Re: [time-nuts] No more 60Hz! TEC Elimination

HM
Hal Murray
Sat, Jun 25, 2011 1:47 AM

I don't see how they connect grid that aren't totally in sync.

Each grid is in sync with itself.  In the US, there are several grids.  They
aren't connected except maybe by DC lines.

--
These are my opinions, not necessarily my employer's.  I hate spam.

> I don't see how they connect grid that aren't totally in sync. Each grid is in sync with itself. In the US, there are several grids. They aren't connected except maybe by DC lines. -- These are my opinions, not necessarily my employer's. I hate spam.
JL
Jim Lux
Sat, Jun 25, 2011 4:18 AM

On 6/24/11 6:47 PM, Hal Murray wrote:

I don't see how they connect grid that aren't totally in sync.

Each grid is in sync with itself.  In the US, there are several grids.  They
aren't connected except maybe by DC lines.

all of the US is interconnected, except for Texas.

That said there's not much interchange across the intermountain West
(e.g. not much power is run from the Pacific coast across Utah and
Colorado).  This is why the Pacific coast will have less variation than
the east coast.

As others have pointed out, power flows are done by changing the
relative phase of the two zones.  You can either keep the power flows
carefully "net zero" or you can keep the frequency the same, but not
both. So what they do is try to have times when they don't need to flow
power, so they can "open the switch" on the intertie, change the
frequency for a while to get back to where they think they should be,
then carefully resynchronize and reclose the switch.

There are remarkably few DC interties to help.  the big Pacific DC
intertie is done not so much to flow power both ways (it's almost
entirely southbound), but to make it even feasible to send power several
thousand km.  The alternate (AC) path down through the middle of
California is a apparently a bear to keep stable, and transients can
take tens of hours to die out.

After all, that transmission line is starting to be a significant
fraction of a wavelength at 60 Hz. (lambda in free space is 5000km..
prop velocity on a power line is quite a bit slower)

On 6/24/11 6:47 PM, Hal Murray wrote: >> I don't see how they connect grid that aren't totally in sync. > > Each grid is in sync with itself. In the US, there are several grids. They > aren't connected except maybe by DC lines. > > all of the US is interconnected, except for Texas. That said there's not much interchange across the intermountain West (e.g. not much power is run from the Pacific coast across Utah and Colorado). This is why the Pacific coast will have less variation than the east coast. As others have pointed out, power flows are done by changing the relative phase of the two zones. You can either keep the power flows carefully "net zero" or you can keep the frequency the same, but not both. So what they do is try to have times when they don't need to flow power, so they can "open the switch" on the intertie, change the frequency for a while to get back to where they think they should be, then carefully resynchronize and reclose the switch. There are remarkably few DC interties to help. the big Pacific DC intertie is done not so much to flow power both ways (it's almost entirely southbound), but to make it even feasible to send power several thousand km. The alternate (AC) path down through the middle of California is a apparently a bear to keep stable, and transients can take tens of hours to die out. After all, that transmission line is starting to be a significant fraction of a wavelength at 60 Hz. (lambda in free space is 5000km.. prop velocity on a power line is quite a bit slower)
JF
J. Forster
Sat, Jun 25, 2011 4:34 AM

Mostly correct, but:

As others have pointed out, power flows are done by changing the
relative phase of the two zones.  You can either keep the power flows
carefully "net zero" or you can keep the frequency the same, but not
both.

When two parts of the system are interconnected, the frequency must be the
same, except very briefly when the relative phase is being changed. The
direction and size of the power flow over the link is controlled by the
differential phase.

So what they do is try to have times when they don't need to flow
power, so they can "open the switch" on the intertie, change the
frequency for a while to get back to where they think they should be,
then carefully resynchronize and reclose the switch.

And adjust the voltages to be equal. Bth phase and voltage have to be
equal to avoid transients.

There are remarkably few DC interties to help.  the big Pacific DC
intertie is done not so much to flow power both ways (it's almost
entirely southbound), but to make it even feasible to send power several
thousand km.  The alternate (AC) path down through the middle of
California is a apparently a bear to keep stable, and transients can
take tens of hours to die out.

The transients are very lightly damped, unless the generator rotors have
quadrature windings with active controls.

-John

=============

After all, that transmission line is starting to be a significant
fraction of a wavelength at 60 Hz. (lambda in free space is 5000km..
prop velocity on a power line is quite a bit slower)


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Mostly correct, but: > As others have pointed out, power flows are done by changing the > relative phase of the two zones. You can either keep the power flows > carefully "net zero" or you can keep the frequency the same, but not > both. When two parts of the system are interconnected, the frequency must be the same, except very briefly when the relative phase is being changed. The direction and size of the power flow over the link is controlled by the differential phase. > So what they do is try to have times when they don't need to flow > power, so they can "open the switch" on the intertie, change the > frequency for a while to get back to where they think they should be, > then carefully resynchronize and reclose the switch. And adjust the voltages to be equal. Bth phase and voltage have to be equal to avoid transients. > There are remarkably few DC interties to help. the big Pacific DC > intertie is done not so much to flow power both ways (it's almost > entirely southbound), but to make it even feasible to send power several > thousand km. The alternate (AC) path down through the middle of > California is a apparently a bear to keep stable, and transients can > take tens of hours to die out. The transients are very lightly damped, unless the generator rotors have quadrature windings with active controls. -John ============= > After all, that transmission line is starting to be a significant > fraction of a wavelength at 60 Hz. (lambda in free space is 5000km.. > prop velocity on a power line is quite a bit slower) > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > >