Thanks, Ken, for your answer and link to ABYC.
Since it was my duty, in the 80s, to keep a fleet of inspected vessels in
compliance with CG regs I find the concept of automagic (sic) paralleling and
synchronizing inverters fascinating, as anyone who has had to synchronize AC
gensets by hand would.
I believe that the reference (11.5.3.7.) to "individual circuits" not being
powered from multiple sources likely was intended to apply to branch or
feeder circuits, because combinations of inverters, and combinations of inverters
with other sources seem to be permitted:
11.10.2.1.3. On Board AC Generator(s) or
Inverter(s) - On board AC generator(s) or inverter(s)
to supply the total load as calculated. Total minimum
installed KVA for a single phase system is as follows:
KVA =
Maximum Total Leg Amps. X System Voltage/1000
also:
11.10.2.1.4. Combination of Shore Power
Cable(s), On-board Generator(s) and Inverter(s) -
A combination of power sources, used simultaneously
if the boat circuitry is arranged such that the load
connected to each source is isolated from the other in
accordance with E-11.5.3.6. Shore power cable(s)
plus on-board generator(s) and inverter(s) capacity
shall be at least as large as the total electrical load
requirements as calculated. Generator(s) and
inverters(s) installation and switching shall be as
required in E-11.7.3.
It's interesting that these rules do not refer to any sort of AC bus other
than the "main AC grounding bus" and the "panelboard bus." No reference is made
to combinations of multiple sources connected through overcurrent devices to
a "bus," which is how it would be done.
Also interesting that the ABYC rules appear to be, over time, adopting much
of what has been in 46CFR for so long (for inspected vessels).
Regards,
John
"Seahorse"