talked the boss into adding a shunt across the n.o. contacts on the 250 Vdc contactors to quench any arcing. The motors stator itself ran on 4160 Vac. Would the other compressors have to run in sync somehow, as all of them had these motors, just some a little smaller than the others? They drove large single cylinder compressors that fed something like a 6 inch air line (pipe). However, they all did not run at once, and they only did when there was a larger demand for air. Timing is the only thing I can lay this to, and was wondering about it. Best, Will
JL
Jim Lux
Mon, Jun 27, 2011 3:23 AM

On 6/26/11 6:29 PM, Thomas A Frank wrote:

On Jun 25, 2011, at 7:31 PM, Jim Lux wrote:

although it's a lot easier if one of the links is down and they're running with the ocean return path.

Ocean return path?  Please say more.

I picture a gigantic carbon electrode stuck in the ocean by a power station - rather like the core of a really large "D" cell.

Not far from the truth, actually..  cast iron electrodes at the north
end buried in a 2 mile diameter ring.  iron alloy electrodes in concrete
in the ocean at the south end..

Electrodes  :

           At Celilo : the ground electrode is located 10.6 km from 

the converter station, in Rice Flates. The electrode is designed as a
ring type 3255 m circumference, 1067 cast iron anodes, and 2' X 2' coke
backfill is used. Total resistance in 2 parallel electrode lines and
ground electrode = 0.43 ohms.

           At Sylmar : the sea electrode is located 48 km from the 

converter station, in the Pacific Ocean and consists of a linear array
of 24 horizontal electrode elements made up of silicon-iron alloy rods
suspended 0.5 to 1 m above the ocean bottom and located within concrete
enclosures. Total resistance in 2 parallel electrode lines and sea
electrode = 1.13 ohms.

That sounds like a recipe for excitement - DC current into seawater should generate hydrogen on one and and oxygen on the other electrode.  At 3000 amps, rather a lot of it.

I imagine they keep the current density low enough that the gas is
absorbed into the water as it's evolved.  But yes.. a fascinating concept.

And I'm curious where, exactly, that DC line to the ocean runs.  (since
I live between Sylmar and the ocean, as do about 10 million other people)

I guess I can draw a circle of radius 48km  from Sylmar..

At Sylmar : 2 X 644 mm2 ACSR conductors in parallel are used for the
first 35 km, supported by the 230 kV line towers. For the remaining 13
km, two parallel paper-insulated underground cables are used, each with
a 633 mm2 Cu-conductor.

I just have to look for a set of towers with a single duplex cable.

(actually a bit of googling found a report

www.kentercanyon.org/index.php/download-public-docs/doc/25/raw

)

On 6/26/11 6:29 PM, Thomas A Frank wrote: > > On Jun 25, 2011, at 7:31 PM, Jim Lux wrote: > >> although it's a lot easier if one of the links is down and they're running with the ocean return path. > > > Ocean return path? Please say more. > > I picture a gigantic carbon electrode stuck in the ocean by a power station - rather like the core of a really large "D" cell. > Not far from the truth, actually.. cast iron electrodes at the north end buried in a 2 mile diameter ring. iron alloy electrodes in concrete in the ocean at the south end.. Electrodes : At Celilo : the ground electrode is located 10.6 km from the converter station, in Rice Flates. The electrode is designed as a ring type 3255 m circumference, 1067 cast iron anodes, and 2' X 2' coke backfill is used. Total resistance in 2 parallel electrode lines and ground electrode = 0.43 ohms. At Sylmar : the sea electrode is located 48 km from the converter station, in the Pacific Ocean and consists of a linear array of 24 horizontal electrode elements made up of silicon-iron alloy rods suspended 0.5 to 1 m above the ocean bottom and located within concrete enclosures. Total resistance in 2 parallel electrode lines and sea electrode = 1.13 ohms. > That sounds like a recipe for excitement - DC current into seawater should generate hydrogen on one and and oxygen on the other electrode. At 3000 amps, rather a lot of it. > I imagine they keep the current density low enough that the gas is absorbed into the water as it's evolved. But yes.. a fascinating concept. And I'm curious where, exactly, that DC line to the ocean runs. (since I live between Sylmar and the ocean, as do about 10 million other people) I guess I can draw a circle of radius 48km from Sylmar.. At Sylmar : 2 X 644 mm2 ACSR conductors in parallel are used for the first 35 km, supported by the 230 kV line towers. For the remaining 13 km, two parallel paper-insulated underground cables are used, each with a 633 mm2 Cu-conductor. I just have to look for a set of towers with a single duplex cable. (actually a bit of googling found a report www.kentercanyon.org/index.php/download-public-docs/doc/25/raw )
WM
Will Matney
Mon, Jun 27, 2011 3:30 AM

Bill,

I never did set back and think why they used them, but that would make
sense. The new plant engineer they hired, during my time there, talked them
into installing a new power house (air compressor system) in the paint
department. However, he had ordered screw compressors, running on 460 V, 3
phase motors. He was cursed by every electrician on that job over the big
cables that had to be pulled for the current they consumed.

