I understand what you are describing, however, the E1938A
(I typed in the wrong number on the original posting) is
a true single oven. The "double integrator" is just a
mathematical function in addition to the proportional,
integral, and differential functions that are normally used.
The double integrator improves transient response to
the extent that a typical environmental chamber ramping
as fast as it can go is not enough to get a significant
temperature error. Credit goes to Len Cutler for this.
Without the double integrator, the oven still has a thermal
gain in the many 100,000's in production. (Hand built
ones can exceed 1,000,000). This breakthrough occurred
one night when I was working late and hit upon the idea
of adding an additional heater winding around the rim
of the "hockey puck". The first try was worth over an order
of magnitude, and we later got another. I agree that we are
mainly after stability. However, another interesting
feature of the E1938A is that we carefully set each oven
at the exact turnover. Unlike 10811 crystals, all E1938A
crystals have turnovers. So accuracy matters to some
extent.
You mentioned insulation. You cannot highly insulate
an oven oscillator because you have to get rid of the
overhead heat. In any event, the key is getting rid of
heater induced thermal gradients. These are not caused
by insufficient insulation. See my 1997 FCS papers for
additional details.
The E1938A is a proof of concept that you can get
ridiculously good thermal performance without using
any extreme measures like thermos bottles, or large
thermal "flywheels", etc that are sometimes proposed for some
"ultimate" oven design. Whether they would work or not,
they are not necessary.
Rick Karlquist
N6RK
On Sat 13/11/10 7:41 PM , "Bill Hawkins" wrote:
Rick,
Is the double integrator actually a cascade of two controllers,
where the primary controls the crystal temperature and its
output sets the setpoint for a heater temperature controller?
That's how industrial control handles the lag between a 5000
gallon reactor and its steam-heated jacket. There's a sensor and
primary PID for the reactor contents (stirred) and a sensor and
PID for the jacket temperature.
When I said "ambient" I was thinking of the range that a military
receiver like the R-390 was designed for.
Seems to me that if the only disturbance to the crystal temperature
is the ambient temperature, then you can lag ambient with enough
insulation so that the internal controller can be slow enough to
have adequate gain.
There are disturbances within the internal loop that would have
to be dealt with, such as the heater supply voltage and the offset
voltage of the first error amplifier.
We are going for stability, not accuracy, right?
Bill Hawkins
P.S. Really good story to wind up the "loosing things" thread.
-----Original Message-----
From: Richard Karlquist
Sent: Saturday, November 13, 2010 3:24 PM
Yes, E1938A. I was operating on limited sleep when I posted that.
Rick
On Sat 13/11/10 8:35 AM , Magnus Danielson wrote:
On 11/13/2010 04:48 PM, Richard Karlquist wrote:
The HP E9183A achieved 1 millidegree over -55 to +85C
in a single oven. The time lag was dealt with by adding
a double integrator to PID.
I'd assume you would intend to write HP E1938A, right?
Cheers,
Magnus
Rick Karlquist N6RK
On Fri 12/11/10 8:26 AM , "Bill Hawkins" wrote:
in the heater control loop. Of course, you can't get to a
millidegree from ambient with just one oven. And you can't
eliminate time lags if you have any thermal mass.