I found a leak in the closed side of the heat exchanger/manifold tank on
top of my unit. Must have 10 connections on it. Feared making it worse so
I temporarily fixed it with a throughbolt and JBweld (miracle product!).
(Might be too good and will be there forever!) Now want to drain all the
old nasty fluid (it must be horrible if it allowed corrosion like I found and
when I opened the bleed fitting on top some nasty looking fluid oozed out)
and am not sure of the best methodology to drain and FLUSH it. Anybody
done this? Guidance? I have a gallon of antifreeze ready to go. Thanks in
advance, Jim
done this? Guidance? I have a gallon of antifreeze ready to go. Thanks in
advance, Jim
Jim,
I replaced a leaking exchanger on my 12.5BTDA a year ago, had a leak
between the seawater and closed side- (at about 1100 hrs). Make sure you
don't have seawater in the engine cooling side before you put a bunch of
time into flushing it. If you're considering a flush out, it seems now
might be the time to do a pressure test to assess the integrity of the
system.
To flush mine once the exchanger was replaced, I removed the thermostat,
filled the engine side with a strong mix of TSP, and ran the genset
loaded to heat it up. I drained the TSP solution, flushed from the
bottom, drained then re-filled with plain water, ran up to temps,
drained, flushed. I did the freshwater run cycle twice, so once with the
TSP, then twice with freshwater with a flush out in between. I wanted to
be sure the seawater was gone before I put it back into service. After
that, I drained the final time and did the final fill with antifreeze mix.