I also wondered if it could have had something to do with the starting
torque of the sync motors over induction motors. Those old compressors had
flywheels on them almost the diameter of the motors that ran them, and it
would take a huge amount of torque to set them to turning, especially when
the compressor was pumping into a pipe full of compressed air. It would be
about like trying to start or run the engine in your car with the tail pipe
stopped up.

Thanks,

Will

*********** REPLY SEPARATOR  ***********

On 6/26/2011 at 10:12 PM Bill Hawkins wrote:

Will, and the rest of you fascinated by power distribution,

A big synchronous motor allows its power factor to be changed by
changing the field current for a given load. The motor can be
adjusted to look like a resistive load instead of inductive, or
even capacitive to correct plant power factor. Look it up.

Industrial power consumers are charged extra for power factors
less than unity because the distribution system must carry more
current for the same watts as the power factor departs from
unity.

Induction motors have inductive power factors because there must
be slip between the rotating field and the speed of the rotor.
Synchronous motors don't have slip, just phase angle. Zero angle
looks like a resistive load, yes?

The compressors don't have to run in sync.

Best,
Bill Hawkins
(who heaves a nostalgic sigh just thinking about those fine old
engines of progress)

-----Original Message-----
From: Will Matney
Sent: Sunday, June 26, 2011 1:11 PM
To: time-nuts@febo.com
Subject: Re: [time-nuts] 60 Hz measurement party

I quite like your generator description of "huge rotating lumps of
copper-ensnarled iron". It brings me back to around 20 years ago, when I
was a plant electrician at an older railcar manufacturer. They had huge
open-frame synchronous motors, from around the 1930's, that ran their air
compressors, and why they used this type of motor is anybodies guess. If I
remember right, they were rated at around 200 HP, or so, and were about 8
feet in diameter. The rotor shaft was mounted on huge babbit bearings upon
concrete pillars, and about 1/3 of the motor sat in a pit in the concrete
floor. I used to have to repair the brushes on the slip rings constantly,
until I talked the boss into adding a shunt across the n.o. contacts on

the

250 Vdc contactors to quench any arcing. The motors stator itself ran on
4160 Vac. Would the other compressors have to run in sync somehow, as all
of them had these motors, just some a little smaller than the others? They
drove large single cylinder compressors that fed something like a 6 inch
air line (pipe). However, they all did not run at once, and they only did
when there was a larger demand for air. Timing is the only thing I can lay
this to, and was wondering about it.

Best,

Will


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.

__________ Information from ESET Smart Security, version of virus

signature database 5851 (20110206) __________

The message was checked by ESET Smart Security.

http://www.eset.com

Bill, I never did set back and think why they used them, but that would make sense. The new plant engineer they hired, during my time there, talked them into installing a new power house (air compressor system) in the paint department. However, he had ordered screw compressors, running on 460 V, 3 phase motors. He was cursed by every electrician on that job over the big cables that had to be pulled for the current they consumed. I also wondered if it could have had something to do with the starting torque of the sync motors over induction motors. Those old compressors had flywheels on them almost the diameter of the motors that ran them, and it would take a huge amount of torque to set them to turning, especially when the compressor was pumping into a pipe full of compressed air. It would be about like trying to start or run the engine in your car with the tail pipe stopped up. Thanks, Will *********** REPLY SEPARATOR *********** On 6/26/2011 at 10:12 PM Bill Hawkins wrote: >Will, and the rest of you fascinated by power distribution, > >A big synchronous motor allows its power factor to be changed by >changing the field current for a given load. The motor can be >adjusted to look like a resistive load instead of inductive, or >even capacitive to correct plant power factor. Look it up. > >Industrial power consumers are charged extra for power factors >less than unity because the distribution system must carry more >current for the same watts as the power factor departs from >unity. > >Induction motors have inductive power factors because there must >be slip between the rotating field and the speed of the rotor. >Synchronous motors don't have slip, just phase angle. Zero angle >looks like a resistive load, yes? > >The compressors don't have to run in sync. > >Best, >Bill Hawkins >(who heaves a nostalgic sigh just thinking about those fine old > engines of progress) > >-----Original Message----- >From: Will Matney >Sent: Sunday, June 26, 2011 1:11 PM >To: time-nuts@febo.com >Subject: Re: [time-nuts] 60 Hz measurement party > >I quite like your generator description of "huge rotating lumps of >copper-ensnarled iron". It brings me back to around 20 years ago, when I >was a plant electrician at an older railcar manufacturer. They had huge >open-frame synchronous motors, from around the 1930's, that ran their air >compressors, and why they used this type of motor is anybodies guess. If I >remember right, they were rated at around 200 HP, or so, and were about 8 >feet in diameter. The rotor shaft was mounted on huge babbit bearings upon >concrete pillars, and about 1/3 of the motor sat in a pit in the concrete >floor. I used to have to repair the brushes on the slip rings constantly, >until I talked the boss into adding a shunt across the n.o. contacts on the >250 Vdc contactors to quench any arcing. The motors stator itself ran on >4160 Vac. Would the other compressors have to run in sync somehow, as all >of them had these motors, just some a little smaller than the others? They >drove large single cylinder compressors that fed something like a 6 inch >air line (pipe). However, they all did not run at once, and they only did >when there was a larger demand for air. Timing is the only thing I can lay >this to, and was wondering about it. > >Best, > >Will > > > >_______________________________________________ >time-nuts mailing list -- time-nuts@febo.com >To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >and follow the instructions there. > >__________ Information from ESET Smart Security, version of virus signature database 5851 (20110206) __________ > >The message was checked by ESET Smart Security. > >http://www.eset.com
JL
Jim Lux
Mon, Jun 27, 2011 3:47 AM

On 6/26/11 8:23 PM, Jim Lux wrote:

I just have to look for a set of towers with a single duplex cable.

(actually a bit of googling found a report

www.kentercanyon.org/index.php/download-public-docs/doc/25/raw

)

OK.. the electrodes are about a mile off shore from Gladstone's-4-Fish
on PCH (for those of you familiar with the area). The onshore vault is
in their parking lot.

I wonder what it looks like, and how deep the water is?  ANd whether one
would want to dive there when it's turned on?

Fascinating.. it runs 20 hours a year..

There's a some folks concerned about the overhead line going near/over a
school.  I'll bet they didn't actually know the line is unenergized
virtually all the time.

On 6/26/11 8:23 PM, Jim Lux wrote: > I just have to look for a set of towers with a single duplex cable. > > (actually a bit of googling found a report > > www.kentercanyon.org/index.php/download-public-docs/doc/25/raw > > ) OK.. the electrodes are about a mile off shore from Gladstone's-4-Fish on PCH (for those of you familiar with the area). The onshore vault is in their parking lot. I wonder what it looks like, and how deep the water is? ANd whether one would want to dive there when it's turned on? Fascinating.. it runs 20 hours a year.. There's a some folks concerned about the overhead line going near/over a school. I'll bet they didn't actually know the line is unenergized virtually all the time.
WM
Will Matney
Mon, Jun 27, 2011 4:13 AM

Here's another thought on all of this. How will this effect the newer
electronic watthour meters at peoples homes? I remember looking at the
schematics on one of these, and I don't remember seeing an internal time
base, crystal, or resonator in the circuit, so I suppose they might get
their timing from the 60 Hz line. Lets say that the frequency is slowed a
small amount, and over the year, they lose a little, which amounts to
pocket change per customer they lost, but multiply that by all the people
using it, well that's a lot of saw bucks. Also, if it was the reverse, and
the frequency was sped up by a small amount, that might translate into
paying out more, as I'm not sure exactly how those new meters work. The
only way I could see this happening, would be that the meters were not
using an internal timebase of some sort, thus depending on the line
frequency for timing, and raising and lowering with the line frequency over
a time period. Any thoughts on this?

Best,

Will

*********** REPLY SEPARATOR  ***********

On 6/26/2011 at 8:02 PM Tom Van Baak wrote:

As for monitoring 60 Hz, I was doing some on line research, and found

some interesting power line frequency meters at:

http://www.laurels.com/frequency.htm

Surprisingly affordable (less than $300).

Tom Frank

For this experiment you want an [accumulated] phase error meter,
not a line frequency meter. Remember, NERC is not dramatically
changing the 60 Hz frequency; the proposal is simply to eliminate
the steering that used to keep the cycles roughly aligned with UTC.

So a 3 or 4 or 5 digit sampling frequency counter will not reveal
the change. But over hours or days a mains connected kitchen
clock compared with your cell phone, will. In general, to see the
effect, you want something that faithfully tracks the phase and
compares it to a reference that's at least 1 ppm accurate.

Another approach, the one I use, is to continuously compare
60 Hz phase against UTC using a TIC, handling rollovers, etc.

/tvb


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.

__________ Information from ESET Smart Security, version of virus

signature database 5851 (20110206) __________

The message was checked by ESET Smart Security.

http://www.eset.com

Here's another thought on all of this. How will this effect the newer electronic watthour meters at peoples homes? I remember looking at the schematics on one of these, and I don't remember seeing an internal time base, crystal, or resonator in the circuit, so I suppose they might get their timing from the 60 Hz line. Lets say that the frequency is slowed a small amount, and over the year, they lose a little, which amounts to pocket change per customer they lost, but multiply that by all the people using it, well that's a lot of saw bucks. Also, if it was the reverse, and the frequency was sped up by a small amount, that might translate into paying out more, as I'm not sure exactly how those new meters work. The only way I could see this happening, would be that the meters were not using an internal timebase of some sort, thus depending on the line frequency for timing, and raising and lowering with the line frequency over a time period. Any thoughts on this? Best, Will *********** REPLY SEPARATOR *********** On 6/26/2011 at 8:02 PM Tom Van Baak wrote: >> As for monitoring 60 Hz, I was doing some on line research, and found some interesting power line frequency meters at: >> >> http://www.laurels.com/frequency.htm >> >> Surprisingly affordable (less than $300). >> >> Tom Frank > >For this experiment you want an [accumulated] phase error meter, >not a line frequency meter. Remember, NERC is not dramatically >changing the 60 Hz frequency; the proposal is simply to eliminate >the steering that used to keep the cycles roughly aligned with UTC. > >So a 3 or 4 or 5 digit sampling frequency counter will not reveal >the change. But over hours or days a mains connected kitchen >clock compared with your cell phone, will. In general, to see the >effect, you want something that faithfully tracks the phase and >compares it to a reference that's at least 1 ppm accurate. > >Another approach, the one I use, is to continuously compare >60 Hz phase against UTC using a TIC, handling rollovers, etc. > >/tvb > >_______________________________________________ >time-nuts mailing list -- time-nuts@febo.com >To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >and follow the instructions there. > >__________ Information from ESET Smart Security, version of virus signature database 5851 (20110206) __________ > >The message was checked by ESET Smart Security. > >http://www.eset.com
PK
Poul-Henning Kamp
Mon, Jun 27, 2011 4:59 AM

In message 4E07F7C7.9070000@earthlink.net, Jim Lux writes:

That sounds like a recipe for excitement - DC current into
seawater should generate hydrogen on one and and oxygen on the other
electrode.  At 3000 amps, rather a lot of it.

Actually you get chlorine gas at one end, can't remember which.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

In message <4E07F7C7.9070000@earthlink.net>, Jim Lux writes: >> That sounds like a recipe for excitement - DC current into >> seawater should generate hydrogen on one and and oxygen on the other >> electrode. At 3000 amps, rather a lot of it. Actually you get chlorine gas at one end, can't remember which. -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.
PK
Poul-Henning Kamp
Mon, Jun 27, 2011 5:02 AM

In message 201106270013470285.1B239AEA@smtp.citynet.net, "Will Matney" writes
:

Here's another thought on all of this. How will this effect the newer
electronic watthour meters at peoples homes? I remember looking at the
schematics on one of these, and I don't remember seeing an internal time
base, crystal, or resonator in the circuit, so I suppose they might get
their timing from the 60 Hz line.

Modern microcontrollers contain a on-chip resonator, typically 8MHz,
which is surprisingly stable, often a lot more stable than the mains
frequency.

Electricity meters are usually only precise to 1 or 2%.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

In message <201106270013470285.1B239AEA@smtp.citynet.net>, "Will Matney" writes : >Here's another thought on all of this. How will this effect the newer >electronic watthour meters at peoples homes? I remember looking at the >schematics on one of these, and I don't remember seeing an internal time >base, crystal, or resonator in the circuit, so I suppose they might get >their timing from the 60 Hz line. Modern microcontrollers contain a on-chip resonator, typically 8MHz, which is surprisingly stable, often a lot more stable than the mains frequency. Electricity meters are usually only precise to 1 or 2%. -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.